<font size=2 face="sans-serif">Hi:</font>
<br>
<br><font size=2 face="sans-serif">This link takes you to a site in Romania
so you (likely) wont be able to read the text, but &nbsp;it does have a
lot of good pictures.</font>
<br>
<br><font size=2 face="sans-serif">This installer has been using XW since
about 2007 and has a tons of experience. &nbsp;I like what he does with
the DC wiring/busbars. &nbsp;The breakers are in the box below the inverters
and charge controllers.</font>
<br>
<br><a href=http://customer.lpelectric.ro/doc/sibiu2/sibiu2_28kw_fotovoltaic.html><font size=2 color=blue face="sans-serif">http://customer.lpelectric.ro/doc/sibiu2/sibiu2_28kw_fotovoltaic.html</font></a>
<br>
<br><font size=2 face="sans-serif">JARMO<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Jarmo Venalainen</b> &nbsp;| &nbsp;</font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>&nbsp; | &nbsp;Solar
Business</b> &nbsp;| &nbsp; <b>CANADA</b> &nbsp;| &nbsp; <b>Training &amp;
Development Specialist - Senior</b> <b><br>
Phone:</b> +604-422-2528 &nbsp;| &nbsp; <b>Fax:</b> +604-420-1591 &nbsp;|
&nbsp; <b>Mobile:</b> +604-505-0291 <b><br>
Email:</b> </font><a href="mailto:jarmo.venalainen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>jarmo.venalainen@schneider-electric.com</u></font></a><font size=1 face="Arial">
&nbsp;| &nbsp; <b>Site:</b></font><a href=http://www.sesolar.com/ target=_blank><font size=1 color=blue face="Arial"><u>
www.SEsolar.com</u></font></a><font size=1 face="Arial"> &nbsp;| &nbsp;
<b>Address:</b> 3700 Gilmore Way, Burnaby, BC V5G4M1 <br>
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><a href="http:// www.sesolar.com/"><img src=cid:_2_0B72537C0B7426D40058668D88257DC2></a><font size=1 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=3>
<br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">drake.chamberlin@redwoodalliance.org</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">&quot;RE-wrenches&quot; &lt;re-wrenches@lists.re-wrenches.org&gt;,
</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">01/02/2015 05:18 PM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">Re: [RE-wrenches] wire sizing question</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">&quot;RE-wrenches&quot; &lt;re-wrenches-bounces@lists.re-wrenches.org&gt;</font></table>
<br>
<hr noshade>
<br>
<br>
<br><tt><font size=2>4/0 copper is good for a 24V, 4000 W inverter. What
is being used for<br>
multiple inverters?<br>
<br>
I've paralleled 4/0 into outback boxes using 2, 2&quot; PVC conduits. It
gets<br>
pretty messy trying to put 4 sets of 4/0s into enclosures and battery<br>
boxes (although I have worked on such systems). Does anyone have clean<br>
solutions for these systems?<br>
<br>
Thanks,<br>
<br>
Drake<br>
<br>
<br>
<br>
<br>
<br>
&gt; Some other things: &nbsp;If you keep the conduit less than 24&quot;
long, which is<br>
&gt; recommended anyway for main battery connections, the conduit fill<br>
&gt; requirements don't apply. (see exception: 310.15(B)3a2)<br>
&gt; Using table 310.15(B)16 yeilds 230 amps for 4/0 at 75 C. &nbsp;Then
240.6<br>
&gt; lists 250 amp as the next standard size of OCPD which is allowed to
be<br>
&gt; used by 240.4(B) &nbsp;So you can just justify 4/0.<br>
&gt; Further, many manufacturers (like Midnite) use the open air ampacity<br>
&gt; table: 310.15(B)17, since the cable is not &quot;in conduit&quot;
and 4/0 cable at<br>
&gt; 75 C is rated to 360 amps.<br>
&gt; The Free Air interpretation is not completely substantiated in the
code<br>
&gt; from my read of it though. &nbsp;Maybe someone more knowledgable could
cite<br>
&gt; the chapter and verse that defines when the free air rating can and<br>
&gt; cannot be used.<br>
&gt; Also remember those breakers are 100% duty cycle rated, and that the<br>
&gt; inverter usually can't run any where close to 250 amps continuously.<br>
&gt; Bottomline is we've been using 4/0 with 250 amp breakers for almost
20<br>
&gt; years, and I've never seen or heard of a problem.<br>
&gt;<br>
&gt; R.Ray Walters<br>
&gt; CTO, Solarray, Inc<br>
&gt; Nabcep Certified PV Installer,<br>
&gt; Licensed Master Electrician<br>
&gt; Solar Design Engineer<br>
&gt; 303 505-8760<br>
&gt;<br>
&gt; On 1/1/2015 7:23 PM, jay peltz wrote:<br>
&gt;&gt; Happy new year all.<br>
&gt;&gt;<br>
&gt;&gt; I have a question on wire sizing for the following.<br>
&gt;&gt;<br>
&gt;&gt; 250 amp breaker, in a UL enclosure ( say midnite or outback etc)<br>
&gt;&gt; conduit from battery box to enclosure<br>
&gt;&gt;<br>
&gt;&gt; I'm wondering how folks size this for ampacity not voltage drop.<br>
&gt;&gt;<br>
&gt;&gt; thanks<br>
&gt;&gt;<br>
&gt;&gt; jay<br>
&gt;&gt;<br>
&gt;&gt; peltz power<br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt; _______________________________________________<br>
&gt;&gt; List sponsored by Redwood Alliance<br>
&gt;&gt;<br>
&gt;&gt; List Address: RE-wrenches@lists.re-wrenches.org<br>
&gt;&gt;<br>
&gt;&gt; Change listserver email address &amp; settings:<br>
&gt;&gt; </font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
&gt;&gt;<br>
&gt;&gt; List-Archive:<br>
&gt;&gt; </font></tt><a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"><tt><font size=2>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</font></tt></a><tt><font size=2><br>
&gt;&gt;<br>
&gt;&gt; List rules &amp; etiquette:<br>
&gt;&gt; </font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
&gt;&gt;<br>
&gt;&gt; Check out or update participant bios:<br>
&gt;&gt; </font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;<br>
&gt; _______________________________________________<br>
&gt; List sponsored by Redwood Alliance<br>
&gt;<br>
&gt; List Address: RE-wrenches@lists.re-wrenches.org<br>
&gt;<br>
&gt; Change listserver email address &amp; settings:<br>
&gt; </font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
&gt;<br>
&gt; List-Archive:<br>
&gt; </font></tt><a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"><tt><font size=2>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</font></tt></a><tt><font size=2><br>
&gt;<br>
&gt; List rules &amp; etiquette:<br>
&gt; </font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
&gt;<br>
&gt; Check out or update participant bios:<br>
&gt; </font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
&gt;<br>
&gt;<br>
<br>
<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change listserver email address &amp; settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"><tt><font size=2>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</font></tt></a><tt><font size=2><br>
<br>
List rules &amp; etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out or update participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
<br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________<br>
</font></tt>
<br>
<br>