<div dir="ltr">Hello wrenches, question about running conductors in cable tray.  So we have our allowance in 690.31(C)(2) for using small PV Wire in cable tray for PV source and output circuits.  I&#39;m trying to determine what adjustment factor to apply when there are a bunch of small conductors.<div><br></div><div>392.80(A)(2)(a) and (b) both address single conductor cable in covered cable tray, but only refer to conductors from 1/0 to 500 kcmil, and 600 kcmil and up.  I&#39;m looking more at 40 or 50 12 AWG conductors (20 to 30 source circuits).  The adjustment factors in 392.80(A)(2) are pretty hefty - only 60 to 70% of the rated ampacity, but as stated in Table 301.15(B)(17) (conductors in free air, so that helps). </div><div><br></div><div>Any guidance would be much appreciated, and thanks for your time,<br clear="all"><div><div class="gmail_signature"><div dir="ltr"><div><br></div><div>Brian Mehalic <br>NABCEP Certified Solar PV Installation Professional\u2122 R031508-59<div><br></div><div><div>PV Curriculum Developer and Instructor<div>Solar Energy International<br><a href="http://www.solarenergy.org" target="_blank">http://www.solarenergy.org</a></div></div></div></div></div></div></div>