<html><head><meta http-equiv="Content-Type" content="text/html charset=iso-8859-1"></head><body style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space;" class="">HI Drake,<div class=""><br class=""></div><div class="">What sort of multi stage relay control are you using?</div><div class=""><br class=""></div><div class="">jay</div><div class="">peltz power</div><div class=""><br class=""></div><div class=""><br class=""><div><blockquote type="cite" class=""><div class="">On Aug 21, 2015, at 5:27 AM, Drake &lt;<a href="mailto:drake.chamberlin@redwoodalliance.org" class="">drake.chamberlin@redwoodalliance.org</a>&gt; wrote:</div><br class="Apple-interchange-newline"><div class="">
<div class="">
I'm considering an AC coupled system with Enphase that would shed
inverters a group at a time, ending up with one still charging until the
set point is reached. <br class=""><br class="">
At 12:56 AM 8/21/2015, you wrote:<br class="">
<blockquote type="cite" class="cite" cite="">Hi Folks;<br class="">
<br class="">
I've done more research on the whole AC coupled issue, and one flaw I
found with both the Sunny Island and the Radian is that they can't really
do a full 3 stage charge for the batteries in off grid mode.<br class="">
They detect that the batteries are full and disconnect the AC coupled GT
inverters, but this is about as subtle as the very early charge
controllers, and amounts to 1 stage charging.&nbsp; This is fine for
temporary outages, and when the grid comes back, the batteries get a good
3 stage charge.&nbsp; But these folks are really wanting a design that
could be taken off grid permanently.&nbsp;&nbsp; Also as you my recall,
the GT PV system is Enphase, so we can't use the more sophisticated
controls that SMA offers for the Sunny boys. <br class="">
I hate to say it, but I might be back to a diversion load with PWM
controller.&nbsp; Not elegant, but we could get 3 stage charging.&nbsp;
<br class="">
Every time I look at AC coupled setups, I just want to start over with
charge controllers. <br class=""><br class="">
<pre class="">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre><font face="Courier New, Courier" class=""></font>On 8/17/2015
9:39 PM, Mac Lewis wrote:<br class="">
<blockquote type="cite" class="cite" cite="">Hi Ray, <br class=""><br class="">
With that size grid-tied system, you would want to use a battery based
inverter(s) near the (6.7/0.8) 8000W range.&nbsp; <br class=""><br class="">
The frequency shift of the Sunny Islands will work with kicking out the
enphase inverters but you wouldn't get the same output ramping that it
would offer if it was a Sunny Boy grid-tied inverter.&nbsp; The Sunny
Island can effectively solve your generator backfeeding because there is
a reverse current sensor that will disconnect the AC input at whatever
level you want, 50 mA is default I think.&nbsp; You may need to give the
Sunny Island generator start control for this however.<br class=""><br class="">
You can read about it here on page 137.<br class=""><br class="">
<a href="http://files.sma.de/dl/15216/SI4548-6048-US-BE-en-21W.pdf" class="">
http://files.sma.de/dl/15216/SI4548-6048-US-BE-en-21W.pdf</a><br class=""><br class="">
You'll need to give the Sunny Island a digital signal that tell it
whether its connected to a generator or a grid as outlined in the manual.
<br class=""><br class="">
&nbsp;This is where the Radian is nice because it has two AC Input
terminals.<br class=""><br class="">
Sounds like an interesting project.<br class=""><br class="">
Good Luck.<br class=""><br class="">
<br class=""><br class="">
<br class="">
On Mon, Aug 17, 2015 at 8:36 PM, Jerry Shafer
&lt;<a href="mailto:jerrysgarage01@gmail.com" class="">jerrysgarage01@gmail.com</a>
&gt; wrote:<br class="">

<dl class=""><br class="">

<dd class="">I cant see this working well without some battery based
inverter<font color="#888888" class=""><br class="">

</font></dd><dd class=""><font color="#888888" class="">Jerry<br class="">
</font>
</dd><dd class="">On Aug 17, 2015 10:10 AM, "Ray Walters"
&lt;<a href="mailto:ray@solarray.com" class="">ray@solarray.com</a>&gt;
wrote:<br class="">

<dl class="">
<dd class="">HI Esteemed Wrenches:<br class=""><br class="">

</dd><dd class="">I am consulting on a system I have never seen, that consists of a
6.7Kw Enphase roof mounted system, and 2 backup generators.&nbsp; Each
generator has an automatic 200 amp transfer switch to back up its own 200
amp panel.&nbsp; Both 200 amp panels are fed by a 400 amp service from
the grid.<br class="">

</dd><dd class="">The Enphase PV backfeeds a subpanel in another building which then is
fed by a 2 pole 60 amp breaker in one of the 200 amp panels.<br class="">

</dd><dd class="">Currently they are having issues with the generators kicking out
because of the Enphase inverters.&nbsp; That part I understand: you can't
backfeed a generator, or its voltage regulation freaks out.<br class=""><br class="">

</dd><dd class="">Now we get to the fun part: they want to create a third critical load
subpanel with loads selected from both 200 amp panels to be powered by
batteries and an inverter.<br class="">

</dd><dd class="">I am considering the Sunny Island since it makes the most sense with
its ability to signal the Enphase inverters to shut off when the
batteries are full.&nbsp; I also see this as a partial solution to the
generator issue, since normally the Enphase will be connected to the
output side of the Sunny Island.&nbsp; However, when the generator is
used to charge, we will be back to directly coupling the generator output
to the Enphase.<br class="">
<br class="">

</dd><dd class="">Here are some possible solutions I'm considering:<br class="">

</dd><dd class="">1) Use a separate charger for the generator so that it will only feed
DC to the batteries, and not be AC coupled.<br class="">

</dd><dd class="">2) convert the PV back to DC with charge controllers, but that would
involve ditching and adding another conduit run between buildings.<br class="">

</dd><dd class="">3)&nbsp; Put the Enphase PV on a relay that would disconnect the PV
when charging with the generator.<br class="">

</dd><dd class="">4) Something I haven't thought of that one of you clever folks can
suggest......<br class=""><br class="">

</dd><dd class="">As always, thanks in advance for all you responses,<br class=""><br class="">

</dd><dd class="">-- <br class="">

</dd><dd class="">R.Ray Walters<br class="">

</dd><dd class="">CTO, Solarray, Inc<br class="">

</dd><dd class="">Nabcep Certified PV Installer,<br class="">

</dd><dd class="">Licensed Master Electrician<br class="">

</dd><dd class="">Solar Design Engineer<br class="">

</dd><dd class=""><a href="tel:303%20505-8760" class="">303 505-8760</a><br class=""><br class="">

</dd><dd class="">______</dd></dl></dd></dl></blockquote></blockquote></div><br class=""></div></blockquote></div><br class=""></div></body></html>