    The 0.8 PF is a design criteria by which the generator manufacturer
    specs the capacity of the genset. The genset has to provide the
    reactive power not just the real component, so most use the 0.8PF as
    a reasonable spec. In your case with the Magnum charger presenting a
    1.0PF, the genset output should match that value.<br>
    <br>
    Regards, Gary<br>
    <br>
    <div class="moz-cite-prefix">On 7/14/15 8:45 PM, Mac Lewis wrote:<br>
    </div>
    <blockquote
cite="mid:CAOABG48UBPys79BCOSQ3ommaiQ0R7JoEHYSAAH-68-KLwgc3YQ@mail.gmail.com"
      type="cite">
      <div dir="ltr">Wrenches,
        <div><br>
        </div>
        <div>Thanks for these productive responses.  I will attempt to
          get an instrument that can examine the current waveform.  I
          want to understand power factor possibility a bit more.  I
          neglected to mention that during the oscilloscope tests, we
          turned off the AC output of the inverter so the only loading
          of the generator would have been the charger on the Magnum. 
          The Magnum has power factor corrected charger, so I am
          assuming that when I measure the power factor, it should be
          near unity.</div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div>I was talking to an electrical engineering friend about it
          and he said that most generators have a pf of about 0.8.  This
          confuses me because I thought current (and hence power factor)
          is determined by the load.  How does the power source
          influence power factor (assuming we aren't near its current
          production limit)?  </div>
        <div><br>
        </div>
        <div>Thanks in advance</div>
      </div>
      <div class="gmail_extra"><br>
        <div class="gmail_quote">On Tue, Jul 14, 2015 at 10:43 AM, <span
            dir="ltr">&lt;<a moz-do-not-send="true"
              href="mailto:Jarmo.Venalainen@schneider-electric.com"
              target="_blank">Jarmo.Venalainen@schneider-electric.com</a>&gt;</span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex"><font
              face="sans-serif" size="2">Hi:</font>
            <br>
            <br>
            <font face="sans-serif" size="2">I'm assuming the
              oscilloscope waveforms
              are voltages.  If so, they don't look bad.</font>
            <br>
            <br>
            <font face="sans-serif" size="2">I would get a current for
              the oscilloscope
              and and measure the L1, L2 and Neutral currents.  That
              should reveal
              what is going on.</font>
            <br>
            <br>
            <font face="sans-serif" size="2">JARMO <br>
            </font><font color="#008000" size="3">_____________________________________________________________________________________</font><font
              size="3">
              <br>
            </font><font face="Arial" size="1"><b><br>
                Jarmo Venalainen</b>  |  </font><font color="#008000"
              face="Arial" size="1"><b>
                Schneider Electric </b></font><font face="Arial"
              size="1"><b>  |  Xantrex
                Brand</b>  |   <b>CANADA</b>  |   <b>Sales Application
                Engineer</b> <b><br>
                Phone:</b> <a moz-do-not-send="true"
                href="tel:%2B604-422-2528" value="+6044222528"
                target="_blank">+604-422-2528</a>  |   <b>Tech Support:</b>
              <a moz-do-not-send="true" href="tel:800-670-0707"
                value="+18006700707" target="_blank">800-670-0707</a>
               |   <b>Mobile:</b> <a moz-do-not-send="true"
                href="tel:%2B604-505-0291" value="+6045050291"
                target="_blank">+604-505-0291</a> <b><br>
                Email:</b> </font><a moz-do-not-send="true"
              href="mailto:jarmo.venalainen@schneider-electric.com"
              target="_blank"><font color="blue" face="Arial" size="1"><u>jarmo.venalainen@schneider-electric.com</u></font></a><font
              face="Arial" size="1">
               |   <b>Site:</b></font><a moz-do-not-send="true"
              href="http://www.xantrex.com/" target="_blank"><font
                color="blue" face="Arial" size="1"><u>
                  www.Xantrex.com</u></font></a><font face="Arial"
              size="1">  |  
