<html><head><meta http-equiv="content-type" content="text/html; charset=utf-8"></head><body dir="auto"><div>Hi Ray</div><div>Well you got me there</div><div>I meant no disrespect to you personally.</div><div>I think as a whole the code making panels do their best to keep up.</div><div>If I missed some of the particulars</div><div>Please excuse me.</div><div>And I guess it would be more useful to offer a workable solution</div><div>Maybe I've missed some of the details but doesn't mid nite offer a shunt trip breaker as part of their ebox that works with the birdhouse</div><div>I've used one in the past</div><div>Is it not ul listed</div><div>That's all from me</div><div>Pat<br><br><div>Patrick A. Shortell<div>Licensed Master Electrician</div><div>Certified Solar Installer</div><div>71 Oregon Street</div><div>Long Beach N.Y. 11561</div><div><a href="http://www.thesolarstorehouse.com">Www.thesolarstorehouse.com</a></div><div><br></div></div></div><div><br>On Mar 15, 2016, at 5:16 PM, Ray Walters &lt;<a href="mailto:ray@solarray.com">ray@solarray.com</a>&gt; wrote:<br><br></div><blockquote type="cite"><div>
  
    <meta content="text/html; charset=windows-1252" http-equiv="Content-Type">
  
  
    So Pat, you stated "<i>There are simple ways to work around these
      issues</i>".&nbsp; Actually, the major off grid inverter manus do not
    have a solution for this ( Magnum, Outback, Exeltech, Schneider,
    SMA)&nbsp; <br>
    Can you show us an example of a UL listed system that has multiple
    inverters (over 8 kW cont.), with rapid disconnects within 5 ft?&nbsp;
    I'm really looking for actual solutions here folks, and I haven't
    seen a single system ever built, much less even a simple wiring
    diagram that would comply with this new requirement. (<i>690.12(5)
      Equipment that performs the rapid shutdown shall be listed and
      identified</i>)<br>
    <br>
    Also, for every improvement comes a whole new set of problems.&nbsp; Your
    "<i>What would I do in my own house?</i>" is an excellent point.&nbsp;
    Personally, I would not want the neighbor's kids to be able to shut
    off my refrigerator or grandma's breathing machine with the touch of
    an outside accessible, unlockable button.<br>
    <br>
    I've been cobbling together code compliant systems for 2 decades, so
    yes, I'm sure I could scavenge relays from the EV world to do this.&nbsp;
    But the days of inventing custom (non UL) solutions to meet new
    requirements should be over.&nbsp; If this is to be a national
    requirement, the industry should be mature enough to offer multiple
    solutions for code compliance.&nbsp; I'm all for improving safety, but it
    needs to be done as an industry: together, incrementally.<br>
    <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
    <div class="moz-cite-prefix">On 3/15/2016 1:48 PM, Patrick Shortell
      wrote:<br>
    </div>
    <blockquote cite="mid:CAHcXnFUCBqdavA406sYZLkEGwVZxM5B8OLmFVeJLp+6tQ1MRGQ@mail.gmail.com" type="cite">
      <div dir="ltr">
        <div>
          <div>
            <div>
              <div>
                <div>
                  <div>
                    <div>
                      <div>Dear List,<br>
                      </div>
                      Maybe it's an over simplistic opinion, but
                      shouldnt all sources be disconnected rapidly in an
                      emergency situation.<br>
                    </div>
                    We can always do better than what the code requires.
                    I get frustrated when people go to the book, (and
                    try to hide behind the text).&nbsp; instead of thinking
                    through real life scenarios.<br>
                  </div>
                  There are simple ways to work around these issues.<br>
                </div>
                I find when something is questionable, Ill call the AHJ
                and get his approval First.<br>
              </div>
              What would I do in my own house?<br>
            </div>
            What if someone thought all the power was off when they
            dragged a hoseline into my basement.<br>
          </div>
          My two cents<br>
        </div>
        Pat<br>
      </div>
      <div class="gmail_extra"><br>
        <div class="gmail_quote">On Tue, Mar 15, 2016 at 1:10 PM, <span dir="ltr">&lt;<a moz-do-not-send="true" href="mailto:billbrooks7@sbcglobal.net" target="_blank">billbrooks7@sbcglobal.net</a>&gt;</span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">Ray,<br>
            <br>
            I guess I have to step in after that acknowledgement. PV
            system circuit is a<br>
            self-defined term and therefore cannot be defined unless you
            are going to<br>
            develop a meaning that is different from the
            self-definition. It means ANY<br>
            circuit in a PV system. This includes battery and
            stand-alone circuits in<br>
            the 2014 NEC.<br>
            <br>
            The language of the 2014 NEC was a compromise between the
            fire service and<br>
            the PV industry.&nbsp; Originally, the language required
            essentially module-level<br>
            shutdown. I raised the concern with the PV industry to get
            them involved<br>
            since most were not paying attention at the time. This
            language was<br>
            developed and intended to cover all circuits in a PV system.
            In the 2014<br>
            NEC, batteries are part of a PV system and therefore fall
            under this<br>
            requirement.<br>
            <br>
            In the 2017 NEC, we were very careful to carve out all
            batteries and loads,<br>
            that were previously part of PV systems, and place them in
            their own<br>
            articles. Don't shoot the messenger on this one and don't
            think for a minute<br>
            that I alone made this requirement or am alone in
            interpreting it in this<br>
            way. I did author this compromise with other representatives
            of the PV<br>
            industry so I think I know what the intent was.<br>
            <br>
            It is understandably difficult for battery systems and I
            would try to keep<br>
            battery circuits as short as possible. The 5-feet was
            intended to match the<br>
            requirement of 690.71(H)--which is further evidence of the
            intent of the<br>
            2014 NEC.<br>
            <br>
            The 2017 NEC removes batteries from the requirement, but
            they still cannot<br>
