<div dir="ltr"><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">Combined circuits use the sum of inverter output ratings x 1.25, so the 225A fuse is your answer I believe.</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">Consider the case with paralleled microinverters. For example, the max Enphase M250 with 1.0A rating on a 20A string is 16 x 1.0 x 1.25 = 20A. If you have multiple branch circuits you would take the total number of microinverters times the rating time 1.25 to get the combined circuit wire size and OCPD requirements.</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">The same methodology would apply to string inverters.</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">Jason Szumlanski</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">Florida Solar Design Group</div><div class="gmail_extra"><br clear="all"><div><div class="gmail_signature"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"></div></div></div></div></div></div></div></div>
<br><div class="gmail_quote">On Sat, Oct 24, 2015 at 7:50 AM, Allen Frishman <span dir="ltr">&lt;<a href="mailto:amfrish@aeonsolar.com" target="_blank">amfrish@aeonsolar.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div style="word-wrap:break-word">Wrencher&#39;s,<div>Quick question regarding sizing the fuse for a combined group of inverters.   If I have six 10KW three phase inverters each with a max AC current of 30A they each require a 3 pole 40 A breaker.   If I then take the combined output of the AC combiner panel I see two possible options for sizing the combined fuse size.    </div><div><br></div><div>6 inverters x 40A breakers each = 240A so I need to use a 250A fuse</div><div>6 Inverters x 30A max output each = 180A x 1.25 = 225A Fuse</div><div><br></div><div>Seems like both are acceptable options since all wire will be protected.</div><div><br></div><div>All feedback is appreciated.<br><div>
<span style="border-collapse:separate;color:rgb(0,0,0);font-family:Helvetica;font-style:normal;font-variant:normal;font-weight:normal;letter-spacing:normal;line-height:normal;text-align:auto;text-indent:0px;text-transform:none;white-space:normal;word-spacing:0px;font-size:medium"><div><p class="MsoNormal"><i><span style="font-size:10.5pt;color:black">Al Frishman</span></i><span style="font-size:13.5pt;color:black"><br></span><span style="font-size:13.5pt;color:rgb(3,1,0)">Aeon</span><span style="font-size:13.5pt;color:rgb(255,151,0)">Solar</span><span style="font-size:13.5pt;color:black"></span></p><p class="MsoNormal"><i><span style="font-size:10.5pt;color:black"><a href="tel:%28917%29%20699-6641" value="+19176996641" target="_blank">(917) 699-6641</a> - cell</span></i><span style="font-size:10.5pt;color:black"><br></span><i><span style="font-size:10.5pt;color:black"><a href="tel:%28888%29%20460-2867" value="+18884602867" target="_blank">(888) 460-2867</a></span></i><span style="font-size:10.5pt;color:black"><br></span><i><span style="font-size:10.5pt;color:black"><a href="http://www.aeonsolar.com/" target="_blank">www.aeonsolar.com</a></span></i></p></div></span></div></div></div>
<br>
<br></blockquote></div><br></div></div>