<html><head><meta http-equiv="Content-Type" content="text/html; charset=UTF-8"></head><body ><div>Wrenches</div><div>The ability for proper charging has always been an issue way back befor ac coupling was a thing. Its near an uncontrolled charge and if you tank the batteries and shut down that's it no charging from the ac coupling component&nbsp;</div><div>Jerry</div><div><br></div><div><br></div><div><div style="font-size:9px;color:#575757">Sent via the Samsung Galaxy S\u2122 III, an AT&amp;T 4G LTE smartphone</div></div><br><br><div>-------- Original message --------</div><div>From: Ray Walters <ray@solarray.com> </div><div>Date:08/20/2015  6:56 PM  (GMT-10:00) </div><div>To: RE-wrenches <re-wrenches@lists.re-wrenches.org> </div><div>Subject: Re: [RE-wrenches] AC Coupled with Generator </div><div><br></div>
    Hi Folks;<br>
    <br>
    I've done more research on the whole AC coupled issue, and one flaw
    I found with both the Sunny Island and the Radian is that they can't
    really do a full 3 stage charge for the batteries in off grid mode.<br>
    They detect that the batteries are full and disconnect the AC
    coupled GT inverters, but this is about as subtle as the very early
    charge controllers, and amounts to 1 stage charging.&nbsp; This is fine
    for temporary outages, and when the grid comes back, the batteries
    get a good 3 stage charge.&nbsp; But these folks are really wanting a
    design that could be taken off grid permanently.&nbsp;&nbsp; Also as you my
    recall, the GT PV system is Enphase, so we can't use the more
    sophisticated controls that SMA offers for the Sunny boys. <br>
    I hate to say it, but I might be back to a diversion load with PWM
    controller.&nbsp; Not elegant, but we could get 3 stage charging.&nbsp; <br>
    Every time I look at AC coupled setups, I just want to start over
    with charge controllers. <br>
    <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
    <div class="moz-cite-prefix">On 8/17/2015 9:39 PM, Mac Lewis wrote:<br>
    </div>
    <blockquote cite="mid:CAOABG4_E0OWuKThmiVmhtvkfY0XDHO7Kf3+A8-=EKVvPn_ZX0g@mail.gmail.com" type="cite">
      <div dir="ltr">Hi Ray,
        <div><br>
        </div>
        <div>With that size grid-tied system, you would want to use a
          battery based inverter(s) near the (6.7/0.8) 8000W range. &nbsp;</div>
        <div><br>
        </div>
        <div>The frequency shift of the Sunny Islands will work with
          kicking out the enphase inverters but you wouldn't get the
          same output ramping that it would offer if it was a Sunny Boy
          grid-tied inverter.&nbsp; The Sunny Island can effectively solve
          your generator backfeeding because there is a reverse current
          sensor that will disconnect the AC input at whatever level you
          want, 50 mA is default I think.&nbsp; You may need to give the
          Sunny Island generator start control for this however.</div>
        <div><br>
        </div>
        <div>You can read about it here on page 137.</div>
        <div><br>
        </div>
        <div><a moz-do-not-send="true" href="http://files.sma.de/dl/15216/SI4548-6048-US-BE-en-21W.pdf">http://files.sma.de/dl/15216/SI4548-6048-US-BE-en-21W.pdf</a><br>
        </div>
        <div><br>
        </div>
        <div>You'll need to give the Sunny Island a digital signal that
          tell it whether its connected to a generator or a grid as
          outlined in the manual.&nbsp;</div>
        <div><br>
        </div>
        <div>&nbsp;This is where the Radian is nice because it has two AC
          Input terminals.</div>
        <div><br>
        </div>
        <div>Sounds like an interesting project.</div>
        <div><br>
        </div>
        <div>Good Luck.</div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
      </div>
      <div class="gmail_extra"><br>
        <div class="gmail_quote">On Mon, Aug 17, 2015 at 8:36 PM, Jerry
          Shafer <span dir="ltr">&lt;<a moz-do-not-send="true" href="mailto:jerrysgarage01@gmail.com" target="_blank">jerrysgarage01@gmail.com</a>&gt;</span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <p dir="ltr">I cant see this working well without some
              battery based inverter<span class="HOEnZb"><font color="#888888"><br>
                  Jerry</font></span></p>
            <div class="HOEnZb">
              <div class="h5">
                <div class="gmail_quote">On Aug 17, 2015 10:10 AM, "Ray
                  Walters" &lt;<a moz-do-not-send="true" href="mailto:ray@solarray.com" target="_blank">ray@solarray.com</a>&gt;
                  wrote:<br type="attribution">
                  <blockquote class="gmail_quote" style="margin:0 0 0
                    .8ex;border-left:1px #ccc solid;padding-left:1ex">HI
                    Esteemed Wrenches:<br>
                    <br>
                    I am consulting on a system I have never seen, that
                    consists of a 6.7Kw Enphase roof mounted system, and
                    2 backup generators.&nbsp; Each generator has an
                    automatic 200 amp transfer switch to back up its own
                    200 amp panel.&nbsp; Both 200 amp panels are fed by a 400
                    amp service from the grid.<br>
                    The Enphase PV backfeeds a subpanel in another