              <b>Address:</b> 3700 Gilmore Way, Burnaby, BC V5G4M1 <br>
            </font>
            <table>
              <tbody>
                <tr>
                  <td colspan="4"><a moz-do-not-send="true"
                      href="http://www.xantrexrebate.com/"
                      target="_blank"><img
                        src="cid:part7.09000006.04020105@IcarusSolarServices.com"
                        width="1" height="1"></a>
                  </td>
                </tr>
                <tr>
                  <td><a moz-do-not-send="true"
                      href="http://www.xantrex.com/" target="_blank"><img
src="cid:part9.01040404.04080105@IcarusSolarServices.com"></a>
                  </td>
                  <td><a moz-do-not-send="true"
                      href="https://www.facebook.com/Xantrex"
                      target="_blank"><img
                        src="cid:part11.03060103.07070204@IcarusSolarServices.com"></a>
                  </td>
                  <td><a moz-do-not-send="true"
                      href="https://twitter.com/Xantrex" target="_blank"><img
src="cid:part13.02060407.08010606@IcarusSolarServices.com"></a>
                  </td>
                  <td><a moz-do-not-send="true"
                      href="https://twitter.com/Xantrex" target="_blank"><img
src="cid:part15.02050200.07070903@IcarusSolarServices.com"></a></td>
                </tr>
              </tbody>
            </table>
            <span class="">
              <br>
              <br>
              <font color="#00a000" face="Arial" size="1"><br>
                *** Please consider the environment before printing this
                e-mail</font><font size="3"><br>
              </font>
              <br>
              <br>
              <br>
            </span>
            <table width="100%">
              <tbody>
                <tr valign="top">
                  <td><font color="#5f5f5f" face="sans-serif" size="1">From:</font>
                  </td>
                  <td><font face="sans-serif" size="1">Mac Lewis &lt;<a
                        moz-do-not-send="true"
                        href="mailto:maclewis1@gmail.com"
                        target="_blank">maclewis1@gmail.com</a>&gt;</font>
                  </td>
                </tr>
                <tr valign="top">
                  <td><font color="#5f5f5f" face="sans-serif" size="1">To:</font>
                  </td>
                  <td><font face="sans-serif" size="1">RE-wrenches &lt;<a
                        moz-do-not-send="true"
                        href="mailto:re-wrenches@lists.re-wrenches.org"
                        target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt;,
                    </font>
                  </td>
                </tr>
                <tr valign="top">
                  <td><font color="#5f5f5f" face="sans-serif" size="1">Date:</font>
                  </td>
                  <td><font face="sans-serif" size="1">07/14/2015 06:01
                      AM</font>
                  </td>
                </tr>
                <tr valign="top">
                  <td><font color="#5f5f5f" face="sans-serif" size="1">Subject:</font>
                  </td>
                  <td><font face="sans-serif" size="1">Re: [RE-wrenches]
                      Generac QT series</font>
                  </td>
                </tr>
                <tr valign="top">
                  <td><font color="#5f5f5f" face="sans-serif" size="1">Sent
                      by:</font>
                  </td>
                  <td><font face="sans-serif" size="1">"RE-wrenches"
                      &lt;<a moz-do-not-send="true"
                        href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
                        target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>&gt;</font></td>
                </tr>
              </tbody>
            </table>
            <div>
              <div class="h5">
                <br>
                <hr noshade="noshade">
                <br>
                <br>
                <br>
                <font size="3">Hello wrenches,</font>
                <br>
                <br>
                <font size="3">Last December I posted about a Magnum
                  4448 and a Generac
                  22 kW generator that aren't working well together. 
