<div dir="ltr">Hi Dave -<div><br></div><div>I keep hearing that Tesla is having a hard time keeping up with demand, so they may not be very motivated to add more dealers at this point. Just speculation.</div><div><br></div><div>Yes, the max continuous and peak powers add as you add up as you add more powerwalls. Energy capacity adds too. Yes, Powerwall has liquid cooling - I don&#39;t know what type of fluid it is. According to the Powerwall newsletter I received, the Powerwall will heat itself with the liquid cooling/heating system to deal with sub-freezing conditions. This will use some energy. </div><div><br></div><div>August</div><div><br></div><div class="gmail_extra"><div class="gmail_quote">On Tue, Feb 13, 2018 at 10:14 AM, Dave Angelini Offgrid Solar <span dir="ltr">&lt;<a href="mailto:offgridsolar@sti.net" target="_blank">offgridsolar@sti.net</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">The AC powerwall has cooling, it is a liquid? Anyone know if the 5kw<br>
continuous and 7kw peak limits change with multiple units?<br>
<span class=""><br>
<br>
Dave Angelini Offgrid Solar<br>
&quot;we go where powerlines don&#39;t&quot;<br>
<a href="http://members.sti.net/offgridsolar/" rel="noreferrer" target="_blank">http://members.sti.net/<wbr>offgridsolar/</a><br>
e-mail  <a href="mailto:offgridsolar@sti.net">offgridsolar@sti.net</a><br>
text <a href="tel:209%20813%200060" value="+12098130060">209 813 0060</a><br>
<br>
</span><span class="">&gt; I think that this may have come up before, but I do not remember there<br>
&gt; being a resolution:<br>
&gt; Do you guys have any tips on becoming a Tesla dealer? We have people ask<br>
&gt; about it all the time, but we have not been able to get Tesla to respond.<br>
&gt; We have installed Sonnen, which is also a great system, but the up front<br>
&gt; expense scares many people away. We are located in upstate NY which may<br>
&gt; have something to do with it.<br>
&gt;<br>
&gt; Cheers,<br>
&gt; Dave<br>
&gt;<br>
&gt;<br>
</span>&gt; *--*<br>
&gt;<br>
&gt;<br>
&gt; *Dave Tedeyan*<br>
&gt; *Senior Engineer*<br>
&gt;<br>
&gt; *Taitem Engineering, PC*<br>
<div><div class="h5">&gt; 10 Verizon Lane, Lansing, NY 14882<br>
&gt; Voice: <a href="tel:%28607%29%20930-3481%20x6" value="+16079303481">(607) 930-3481 x6</a><br>
&gt; <a href="http://www.taitem.com" rel="noreferrer" target="_blank">www.taitem.com</a><br>
&gt;<br>
&gt; On Tue, Feb 13, 2018 at 10:36 AM, August Goers &lt;<a href="mailto:august@luminalt.com">august@luminalt.com</a>&gt;<br>
&gt; wrote:<br>
&gt;<br>
&gt;&gt; Marco,<br>
&gt;&gt;<br>
&gt;&gt; Thanks for sharing, it is good to hear details from an installer who is<br>
&gt;&gt; living with a Powerwall. We starting selling the Powerwall 2 in 2017 and<br>
&gt;&gt; have worked up a large pipeline. We have about 20 installed so far, but<br>
&gt;&gt; are<br>
&gt;&gt; still waiting on utility permission to operate which is taking a long<br>
&gt;&gt; time.<br>
&gt;&gt; We have spent a good deal of time commissioning and testing each system.<br>
&gt;&gt; For the most part, our experience has been good although the<br>
&gt;&gt; commissioning<br>
&gt;&gt; software and internet connectivity features have been buggy. Hopefully<br>
&gt;&gt; those are issues that will be ironed out by Tesla. Otherwise, we&#39;ve had<br>
&gt;&gt; the<br>
&gt;&gt; systems correctly operate in on-grid and off-grid modes with both<br>
&gt;&gt; Solaredge<br>
&gt;&gt; and SunPower Equinox AC coupled systems.<br>
&gt;&gt;<br>
&gt;&gt; We installed conventional lead acid battery backup systems for over 10<br>
&gt;&gt; years and I can confidently say that Tesla&#39;s Powerwall and Gateway setup<br>
&gt;&gt; is truly market-disruptive. The design flexibility of the Gateway setup,<br>
&gt;&gt; the small size, minimal labor to install, and performance blow other<br>
