<p dir="ltr">Why not a simple line side tap?<br></p>
<p dir="ltr">Roy Rakobitsch<br>
NABCEP Certified Small Wind Installer®<br>
NABCEP Certified Solar PV Installer®<br>
Certified Advanced Tower Climbing, Safety &amp; Rescue<br>
Wind/PV Design Engineer<br>
Windsine LLC<br>
631-514-4166<br>
<a href="http://www.windsine.org">www.windsine.org</a></p>
<div class="gmail_quote">On May 25, 2015 3:00 AM, &quot;frenergy&quot; &lt;<a href="mailto:frenergy@psln.com">frenergy@psln.com</a>&gt; wrote:<br type="attribution"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><u></u>





<div text="#000000" bgcolor="#ffffff">
<div>Wrenches,</div>
<div> </div>
<div>        Customer currently has a hacked up 
200 amp Sylvania meter/mains panel.  He also is averaging a load of 74 
KWhrs/day! which will require about 15  KW system size at this site.  
Obviously a system this size cannot backfeed the busses in the load 
center.  Because the exiting panel is a mess anyway, I&#39;m suggesting it gets 
changed out.</div>
<div> </div>
<div>        What sort of new 200 amp service 
would facilitate a clean supply side connection.  One thought is have 
separate Utility meter socket then a 12 X 12 J-box with a monster power 
distribution block in it and then a distribution panel (without the meter 
socket)...this being a way to insert a means to grid-tie between the meter 
and the 200 amp main breaker.  A little spendy but nothing like going to 
higher amp service to be able to load side connect.</div>
<div> </div>
<div>        A 400 amp panel is not an option 
as the existing 165&#39; of 3&quot; pvc underground conduit to the pole currently has 4/0 
alum.  The utility says it would have to be 4&quot; for the new cable and the 
cost $10K+ for the upgrade.</div>
<div> </div>
<div>        Other ideas??</div>
<div> </div>
<div>Thanks in advance</div>
<div> </div>
<div>Bill</div>
<div> </div>
<div>Feather River Solar Electric</div></div>
<br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div>