                  The symptom was
                  that the Magnum transformer would overheat very
                  quickly, even at very low
                  charge rates (&lt;2A DC).  We have verified 120/240
                  VAC operation
                  of the generator.</font>
                <br>
                <br>
                <font size="3">We were able to get up to the site with
                  an oscilloscope
                  and see if we could find anything out.  I've attached
                  some photos
                  of the oscilloscope output.  I don't have anything to
                  compare it to,
                  so I'd like to see if anyone has some insight into why
                  this may be occurring.</font>
                <br>
                <font size="3">The 4 photos are as follows (all photos
                  L1-L2):</font>
                <br>
                <font size="3">1.  Generator Waveform No Load: Unloaded
                  Generator
                  Voltage Waveform</font>
                <br>
                <font size="3">2.  Charger 1st Connected: AC Input
                  Voltage waveform
                  immediately after charger connects</font>
                <br>
                <font size="3">3.  Steady State Operation Editted: AC
                  Input Voltage
                  waveform after about 10 seconds, this waveform
                  continues until transformer
                  overheats (in about 2 minutes)  Note the disturbances.</font>
                <br>
                <font size="3">4.  Zoomed In Ripple: Closer view of the
                  disturbances
                  noted in #3.</font>
                <br>
                <br>
                <font size="3">We have tried replacing the Magnum with
                  an identical unit,
                  and we had the same issue.  We also tried a Honda 6500
                  with atrocious
                  voltage and frequency regulation and it worked fine
                  with the Magnum. 
                  Since I did not sell him the generator, the easy out
                  is to replace the
                  generator.  However, there is some custom exhaust duct
                  work and it
                  will be much more expensive to replace the generator
                  than to try a new
                  inverter.  </font>
                <br>
                <br>
                <font size="3">I think that over all it is preferable
                  for the client
                  to replace the inverter/charger with a different
                  brand.  I have no
                  problem doing that except that I'd like to be
                  relatively sure that this
                  is anomalous behavior between the Magnum and the
                  Generac and not a generator
                  issue.  What are the chances that I'd have the same
                  issue with a different
                  inverter?  What might cause this?  All voltage and
                  frequency
                  measurements have been perfect with the Generac.</font>
                <br>
                <br>
                <font size="3">Your comments or thoughts are
                  appreciated.</font>
                <br>
                <br>
                <font size="3">Thanks</font>
                <br>
                <br>
                <br>
                <br>
                <font size="3">On Tue, Dec 16, 2014 at 11:15 AM, RE
                  Ellison &lt;</font><a moz-do-not-send="true"
                  href="mailto:reellison@gmail.com" target="_blank"><font
                    color="blue" size="3"><u>reellison@gmail.com</u></font></a><font
                  size="3">&gt;
                  wrote:</font>
                <br>
                <font size="3">If memory serves me correctly and this is
                  the off grid
                  Generac they are available as a 120 volt and it takes
                  a new breaker and
                  rewiring to get 120 / 240 out of them</font>
                <br>
                <br>
                <font size="3">I run into this in the past they actually
                  had it wired
                  for 240 into a balancing transformer to feed 120 into
                  the inverter</font>
                <br>
                <br>
                <font size="3">We could've just left it at 120 volt </font>
                <br>
                <br>
                <font size="3">Later,</font>
                <br>
                <font size="3">Bob ellison <br>
                  <br>
                </font>
                <br>
                <font size="3">Bob Ellison</font>
                <br>
                <font size="3"><br>
                  On Dec 16, 2014, at 11:33 AM, "Baxter, Gary" &lt;</font><a
                  moz-do-not-send="true"
                  href="mailto:gbaxter@sensata.com" target="_blank"><font
                    color="blue" size="3"><u>gbaxter@sensata.com</u></font></a><font
                  size="3">&gt;
                  wrote:<br>
                </font>
                <br>
                <font size="3">Hi Mac,</font>
                <br>
                <font size="3">Jay just had the same issue and it was
                  120v from the gen
                  instead of 120/240. The inverter was charging using
                  half the windings causing
                  it to Overtemp.</font>
                <br>
                <br>
                <font size="3">Check the 60A breakers on the side of the
                  inverter. Also
                  make sure to remove the wires from the input terminal
                  block before measuring
                  voltage as the inverter will make 120v look like
                  120/240v at the terminals.</font>
                <br>
                <br>
                <font size="3">If the generator is 3 Phase it won't work
                  with this inverter
                  unless you only use one leg. This will work but you
                  will need to turn the
                  charge rate to 50% in order to prevent Overtemp.