&gt;&gt; systems out of the water. I hope that other manufacturers are able to<br>
&gt;&gt; catch<br>
&gt;&gt; up with this type of design.<br>
&gt;&gt;<br>
&gt;&gt; Best,<br>
&gt;&gt;<br>
&gt;&gt; August<br>
&gt;&gt;<br>
</div></div>&gt;&gt; *August Goers*<br>
&gt;&gt;<br>
&gt;&gt; Luminalt Energy Corporation<br>
&gt;&gt;<br>
&gt;&gt; o: <a href="tel:415.641.4000" value="+14156414000">415.641.4000</a> &lt;(415)%20641-4000&gt;<br>
<span class="">&gt;&gt;<br>
&gt;&gt; <a href="http://www.luminalt.com" rel="noreferrer" target="_blank">www.luminalt.com</a><br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt; On Sat, Feb 10, 2018 at 12:23 PM, Marco Mangelsdorf<br>
&gt;&gt; &lt;<a href="mailto:marco@pvthawaii.com">marco@pvthawaii.com</a>&gt;<br>
&gt;&gt; wrote:<br>
&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
</span>&gt;&gt;&gt; *Aloha Wrenches,*<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; *I thought I&#39;d share my own experiences with the Powerwall as my<br>
<span class="">&gt;&gt;&gt; company<br>
&gt;&gt;&gt; is now launching a program to add PW to existing NEM systems since the<br>
&gt;&gt;&gt; vast<br>
&gt;&gt;&gt; majority of them do not have storage which means that if the grid goes<br>
&gt;&gt;&gt; down, so does their PV system.  (With the exception of the SMA SB line<br>
&gt;&gt;&gt; and<br>
</span>&gt;&gt;&gt; their Secure Power Supply.)*<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; *And no, I&#39;m not a shill or toadie for Tesla.*<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; *marco *<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; *I wanted to walk my own talk.  Before we launched adding Powerwall to<br>
<span class="">&gt;&gt;&gt; existing Net Energy Metered solar electric systems, I wanted to make<br>
&gt;&gt;&gt; sure<br>
&gt;&gt;&gt; that what was promised on paper would work in the real world.  I added<br>
&gt;&gt;&gt; Powerwall to my NEM system last year and have been monitoring and<br>
&gt;&gt;&gt; testing<br>
</span>&gt;&gt;&gt; it during normal grid-on and grid outage modes.  And Iâ\u20ac\u2122m very pleased<br>
&gt;&gt;&gt; to<br>
&gt;&gt;&gt; report that Powerwall has performed flawlessly and as expected.*<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; *When used in a NEM system, Powerwall is programmed to be in<br>
&gt;&gt;&gt; â\u20ac\u0153Backupâ\u20ac<br>
<span class="">&gt;&gt;&gt; mode.  When utility power is on, Powerwall stands ready in a full state<br>
&gt;&gt;&gt; of<br>
&gt;&gt;&gt; charge for any power outage.  During normal grid-on conditions, my<br>
&gt;&gt;&gt; Powerall<br>
&gt;&gt;&gt; takes about .6 kilowatt-hours every other day to stay fully charged.<br>
&gt;&gt;&gt; Over<br>
</span>&gt;&gt;&gt; the course of the month, this Powerwallâ\u20ac\u2122s electricity consumption<br>
&gt;&gt;&gt; comes to<br>
&gt;&gt;&gt; about 9 kWhs or about $3/month at the current HELCO R rate.*<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; *I have turned the utility power off to my home on a number of<br>
<span class="">&gt;&gt;&gt; occasions<br>
&gt;&gt;&gt; in order to experience how Powerwall would perform in a simulated grid<br>
&gt;&gt;&gt; outage.  When the grid goes down, my house effectively becomes a<br>
&gt;&gt;&gt; self-generating micro-grid.  That is, my photovoltaic system (solar<br>
&gt;&gt;&gt; modules<br>
&gt;&gt;&gt; and inverters) and Powerwall (battery storage and integrated inverter)<br>
&gt;&gt;&gt; form<br>
&gt;&gt;&gt; a power grid with energy being created and stored and then consumed by<br>
&gt;&gt;&gt; my<br>
</span>&gt;&gt;&gt; electric loads.*<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; *Several things I noted from my simulated grid outages:*<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; *·         I purposefully overloaded Powerwall by turning on my<br>
