<div dir="ltr">HI Luke,<div><br></div><div>To add here.  I&#39;m unclear if you have measured each string or the whole array at 71v.  </div><div>I would check each string for voc/isc.  </div><div><br></div><div>And then if they are consistent, I agree that putting 2 strings in series with a new controller might help out.  </div><div>You can try it with the MX-60 as you are at only 142v. If it works better then a new higher voltage CC would be required for winter higher voc.</div><div><br></div><div>Let us know what you find out.</div><div><br></div><div>jay</div><div><br></div><div><br></div><div class="gmail_extra">On 5/31/2015 11:55 AM, Luke Christy
      wrote:<br><div class="gmail_quote"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div bgcolor="#FFFFFF" text="#000000">
    <blockquote type="cite">
      <pre>Hello Off-Grid Wrenches,

I recently made a periodic maintenance visit to a residential off-grid system I take care of here in Southern CO, and discovered an interesting problem. 

This system has an array of 48x Uni-Solar PVL-68 laminate modules applied directly to standing-seam metal roofing. 

The data logging on the controller (Outback MX-60) indicated that the system was having trouble completing a charge cycle and going to float. Initially I assumed was due to heavy electrical use by the occupants (renters). After a little checking, I noticed that the module string voltage was only about 0.5V above the battery voltage! 
This was a cool late morning, with full sun, and the array was charging almost 2kW at 54.5V. The module strings were running at 55V. I&#39;ve noticed the module voltage being lower than I&#39;d like before, but it has never been this low. I suspect this is the real reason the system hasn&#39;t been able to complete a charge cycle.

By removing the loads I was able to get an open-circuit voltage of 71V, but that still seems pretty low. 

Has anyone else experienced a voltage degradation issue with the Uni-Solar laminate? What was the expected annual voltage degradation for this technology? 

These modules do have some age on them. The system was installed about 15 years ago (by a competent installer who is now retired). The system was installed before MPPT controllers were common, so I assume the modules are wired in strings of 4 for 48V nominal. 

Any experiences or opinions are appreciated.
Thanks in advance. 

-Luke


Luke Christy

  </pre></blockquote></div></blockquote></div><div class="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div>Jay Peltz<br>Peltz Power<br><a href="mailto:jay.peltz@gmail.com" target="_blank">jay.peltz@gmail.com</a></div></div></div></div></div>