<div dir="ltr">Ray; <div>I&#39;ve even had problems with Magnums and Outbacks not working with certain GFCI outlets.I usually just avoid installing GFCIs in tiny, remote off-grid systems designed for a specialty application with no electrical inspector involved or required. GFCIs cause all kinds of mischief with equipment and are a phantom load. I put them in the same league as hard-wired 120VAC smoke detectors off the grid.</div><div><br></div><div>Exeltech inverters are certainly the most quiet RFI-wise, but the low efficiency, $  and no-load draw are a bummer.</div><div><br></div><div>With William&#39;s application, I&#39;d avoid the inverter entirely and go DC, then you have no GFCI or AC codes. If the sat link DC input specs allow 36VDC input, you have many off-the shelf options available for a boost/buck power supply from 24VDC. Digikey even.</div></div><div class="gmail_extra"><br clear="all"><div><div class="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><span style="font-size:12.8000001907349px">Dan Fink</span><div style="font-size:12.8000001907349px">Adjunct Professor of Solar Energy Technology, Ecotech Institute</div><div style="font-size:12.8000001907349px">IREC Certified Instructor\u2122 for: </div><div style="font-size:12.8000001907349px">~ PV Installation Professional</div><div style="font-size:12.8000001907349px">~ Small Wind Installer</div><div style="font-size:12.8000001907349px">Executive Director, Buckville Energy</div><div style="font-size:12.8000001907349px">NABCEP Registered Continuing Education Providers\u2122<br><a href="tel:970.672.4342" value="+19706724342" style="color:rgb(17,85,204)" target="_blank">970.672.4342</a></div><br> </div></div></div></div></div></div></div></div></div></div>
<br><div class="gmail_quote">On Mon, Mar 28, 2016 at 4:47 PM, Ray Walters <span dir="ltr">&lt;<a href="mailto:ray@solarray.com" target="_blank">ray@solarray.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div bgcolor="#FFFFFF" text="#000000">
    What about building a 30 vdc system (5 x 6v batteries in series) 
    and adjust the settings on a Midnite Classic to work with that?  How
    tight does the 30 vdc output need to be?<br>
    <br>
    On inverters, I&#39;ve had  trouble with the Suresine, basically not
    working with GFCI outlets.<br>
    I keep trying different models of GFCIs, but they keep randomly
    tripping on 2 different systems. <br>
    Morningstar&#39;s list of &quot;approved&quot; GFCIs doesn&#39;t list any currently
    manufactured models, while calls to their tech support yields &quot;Oh,
    that shouldn&#39;t be a problem, it should work with all GFCIs...&quot;<br>
    Way too many free trips out trying to fix this, so I may have to
    abandon GFCI protection, or replace the inverters.  <br>
    My suggestion for that small load: Exeltech 125.  Better than grid
    waveform, and I recently pulled one out of corroded outdoor
    enclosure almost 15 years old: it looked terrible, but was still
    working fine.  It would also be lower cost and fit in a smaller
    enclosure.<br>
    <pre cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
<a href="tel:303%20505-8760" value="+13035058760" target="_blank">303 505-8760</a></pre><div><div class="h5">
    <div>On 3/28/2016 2:24 PM, Dan Fink wrote:<br>
    </div>
    </div></div><blockquote type="cite"><div><div class="h5">
      <div dir="ltr">Hi William;
        <div>30VDC is kind of odd, but 36VDC is common. The folks at
          Solar Converters might be able to fix you up with a custom
          one, or perhaps 36V is within the sat unit&#39;s input range.</div>
        <div>As for the inverter, I&#39;ve never gone wrong with the
          Morningstar SureSine. Slick little unit.<br>
          <div class="gmail_extra"><br clear="all">
            <div>
              <div>
                <div dir="ltr">
                  <div>
                    <div dir="ltr">
                      <div>
                        <div dir="ltr">
                          <div>
                            <div dir="ltr">
                              <div><span style="font-size:12.8000001907349px">Dan
                                  Fink</span>
                                <div style="font-size:12.8000001907349px">Adjunct
                                  Professor of Solar Energy Technology,
                                  Ecotech Institute</div>
                                <div style="font-size:12.8000001907349px">IREC
                                  Certified Instructor\u2122 for: </div>
                                <div style="font-size:12.8000001907349px">~
                                  PV Installation Professional</div>
                                <div style="font-size:12.8000001907349px">~
                                  Small Wind Installer</div>
                                <div style="font-size:12.8000001907349px">Executive
                                  Director, Buckville Energy</div>
                                <div style="font-size:12.8000001907349px">NABCEP