<span class="">&gt;&gt;&gt; electric<br>
&gt;&gt;&gt; dryer and electric oven at the same time.  As expected, since the<br>
&gt;&gt;&gt; maximum<br>
&gt;&gt;&gt; output of Powerwall is 5 kilowatts, it shutdown.  Meaning that all the<br>
&gt;&gt;&gt; power in my house went off.  Within seconds, Powerwall reset itself and<br>
&gt;&gt;&gt; the<br>
&gt;&gt;&gt; power came back on, with the dryer and oven having shut down after the<br>
&gt;&gt;&gt; power went off.  If power does not come back on after your Powerwall<br>
&gt;&gt;&gt; trips<br>
&gt;&gt;&gt; off, you will need to turn off those high-power loads and reset<br>
&gt;&gt;&gt; Powerwall<br>
&gt;&gt;&gt; by turning its black on-off switch, located on the right side of the<br>
&gt;&gt;&gt; unit,<br>
&gt;&gt;&gt; from on to off and then on again.  The important takeaway: during a<br>
&gt;&gt;&gt; utility<br>
&gt;&gt;&gt; outage, you will need to be careful as far as operating heavy electric<br>
&gt;&gt;&gt; loads, especially 240 volt appliances both from the perspective of<br>
&gt;&gt;&gt; overloading your Powerwall and rapidly drawing down the battery<br>
&gt;&gt;&gt; capacity,<br>
</span>&gt;&gt;&gt; especially at night.*<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; *·         The magic of frequency shifting.  Without getting into too<br>
<span class="">&gt;&gt;&gt; much techno-talk, this is the story of frequency shifting.  Normal<br>
&gt;&gt;&gt; utility<br>
&gt;&gt;&gt; frequency is 60 hertz (Hz).  PV inverters require the utility frequency<br>
&gt;&gt;&gt; to<br>
&gt;&gt;&gt; be at or near 60 Hz in order to operate.  During a grid outage,<br>
&gt;&gt;&gt; Powerwall<br>
&gt;&gt;&gt; effectively establishes grid quality power (120/240 volts at 60 Hz),<br>
&gt;&gt;&gt; allowing a micro grid to operate with solar providing power to your<br>
&gt;&gt;&gt; house<br>
&gt;&gt;&gt; loads (during daylight hours) and charge Powerwall as needed.  During<br>
&gt;&gt;&gt; the<br>
&gt;&gt;&gt; day with the loads being met by your PV system and Powerwall being at<br>
&gt;&gt;&gt; or<br>
&gt;&gt;&gt; near full state of charge (97-100 percent), Powerwall will shift the<br>
&gt;&gt;&gt; frequency from 60 to 66 Hz in order to turn off the PV inverter(s).<br>
&gt;&gt;&gt; That<br>
&gt;&gt;&gt; is, the PV inverter(s) see the frequency out of spec and shut down as<br>
</span>&gt;&gt;&gt; theyâ\u20ac\u2122re expected and required to do.  Why? Because with Powerwall at<br>
&gt;&gt;&gt; or<br>
&gt;&gt;&gt; near full and the house loads being met, thereâ\u20ac\u2122s nowhere for any<br>
<span class="">&gt;&gt;&gt; additional<br>
&gt;&gt;&gt; solar generation to go.  Powerwall will wait for its the state of<br>
&gt;&gt;&gt; charge to<br>
&gt;&gt;&gt; drop below 96-97 percent before shifting the frequency back to 60 Hz<br>
&gt;&gt;&gt; which<br>
&gt;&gt;&gt; allows the PV system to restart and generate solar power again.   This<br>
&gt;&gt;&gt; frequency shifting can take place repeatedly over the course of the day<br>
&gt;&gt;&gt; depending on load demands, solar potential and Powerwall state of<br>
&gt;&gt;&gt; charge<br>
</span>&gt;&gt;&gt; and is perfectly normal and does not damage the PV inverters.*<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; *·         **66 Hz and home appliances: when Powerwall is at 66 Hz,<br>
<span class="">&gt;&gt;&gt; some<br>
&gt;&gt;&gt; of your house loads may be affected.  What I and other Powerwall owners<br>
&gt;&gt;&gt; have noticed, while not a comprehensive list, can include: electronic<br>
&gt;&gt;&gt; clocks running fast, motors sounding different (microwave, washing<br>
&gt;&gt;&gt; machine,<br>
&gt;&gt;&gt; pumps), uninterruptible power sources (UPS) not charging and going into<br>