            backfeed the PV array. Energy storage systems (Article 706)
            will have their<br>
            own requirements in time--that is guaranteed.<br>
            <br>
            Bill.<br>
            <div class="HOEnZb">
              <div class="h5"><br>
                <br>
                -----Original Message-----<br>
                From: RE-wrenches [mailto:<a moz-do-not-send="true" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>]
                On<br>
                Behalf Of Ray Walters<br>
                Sent: Tuesday, March 15, 2016 9:02 AM<br>
                To: RE-wrenches &lt;<a moz-do-not-send="true" href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
                Subject: [RE-wrenches] Rapid Shutdown<br>
                <br>
                Greetings Esteemed Wrenches:<br>
                <br>
                I've just heard back from our inspector here in
                Colorado, and we are still<br>
                being required to disconnect the batteries under
                690.12.&nbsp; No where in 690.12<br>
                are batteries mentioned, nor in the appropriate 690.71
                section that deals<br>
                with batteries.&nbsp; The entire reasoning behind this is
                based on a single<br>
                article written by a single person: Bill Brooks.&nbsp; I have
                contacted both<br>
                Outback and Magnum on this issue, and their engineers
                are unaware that rapid<br>
                shutdown applies.<br>
                My interpretation is that I could install an inverter
                and battery system<br>
                that was charged from a generator, and we would not need
                any rapid shutdown<br>
                at all.&nbsp; But according to Bill, as soon as I put a
                single solar module into<br>
                the system, suddenly the entire system becomes PV? The
                problem lies with the<br>
                term 'PV System circuit'&nbsp; used in 690.12.&nbsp; 690.2 Defines
                'PV Output<br>
                circuit', and 'PV source circuit', but there is no 'PV
                system circuit'<br>
                defined.&nbsp; 690.12 therefore uses an undefined term.<br>
                Our design uses 2 inverters, so if we used Midnite's E
                panel with their<br>
                remote trip breakers, the 2nd inverter would be more
                than 5 ft from the<br>
                batteries.&nbsp; If we used Magnum or Outback DC disconnects
                (that would comply<br>
                with the 5 ft rule specified in 690.71) they don't offer
                remote trip.<br>
                We have a Midnite Rapid disconnect Combiner on the roof
                with the Birdhouse,<br>
                so we are complying with 690.12, it should not be
                applied to batteries<br>
                though.<br>
                <br>
                Thanks,<br>
                <br>
                --<br>
                R.Ray Walters<br>
                CTO, Solarray, Inc<br>
                Nabcep Certified PV Installer,<br>
                Licensed Master Electrician<br>
                Solar Design Engineer<br>
                303 505-8760<br>
                <br>
                _______________________________________________<br>
                List sponsored by Redwood Alliance<br>
                <br>
                List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
                <br>
                Change listserver email address &amp; settings:<br>
                <a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                <br>
                List-Archive:<br>
                <a moz-do-not-send="true" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                <br>
                List rules &amp; etiquette:<br>
                <a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
                <br>
                Check out or update participant bios:<br>
                <a moz-do-not-send="true" href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
                <br>
                _______________________________________________<br>
                List sponsored by Redwood Alliance<br>
                <br>
                List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
                <br>
                Change listserver email address &amp; settings:<br>
                <a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                <br>
                List-Archive: <a moz-do-not-send="true" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                <br>
                List rules &amp; etiquette:<br>
                <a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
                <br>
                Check out or update participant bios:<br>
                <a moz-do-not-send="true" href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
                <br>
              </div>
            </div>
          </blockquote>
        </div>
        <br>
        <br clear="all">
        <br>
        -- <br>
        <div class="gmail_signature">
          <div dir="ltr">
            <div>
              <div dir="ltr">
                <div dir="ltr">Patrick A. Shortell
                  <div><i>Licensed Master Electrician</i></div>
                  <div><i>Certified Solar Installer</i></div>
                  <div>71 Oregon Street</div>
                  <div>Long Beach N.Y. 11561</div>
                  <div>cell: 516-477-0221</div>
                  <div><br>
                  </div>
                  <div><br>
                  </div>
                  <div><br>
                  </div>
                  <div><br>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  

</div></blockquote><blockquote type="cite"><div><span>_______________________________________________</span><br><span>List sponsored by Redwood Alliance</span><br><span></span><br><span>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></span><br><span></span><br><span>Change listserver email address &amp; settings:</span><br><span><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br><span></span><br><span>List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a></span><br><span></span><br><span>List rules &amp; etiquette:</span><br><span><a href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a></span><br><span></span><br><span>Check out or update participant bios:</span><br><span><a href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a></span><br><span></span><br></div></blockquote></body></html>