                                  Registered Continuing Education
                                  Providers\u2122<br>
                                  <a href="tel:970.672.4342" value="+19706724342" style="color:rgb(17,85,204)" target="_blank">970.672.4342</a></div>
                                <br>
                                 </div>
                            </div>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
            <br>
            <div class="gmail_quote">On Mon, Mar 28, 2016 at 1:44 PM,
              William Miller <span dir="ltr">&lt;<a href="mailto:william@millersolar.com" target="_blank"></a><a href="mailto:william@millersolar.com" target="_blank">william@millersolar.com</a>&gt;</span>
              wrote:<br>
              <blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
                <div link="blue" vlink="purple" lang="EN-US">
                  <div>
                    <p class="MsoNormal"><span style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">Friends:</span></p>
                    <p class="MsoNormal"><span style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></p>
                    <p class="MsoNormal"><span style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">I
                        am designing a satellite data interface for a
                        large off-grid system for a state highway
                        department facility.  We will be using the
                        Outback Optics data capabilities along with
                        equipment manufactured by Control by Web.</span></p>
                    <p class="MsoNormal"><span style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></p>
                    <p class="MsoNormal"><span style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">I\u2019d
                        like to run the satellite system on a battery
                        power source so I can hope to use it when we
                        need it most, when the power is down.  We have a
                        separate 24 volt battery bank remaining from a
                        previous generator control system.  The
                        satellite system operates on 30 VDC at 2 amps.</span></p>
                    <p class="MsoNormal"><span style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></p>
                    <p class="MsoNormal"><span style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">My
                        first choice is to find a DC to DC converter
                        from nominal 24 volts.  Do any of you know of
                        one that you could recommend?</span></p>
                    <p class="MsoNormal"><span style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></p>
                    <p class="MsoNormal"><span style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">My
                        second choice is to use a small inverter.  Can
                        anyone suggest one at this small wattage?  I
                        don\u2019t know how good the power supply is at
                        rejecting waveform distortion so I presume an
                        inverter needs to be somewhat close to a sine
                        wave.<br>
                        <br>
                      </span></p>
                    <p class="MsoNormal"><span style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">Thanks
                        in advance.</span></p>
                    <p class="MsoNormal"><span style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></p>
                    <p class="MsoNormal"><span style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">William
                        Miller</span></p>
                    <p class="MsoNormal"><span style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></p>
                    <p class="MsoNormal"><span style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></p>
                    <p class="MsoNormal"><span style="font-size:10.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;;color:black"><img src="cid:part3.07090108.01010501@solarray.com" alt="Gradient Cap_mini" height="28" width="64"><br>
                        Lic 773985<br>
                        <a href="http://www.millersolar.com/" target="_blank">millersolar.com</a><br>
                        <a href="tel:805-438-5600" value="+18054385600" target="_blank">805-438-5600</a></span></p>
                    <p class="MsoNormal"> </p>
                  </div>
                </div>
              </blockquote>
            </div>
            <br>
          </div>
        </div>
      </div>
      <br>
      <fieldset></fieldset>
      <br>
      </div></div><span class=""><pre>_______________________________________________
List sponsored by Redwood Alliance

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>

</pre>
    </span></blockquote>
    <br>
  </div>

<br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div>