<div dir="ltr">Hello Allan,<div><br></div><div>Did you check the Voc of each string?  Is it possible that there could one or more shorted bypass diodes in the modules?</div><div><br></div><div>Just a thought.</div><div><br></div><div>Steve Bell</div><div>Morningstar tech support</div></div><div class="gmail_extra"><br><div class="gmail_quote">On Thu, Aug 25, 2016 at 8:04 AM, Allan Sindelar <span dir="ltr">&lt;<a href="mailto:allan@sindelarsolar.com" target="_blank">allan@sindelarsolar.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  

    
  
  <div style="background-color:rgb(255,255,255);color:rgb(0,0,0)" bgcolor="#FFFFFF" text="#000000">
    Wrenches,<br>
    Here&#39;s one I haven&#39;t seen before. 1997 grid-tie battery backup
    system that was one of my first, although actual installation was by
    another before I was licensed. 16 BP 275, 36-cell 12V modules, the
    standard of that time. Early Outback MX60 replaced C40 around 2005;
    array rewired to four 48V strings of four modules at that time,
    serving a 24V battery bank. Tested with an end-of-life 9-year-old
    AGM battery bank in the system, but in Sell mode with a 26.4V Sell
    voltage setpoint.<br>
    <br>
    At 11 am, 68ºF, 900W/m<sup>2</sup> on the Daystar, with the array
    under charge, I measured 3.5A, 3.4A, 2.4A, and 3.6A.
    Short-circuiting each string, I measured 4.0A, 3.7A, 3.8A, and 3.7A.
    Original rating was 4.45A, so except for the third string, current
    is what I&#39;d reasonably expect from 20-year-old module degradation.
    However, watching the periodic MPPT sweep from the MX60 at the
    array, the maximum power point voltage for the entire 48V array
    settled at 14.6A at 37.2V, or about 540 watts from a 1,200W
    (originally rated) array.<br>
    <br>
    I have commonly seen the current reduce substantially with
    age-related degradation, while the MPP voltage remains fairly close
    to original. I have never seen the voltage drop this far - an
    average of 9.3V MPP per each 12V module. All of the cells are
    seriously browned. I have other systems out there with the same
    modules of similar age that don&#39;t exhibit this weird behavior. Can
    anyone help me understand why the MPP voltage would drop so far
    below what is typical?<br>
    <br>
    There is a slight possibility of corroded buried input conductors,
    because of a serious but corrected issue of galvanic corrosion from
    a ground fault (a Romex connector pinching a conductor and allowing
    seepage to ground). This was corrected years ago, but the input
    conductors were direct burial for ~100&#39; and there was never a
    bonding conductor between the array and the house, so there is a
    potential for corrosion damage. However, the voltage measured at
    both ends while charging was identical, so I think that would
    indicate that high conductor resistance isn&#39;t the issue.<br>
    <br>
    As usual, thank you for the collective and individual wisdom shared
    here.<span class="HOEnZb"><font color="#888888"><br>
    Allan<br>
    <div>-- <br>
      
      
      
      
      
      
      
      
      
      
      <div>
        <p class="MsoNormal"><b>Allan Sindelar</b><br>
          <span style="font-size:10.0pt"><a href="mailto:allan@sindelarsolar.com" target="_blank">allan@sindelarsolar.com</a></span><br>
          <span style="font-size:10.0pt">NABCEP Certified PV
            Installation Professional<br>
            NABCEP Certified Technical Sales Professional<br>
            New Mexico EE98J Journeyman Electrician<br>
            Founder (Retired), <span>Positive
              Energy,
              Inc.</span><br>
            <b><a href="tel:505%20780-2738" value="+15057802738" target="_blank">505 780-2738</a> cell</b><br>
            <br>
            <b><u></u><u></u></b></span></p>
        <p class="MsoNormal"><u></u> <u></u></p>
      </div>
    </div>
  </font></span></div>

<br>______________________________<wbr>_________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.<wbr>org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/<wbr>options.cgi/re-wrenches-re-<wbr>wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/<wbr>re-wrenches@lists.re-wrenches.<wbr>org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.<wbr>htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div>