                  Sometimes it works as
                  high as 70%.<br>
                  <br>
                  Gary Baxter </font>
                <br>
                <font size="3">Product Manager</font>
                <br>
                <font size="3">Magnum/Dimensions </font>
                <br>
                <font size="3"><br>
                  On Dec 15, 2014, at 12:12 PM, Mac Lewis &lt;</font><a
                  moz-do-not-send="true"
                  href="mailto:maclewis1@gmail.com" target="_blank"><font
                    color="blue" size="3"><u>maclewis1@gmail.com</u></font></a><font
                  size="3">&gt;
                  wrote:<br>
                </font>
              </div>
            </div>
            <p><font size="3">Hi jarmo,</font>
            </p>
            <div>
              <div class="h5"><font size="3">We have verified this is
                  split phase 120/240. My multimeter
                  gets 120 L-N and 240 L-L.</font>
              </div>
            </div>
            <p><font size="3">Thanks</font>
            </p>
            <p><font size="3">On Dec 15, 2014 10:25 AM, &lt;</font><a
                moz-do-not-send="true"
                href="mailto:Jarmo.Venalainen@schneider-electric.com"
                target="_blank"><font color="blue" size="3"><u>Jarmo.Venalainen@schneider-electric.com</u></font></a><font
                size="3">&gt;
                wrote:</font>
              <br>
              <font face="sans-serif" size="3">Hi:</font><font size="3">
                <br>
              </font><font face="sans-serif" size="3"><br>
                The Generac QT02224GNAX ships as a three-phase 120/208
                VAC.  I believe
                the Magnum is a 120/240 VAC.</font><font size="3"> <br>
              </font><font face="sans-serif" size="3"><br>
                JARMO</font><font color="#008000" size="3"><br>
_____________________________________________________________________________________</font><font
                size="3">
              </font><font face="Arial" size="1"><b><br>
                  <br>
                  Jarmo Venalainen</b>  |  </font><font color="#008000"
                face="Arial" size="1"><b>
                  Schneider Electric </b></font><font face="Arial"
                size="1"><b>  |  Solar
                  Business</b>  |   <b>CANADA</b>  |   <b>Training
                  &amp;
                  Development Specialist - Senior</b> <b><br>
                  Phone:</b> </font><a moz-do-not-send="true"
                href="tel:%2B604-422-2528" target="_blank"><font
                  color="blue" face="Arial" size="1"><u>+604-422-2528</u></font></a><font
                face="Arial" size="1">
                 |   <b>Fax:</b> </font><a moz-do-not-send="true"
                href="tel:%2B604-420-1591" target="_blank"><font
                  color="blue" face="Arial" size="1"><u>+604-420-1591</u></font></a><font
                face="Arial" size="1">
                 |   <b>Mobile:</b> </font><a moz-do-not-send="true"
                href="tel:%2B604-505-0291" target="_blank"><font
                  color="blue" face="Arial" size="1"><u>+604-505-0291</u></font></a><font
                face="Arial" size="1">
                <b><br>
                  Email:</b> </font><a moz-do-not-send="true"
                href="mailto:jarmo.venalainen@schneider-electric.com"
                target="_blank"><font color="blue" face="Arial" size="1"><u>jarmo.venalainen@schneider-electric.com</u></font></a><font
                face="Arial" size="1">
                 |   <b>Site:</b></font><a moz-do-not-send="true"
                href="http://www.sesolar.com/" target="_blank"><font
                  color="blue" face="Arial" size="1"><u>
                    www.SEsolar.com</u></font></a><font face="Arial"
                size="1">  |  
                <b>Address:</b> 3700 Gilmore Way, Burnaby, BC V5G4M1 </font><font
                color="blue" face="Arial" size="1"><u><br>
                </u></font><font color="blue" size="3"><u><br>
                </u></font><a moz-do-not-send="true"
                href="http://%20www.sesolar.com/" target="_blank"><font
                  color="blue" size="3"><u>&lt;mime-attachment.jpg&gt;</u></font></a><font
                face="Arial" size="1"><br>
                *** Please consider the environment before printing this