</span>&gt;&gt;&gt; back-up power mode, appliances having a computer behaving unusually.*<br>
<div class="HOEnZb"><div class="h5">&gt;&gt;&gt;<br>
&gt;&gt;&gt; ______________________________<wbr>_________________<br>
&gt;&gt;&gt; List sponsored by Redwood Alliance<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.<wbr>org</a><br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; Change listserver email address &amp; settings:<br>
&gt;&gt;&gt; <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/<wbr>options.cgi/re-wrenches-re-<wbr>wrenches.org</a><br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; List-Archive: <a href="http://www.mail-archive.com/re" rel="noreferrer" target="_blank">http://www.mail-archive.com/re</a><br>
&gt;&gt;&gt; -<a href="http://wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">wrenches@lists.re-wrenches.<wbr>org/maillist.html</a><br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; List rules &amp; etiquette:<br>
&gt;&gt;&gt; <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.<wbr>htm</a><br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; Check out or update participant bios:<br>
&gt;&gt;&gt; <a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt; ______________________________<wbr>_________________<br>
&gt;&gt; List sponsored by Redwood Alliance<br>
&gt;&gt;<br>
&gt;&gt; List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.<wbr>org</a><br>
&gt;&gt;<br>
&gt;&gt; Change listserver email address &amp; settings:<br>
&gt;&gt; <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/<wbr>options.cgi/re-wrenches-re-<wbr>wrenches.org</a><br>
&gt;&gt;<br>
&gt;&gt; List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches" rel="noreferrer" target="_blank">http://www.mail-archive.com/<wbr>re-wrenches@lists.re-wrenches</a>.<br>
&gt;&gt; org/maillist.html<br>
&gt;&gt;<br>
&gt;&gt; List rules &amp; etiquette:<br>
&gt;&gt; <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.<wbr>htm</a><br>
&gt;&gt;<br>
&gt;&gt; Check out or update participant bios:<br>
&gt;&gt; <a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt; ______________________________<wbr>_________________<br>
&gt; List sponsored by Redwood Alliance<br>
&gt;<br>
&gt; List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.<wbr>org</a><br>
&gt;<br>
&gt; Change listserver email address &amp; settings:<br>
&gt; <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/<wbr>options.cgi/re-wrenches-re-<wbr>wrenches.org</a><br>
&gt;<br>
&gt; List-Archive:<br>
&gt; <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/<wbr>re-wrenches@lists.re-wrenches.<wbr>org/maillist.html</a><br>
&gt;<br>
&gt; List rules &amp; etiquette:<br>
&gt; <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.<wbr>htm</a><br>
&gt;<br>
&gt; Check out or update participant bios:<br>
&gt; <a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
&gt;<br>
&gt;<br>
<br>
<br>
</div></div><span class="im HOEnZb">Dave Angelini Offgrid Solar<br>
&quot;we go where powerlines don&#39;t&quot;<br>
<a href="http://members.sti.net/offgridsolar/" rel="noreferrer" target="_blank">http://members.sti.net/<wbr>offgridsolar/</a><br>
e-mail  <a href="mailto:offgridsolar@sti.net">offgridsolar@sti.net</a><br>
text <a href="tel:209%20813%200060" value="+12098130060">209 813 0060</a><br>
<br>
</span><div class="HOEnZb"><div class="h5">______________________________<wbr>_________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.<wbr>org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/<wbr>options.cgi/re-wrenches-re-<wbr>wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/<wbr>re-wrenches@lists.re-wrenches.<wbr>org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.<wbr>htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</div></div></blockquote></div><br></div></div>