                    building which then is fed by a 2 pole 60 amp
                    breaker in one of the 200 amp panels.<br>
                    Currently they are having issues with the generators
                    kicking out because of the Enphase inverters.&nbsp; That
                    part I understand: you can't backfeed a generator,
                    or its voltage regulation freaks out.<br>
                    <br>
                    Now we get to the fun part: they want to create a
                    third critical load subpanel with loads selected
                    from both 200 amp panels to be powered by batteries
                    and an inverter.<br>
                    I am considering the Sunny Island since it makes the
                    most sense with its ability to signal the Enphase
                    inverters to shut off when the batteries are full.&nbsp;
                    I also see this as a partial solution to the
                    generator issue, since normally the Enphase will be
                    connected to the output side of the Sunny Island.&nbsp;
                    However, when the generator is used to charge, we
                    will be back to directly coupling the generator
                    output to the Enphase.<br>
                    <br>
                    Here are some possible solutions I'm considering:<br>
                    1) Use a separate charger for the generator so that
                    it will only feed DC to the batteries, and not be AC
                    coupled.<br>
                    2) convert the PV back to DC with charge
                    controllers, but that would involve ditching and
                    adding another conduit run between buildings.<br>
                    3)&nbsp; Put the Enphase PV on a relay that would
                    disconnect the PV when charging with the generator.<br>
                    4) Something I haven't thought of that one of you
                    clever folks can suggest......<br>
                    <br>
                    As always, thanks in advance for all you responses,<br>
                    <br>
                    -- <br>
                    R.Ray Walters<br>
                    CTO, Solarray, Inc<br>
                    Nabcep Certified PV Installer,<br>
                    Licensed Master Electrician<br>
                    Solar Design Engineer<br>
                    <a moz-do-not-send="true" href="tel:303%20505-8760" value="+13035058760" target="_blank">303 505-8760</a><br>
                    <br>
                    _______________________________________________<br>
                    List sponsored by Redwood Alliance<br>
                    <br>
                    List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
                    <br>
                    Change listserver email address &amp; settings:<br>
                    <a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                    <br>
                    List-Archive: <a moz-do-not-send="true" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                    <br>
                    List rules &amp; etiquette:<br>
                    <a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
                    <br>
                    Check out or update participant bios:<br>
                    <a moz-do-not-send="true" href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
                    <br>
                  </blockquote>
                </div>
              </div>
            </div>
            <br>
            _______________________________________________<br>
            List sponsored by Redwood Alliance<br>
            <br>
            List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change listserver email address &amp; settings:<br>
            <a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a moz-do-not-send="true" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
            <br>
            List rules &amp; etiquette:<br>
            <a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out or update participant bios:<br>
            <a moz-do-not-send="true" href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
            <br>
            <br>
          </blockquote>
        </div>
        <br>
        <br clear="all">
        <div><br>
        </div>
        -- <br>
        <div class="gmail_signature">
          <div><br>
          </div>
          <div><font color="#305A78" face="'times new roman', serif"><br>
            </font></div>
          <div><br>
          </div>
          Mac Lewis<br>
          <br>
          <span style="font-family:'Times New
            Roman';font-size:medium;color:rgb(255,153,0)"><b><font face="Arial, Helvetica, sans-serif" size="3">
                <p align="left"><font color="#000000" face="Verdana,
                    Arial, Helvetica, sans-serif"><span style="font-size:small"><span style="font-family:arial;font-weight:normal;color:rgb(48,90,120)"><font face="'times new roman', serif">"Yo solo sé
                          que no sé nada."&nbsp;</font><span style="font-weight:700;color:rgb(104,104,104)"><font face="'times new roman', serif">-Sócrates</font></span></span></span></font></p>
              </font></b></span></div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  

</body>