                e-mail</font><font size="3">
                <br>
                <br>
                <br>
              </font>
            </p>
            <table width="100%">
              <tbody>
                <tr valign="top">
                  <td width="13%"><font color="#5f5f5f"
                      face="sans-serif" size="1">From:</font><font
                      size="3">
                    </font>
                  </td>
                  <td width="86%"><font face="sans-serif" size="1">Mac
                      Lewis &lt;</font><a moz-do-not-send="true"
                      href="mailto:maclewis1@gmail.com" target="_blank"><font
                        color="blue" face="sans-serif" size="1"><u>maclewis1@gmail.com</u></font></a><font
                      face="sans-serif" size="1">&gt;</font><font
                      size="3">
                    </font>
                  </td>
                </tr>
                <tr valign="top">
                  <td><font color="#5f5f5f" face="sans-serif" size="1">To:</font><font
                      size="3">
                    </font>
                  </td>
                  <td><font face="sans-serif" size="1">RE-wrenches &lt;</font><a
                      moz-do-not-send="true"
                      href="mailto:re-wrenches@lists.re-wrenches.org"
                      target="_blank"><font color="blue"
                        face="sans-serif" size="1"><u>re-wrenches@lists.re-wrenches.org</u></font></a><font
                      face="sans-serif" size="1">&gt;,
                    </font>
                  </td>
                </tr>
                <tr valign="top">
                  <td><font color="#5f5f5f" face="sans-serif" size="1">Date:</font><font
                      size="3">
                    </font>
                  </td>
                  <td><font face="sans-serif" size="1">12/15/2014 05:52
                      AM</font><font size="3">
                    </font>
                  </td>
                </tr>
                <tr valign="top">
                  <td><font color="#5f5f5f" face="sans-serif" size="1">Subject:</font><font
                      size="3">
                    </font>
                  </td>
                  <td><font face="sans-serif" size="1">[RE-wrenches]
                      Generac QT series</font><font size="3">
                    </font>
                  </td>
                </tr>
                <tr valign="top">
                  <td><font color="#5f5f5f" face="sans-serif" size="1">Sent
                      by:</font><font size="3">
                    </font>
                  </td>
                  <td><font face="sans-serif" size="1">"RE-wrenches"
                      &lt;</font><a moz-do-not-send="true"
                      href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
                      target="_blank"><font color="blue"
                        face="sans-serif" size="1"><u>re-wrenches-bounces@lists.re-wrenches.org</u></font></a><font
                      face="sans-serif" size="1">&gt;</font></td>
                </tr>
              </tbody>
            </table>
            <br>
            <font size="3"><br>
            </font>
            <hr noshade="noshade"><font size="3"><br>
              <br>
              <br>
              Hello wrenches, <br>
              <br>
              We have a newly installed system that has a 22 kW Generac
              Quiet Source </font><font face="sans-serif" size="3">QT02224GNAX</font><font
              size="3"> with
              a Magnum MS4448-PAE.  When we start the generator, the
              Magnum's
              internal transformer temperature climbs to overtemp (240F)
              within a 2 minutes. 
              The batteries are being floated at the time, and haven't
              seen more than
              5A coming out of the generator.  We swapped the Magnum
              out, and we
              have the exact same issue.  We then got a job-site gas
              generator 6500W
              and ran it.  No problem whatsoever.  The problem appears
              to be
              with the Generac, or with the interaction between the
              Generac &amp; the
              Magnum.  I didn't have a scope on site but the fluke
              multimeter doesn't
              detect anything wrong with the voltage or frequency coming
              from the Generac.
