<div dir="ltr"><br><div class="gmail_extra"><br><div class="gmail_quote">On Sat, Jun 18, 2016 at 11:30 PM, Gary Willett <span dir="ltr">&lt;<a href="mailto:Gary@icarussolarservices.com" target="_blank">Gary@icarussolarservices.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div bgcolor="#FFFFFF" text="#000000">
    <p><br></p>
    <p>Page 14: I am assuming that the Sonnen system is comprised of the
      components and functionality encompassed in the box in the upper
      right side of figure 2. And the Outback Radian is the inverter
      used for &quot;F&quot; - the &quot;Storage System&quot; inverter?<br></p></div></blockquote><div>Correct, although the consumption meter is also included. They supply the external metering which you have to install externally in the PV supply cabling.</div><div> </div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div bgcolor="#FFFFFF" text="#000000"><p>
    </p>
    <p>Pages 14, 15, and 29: No info on PV array sizing is provided.
      Does the Sonnen design assume that a totally separate grid-tied
      inverter system already exists or must be installed if PV charging
      is desired? <br></p></div></blockquote><div>The PV design depends on the consumption model, how much battery, but they do advocate no more than 8KW, which is what we are using on the installation. I think you could use about 4kW quite easily for a ECO16. It depends on the daily consumption of the home. </div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div bgcolor="#FFFFFF" text="#000000"><p>
    </p>
    <p>Page 15: The system is AC coupled. When in &quot;Backup Mode&quot; how does
      the Sonnen BMS control charging from the external grid-tied PV
      inverter system once its battery modules are fully charged and the
      house loads are low? Does the Sonnen BMS handle this situation
      without disconnecting relays or frequency-shift throttling?<br></p></div></blockquote><div>Frequency shift. It will change the micro-grid frequency to 60.9hz</div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div bgcolor="#FFFFFF" text="#000000"><p>
    </p>
    <p>Page 15: Is the nomenclature in Figure 2 for the Utility Power
      Meter &quot;G&quot; and the Consumption Meter &quot;D&quot;  reversed?</p></div></blockquote><div> G should be &quot;Home&quot;. Not sure what they were doing there, I will let them know.</div></div>