<div dir="ltr">Hi, <div>Wondering if anyone has insight into Code requirements for securing/supporting PV wire behind the modules? </div><div><br></div><div>I am aware that USE-2 sends you to Section 334.30 requirements for Type NM (12&quot; from box, every 4.5 &#39;). </div><div><br></div><div>However, I think this is totally bogus, for 2 reasons. </div><div>1) Section 338.10(B)(4)(b) that refers the NM article is titled &quot;Branch circuits or Feeders.&quot;  These are PV source and output circuits, not branch circuits or feeders. </div><div><br></div><div>2) it is nearly IMPOSSIBLE to secure the PV wire within 12&quot; of the module junction box for many modules, especially in landscape wiring, without causing more harm than good, too tight a bending radius, stress on conductors. </div><div><br clear="all"><div>334.40(B) maybe leaves a little wiggle room for concealed spaces in structures where it is impracticable to support. </div><div><br></div><div>My big problem here is that both requirements of 334.30 are useless or harmful to PV systems. 12&quot; to the box is often impossible, and 4.5&quot; feet is too long to go without any support behind the array!!! I just noticed there was a proposal in 2017 to Codify the 334.40 requirements for PV cables and so I guess I only have myself to blame for not writing a better proposal at this point. </div><div><br></div><div>Rebekah</div>-- <br><div><div dir="ltr">Tel: 336.266.8800<br>NABCEP Certified Solar PV Installation Professional\u2122 091209-85<br>NC Licensed Electrical Contractor</div></div>