              <br>
              <br>
              Has anyone had issues with the Generac QT?  Anyone paired
              one with
              a Magnum PAE before?  I want to get my scope up there and
              look for
              triplen harmonics, but I'm not sure how to filter these
              out.  Any
              references on how to effectively do that is appreciated. <br>
              <br>
              Thanks in advance <br>
              <br>
              -- <br>
              <br>
              <br>
              <br>
              Mac Lewis</font>
            <div>
              <div class="h5"><font color="#37605e" size="3">"Yo solo sé
                  que no sé nada." </font><font color="#5f5f5f" size="3">-Sócrates</font><font
                  size="3">
                </font>
              </div>
            </div>
            <div>
              <div class="h5"><font size="3"><br>
______________________________________________________________________<br>
                  This email has been scanned by the Symantec Email
                  Security.cloud service.<br>
______________________________________________________________________</font><tt><font
                    size="3">_______________________________________________<br>
                    List sponsored by Redwood Alliance<br>
                    <br>
                    List Address: </font></tt><a moz-do-not-send="true"
                  href="mailto:RE-wrenches@lists.re-wrenches.org"
                  target="_blank"><tt><font color="blue" size="3"><u>RE-wrenches@lists.re-wrenches.org</u></font></tt></a><tt><font
                    size="3"><br>
                    <br>
                    Change listserver email address &amp; settings:</font></tt><font
                  color="blue" size="3"><u><br>
                  </u></font><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                  target="_blank"><tt><font color="blue" size="3"><u>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</u></font></tt></a><tt><font
                    size="3"><br>
                    <br>
                    List-Archive: </font></tt><a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                  target="_blank"><tt><font color="blue" size="3"><u>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</u></font></tt></a><tt><font
                    size="3"><br>
                    <br>
                    List rules &amp; etiquette:</font></tt><font
                  color="blue" size="3"><u><br>
                  </u></font><a moz-do-not-send="true"
                  href="http://www.re-wrenches.org/etiquette.htm"
                  target="_blank"><tt><font color="blue" size="3"><u>www.re-wrenches.org/etiquette.htm</u></font></tt></a><tt><font
                    size="3"><br>
                    <br>
                    Check out or update participant bios:</font></tt><font
                  color="blue" size="3"><u><br>
                  </u></font><a moz-do-not-send="true"
                  href="http://www.members.re-wrenches.org/"
                  target="_blank"><tt><font color="blue" size="3"><u>www.members.re-wrenches.org</u></font></tt></a><tt><font
                    size="3"><br>
                  </font></tt>
              </div>
            </div>
            <div>
              <div class="h5"><font size="3"><br>
                  _______________________________________________<br>
                  List sponsored by Redwood Alliance<br>
                  <br>
                  List Address: </font><a moz-do-not-send="true"
                  href="mailto:RE-wrenches@lists.re-wrenches.org"
                  target="_blank"><font color="blue" size="3"><u>RE-wrenches@lists.re-wrenches.org</u></font></a><font
                  size="3"><br>
                  <br>
                  Change listserver email address &amp; settings:</font><font
                  color="blue" size="3"><u><br>
                  </u></font><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                  target="_blank"><font color="blue" size="3"><u>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</u></font></a><font
                  size="3"><br>
                  <br>
                  List-Archive: </font><a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                  target="_blank"><font color="blue" size="3"><u>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</u></font></a><font
                  size="3"><br>
                  <br>
                  List rules &amp; etiquette:</font><font color="blue"
                  size="3"><u><br>
                  </u></font><a moz-do-not-send="true"
                  href="http://www.re-wrenches.org/etiquette.htm"
                  target="_blank"><font color="blue" size="3"><u>www.re-wrenches.org/etiquette.htm</u></font></a><font
                  size="3"><br>
                  <br>
                  Check out or update participant bios:</font><font
                  color="blue" size="3"><u><br>
                  </u></font><a moz-do-not-send="true"
                  href="http://www.members.re-wrenches.org/"
                  target="_blank"><font color="blue" size="3"><u>www.members.re-wrenches.org</u></font></a><font
                  size="3"><br>
                  <br>
                </font>
                <br>
                <font size="3">_______________________________________________<br>
                  List sponsored by Redwood Alliance<br>
                  <br>
                  List Address: </font><a moz-do-not-send="true"
                  href="mailto:RE-wrenches@lists.re-wrenches.org"
                  target="_blank"><font color="blue" size="3"><u>RE-wrenches@lists.re-wrenches.org</u></font></a><font
                  size="3"><br>
                  <br>
                  Change listserver email address &amp; settings:</font><font
                  color="blue" size="3"><u><br>
                  </u></font><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                  target="_blank"><font color="blue" size="3"><u>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</u></font></a><font
                  size="3"><br>
                  <br>
                  List-Archive: </font><a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                  target="_blank"><font color="blue" size="3"><u>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</u></font></a><font
                  size="3"><br>
                  <br>
                  List rules &amp; etiquette:</font><font color="blue"
                  size="3"><u><br>
                  </u></font><a moz-do-not-send="true"
                  href="http://www.re-wrenches.org/etiquette.htm"
                  target="_blank"><font color="blue" size="3"><u>www.re-wrenches.org/etiquette.htm</u></font></a><font
                  size="3"><br>
                  <br>
                  Check out or update participant bios:</font><font
                  color="blue" size="3"><u><br>
                  </u></font><a moz-do-not-send="true"
                  href="http://www.members.re-wrenches.org/"
                  target="_blank"><font color="blue" size="3"><u>www.members.re-wrenches.org</u></font></a><font
                  size="3"><br>
                </font>
                <br>
                <font size="3">_______________________________________________<br>
                  List sponsored by Redwood Alliance<br>
                  <br>
                  List Address: </font><a moz-do-not-send="true"
                  href="mailto:RE-wrenches@lists.re-wrenches.org"
                  target="_blank"><font color="blue" size="3"><u>RE-wrenches@lists.re-wrenches.org</u></font></a><font
                  size="3"><br>
                  <br>
                  Change listserver email address &amp; settings:</font><font
                  color="blue" size="3"><u><br>
                  </u></font><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                  target="_blank"><font color="blue" size="3"><u>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</u></font></a><font
                  size="3"><br>
                  <br>
                  List-Archive: </font><a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                  target="_blank"><font color="blue" size="3"><u>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</u></font></a><font
                  size="3"><br>
                  <br>
                  List rules &amp; etiquette:</font><font color="blue"
                  size="3"><u><br>
                  </u></font><a moz-do-not-send="true"
                  href="http://www.re-wrenches.org/etiquette.htm"
                  target="_blank"><font color="blue" size="3"><u>www.re-wrenches.org/etiquette.htm</u></font></a><font
                  size="3"><br>
                  <br>
                  Check out or update participant bios:</font><font
                  color="blue" size="3"><u><br>
                  </u></font><a moz-do-not-send="true"
                  href="http://www.members.re-wrenches.org/"
                  target="_blank"><font color="blue" size="3"><u>www.members.re-wrenches.org</u></font></a><font
                  size="3"><br>
                </font>
                <br>
                <font size="3"><br>
                  _______________________________________________<br>
                  List sponsored by Redwood Alliance<br>
                  <br>
                  List Address: </font><a moz-do-not-send="true"
                  href="mailto:RE-wrenches@lists.re-wrenches.org"
                  target="_blank"><font color="blue" size="3"><u>RE-wrenches@lists.re-wrenches.org</u></font></a><font
                  size="3"><br>
                  <br>
                  Change listserver email address &amp; settings:</font><font
                  color="blue" size="3"><u><br>
                  </u></font><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                  target="_blank"><font color="blue" size="3"><u>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</u></font></a><font
                  size="3"><br>
                  <br>
                  List-Archive: </font><a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                  target="_blank"><font color="blue" size="3"><u>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</u></font></a><font
                  size="3"><br>
                  <br>
                  List rules &amp; etiquette:</font><font color="blue"
                  size="3"><u><br>
                  </u></font><a moz-do-not-send="true"
                  href="http://www.re-wrenches.org/etiquette.htm"
                  target="_blank"><font color="blue" size="3"><u>www.re-wrenches.org/etiquette.htm</u></font></a><font
                  size="3"><br>
                  <br>
                  Check out or update participant bios:</font><font
                  color="blue" size="3"><u><br>
                  </u></font><a moz-do-not-send="true"
                  href="http://www.members.re-wrenches.org/"
                  target="_blank"><font color="blue" size="3"><u>www.members.re-wrenches.org</u></font></a><font
                  size="3"><br>
                  <br>
                </font>
                <br>
                <font size="3"><br>
                </font>
                <br>
                <br>
                <font size="3">-- </font>
                <br>
                <br>
                <br>
                <br>
                <font size="3">Mac Lewis<br>
                </font>
              </div>
            </div>
            <div>
              <div class="h5"><font color="#37605e" size="2">"Yo solo sé
                  que no sé nada." </font><font color="#5f5f5f" size="2">-Sócrates</font>
              </div>
            </div>
            <div>
              <div class="h5"><font size="3"><br>
______________________________________________________________________<br>
                  This email has been scanned by the Symantec Email
                  Security.cloud service.<br>
                </font></div>
            </div>
            <font size="3">
              ______________________________________________________________________[attachment
"Generator
              Waveform No Load.jpg" deleted by Jarmo
              Venalainen/Canada/Schneider]
              [attachment "Charger 1st Connected.jpg" deleted by Jarmo
              Venalainen/Canada/Schneider]
              [attachment "Steady State Operation Editted.jpg" deleted
              by Jarmo
              Venalainen/Canada/Schneider] [attachment "Zoomed In
              Ripple.jpg"
              deleted by Jarmo Venalainen/Canada/Schneider] </font><tt><font
                size="2">_______________________________________________<span
                  class=""><br>
                  List sponsored by Redwood Alliance<br>
                  <br>
                  List Address: <a moz-do-not-send="true"
                    href="mailto:RE-wrenches@lists.re-wrenches.org"
                    target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
                  <br>
                  Change listserver email address &amp; settings:<br>
                </span></font></tt><span class=""><a
                moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                target="_blank"><tt><font size="2">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font
                  size="2"><br>
                  <br>
                  List-Archive: </font></tt><a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                target="_blank"><tt><font size="2">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</font></tt></a><tt><font
                  size="2"><br>
                  <br>
                  List rules &amp; etiquette:<br>
                </font></tt><a moz-do-not-send="true"
                href="http://www.re-wrenches.org/etiquette.htm"
                target="_blank"><tt><font size="2">www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font
                  size="2"><br>
                  <br>
                  Check out or update participant bios:<br>
                </font></tt><a moz-do-not-send="true"
                href="http://www.members.re-wrenches.org"
                target="_blank"><tt><font size="2">www.members.re-wrenches.org</font></tt></a><tt><font
                  size="2"><br>
                  <br>
                </font></tt>
              <p>
              </p>
            </span><br>
            _______________________________________________<br>
            List sponsored by Redwood Alliance<br>
            <br>
            List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change listserver email address &amp; settings:<br>
            <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
              rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
              rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
            <br>
            List rules &amp; etiquette:<br>
            <a moz-do-not-send="true"
              href="http://www.re-wrenches.org/etiquette.htm"
              rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out or update participant bios:<br>
            <a moz-do-not-send="true"
              href="http://www.members.re-wrenches.org" rel="noreferrer"
              target="_blank">www.members.re-wrenches.org</a><br>
            <br>
            <br>
          </blockquote>
        </div>
        <br>
        <br clear="all">
        <div><br>
        </div>
        -- <br>
        <div class="gmail_signature">
          <div><br>
          </div>
          <div><font color="#305A78" face="'times new roman', serif"><br>
            </font></div>
          <div><br>
          </div>
          Mac Lewis<br>
          <br>
          <span style="font-family:'Times New
            Roman';font-size:medium;color:rgb(255,153,0)"><b><font
                face="Arial, Helvetica, sans-serif" size="3">
                <p align="left"><font color="#000000" face="Verdana,
                    Arial, Helvetica, sans-serif"><span
                      style="font-size:small"><span
                        style="font-family:arial;font-weight:normal;color:rgb(48,90,120)"><font
                          face="'times new roman', serif">"Yo solo sé
                          que no sé nada." </font><span
                          style="font-weight:700;color:rgb(104,104,104)"><font
                            face="'times new roman', serif">-Sócrates</font></span></span></span></font></p>
              </font></b></span></div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>