<div dir="ltr"><div class="gmail_default" style="font-family:trebuchet ms,sans-serif">I&#39;ll echo what Matt suggests about not relying on an inspector (electrical or plumbing) to &quot;catch&quot; this.  </div><div class="gmail_default" style="font-family:trebuchet ms,sans-serif"><br></div><div class="gmail_default" style="font-family:trebuchet ms,sans-serif">That doesn&#39;t make it a best practice and just because you can get away with it then you should be doing it.  </div><div class="gmail_default" style="font-family:trebuchet ms,sans-serif">Do your due diligence and find out what the Plumbing Code in your area requires AND run the idea/concept by an inspector (plumbing).  </div><div class="gmail_default" style="font-family:trebuchet ms,sans-serif">And again, just because the plumbing code may allow it, technically, it still doesn&#39;t make it a best practice method.</div><div class="gmail_default" style="font-family:trebuchet ms,sans-serif"><br></div><div class="gmail_default" style="font-family:trebuchet ms,sans-serif">I had a plumbing inspector get back to me today and he cited a plumbing code 2.5.6.5 Article 5 (Alberta Plumbing Code, I assume), which basically says the sewer vent must be high enough to prevent any run-off from entering the vent <u>however it cannot be less than 150mm (6 inches)</u>.</div><div class="gmail_default" style="font-family:trebuchet ms,sans-serif">This means we could not install mods over a sewer vent using our typical racking system (on asphalt shingles) which only gets the back of the module 4 to maybe 4-1/2&quot; off the roof.  And if we did install a taller L-foot or stand-off that would give us say an inch or even 3 inches of clearance, then you have the potential issue of condensation freezing and building up on the back of the module in the winter and potentially blocking the vent altogether.</div><div class="gmail_default" style="font-family:trebuchet ms,sans-serif">That might not be a concern if you are in a warmer climate, but here in Alberta and i&#39;m sure much of the US, it is very possible that this could happen.</div><div class="gmail_default" style="font-family:trebuchet ms,sans-serif"><br></div><div class="gmail_default" style="font-family:trebuchet ms,sans-serif">Regardless, i&#39;m pleased to have found out the minimum height required for these vents as i will be looking to trim down any taller ones that will cause some shading.  Always looking to maximize system performance, a few inches (several in some cases) trimmed off the height of a vent will be just that much less shading and increased system output. I can&#39;t imagine it would be too much, but....</div><div class="gmail_default" style="font-family:trebuchet ms,sans-serif"><br></div><div class="gmail_default" style="font-family:trebuchet ms,sans-serif">Cheers,</div><div class="gmail_default" style="font-family:trebuchet ms,sans-serif">Benn</div></div><div class="gmail_extra"><br><div class="gmail_quote">On Thu, Sep 25, 2014 at 6:22 AM, Matt Partymiller <span dir="ltr">&lt;<a href="mailto:matt@solar-energy-solutions.com" target="_blank">matt@solar-energy-solutions.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Carl,<br>
<br>
In our shared region plumbing code requires vents be 12&quot; above roof line.<br>
Electrical inspectors probably won&#39;t catch this, plumbing inspectors<br>
probably won&#39;t get on a roof, but still there is a code concern.  You<br>
might exercise some caution.<br>
<br>
Matt<br>
<br>
<br>
Matthew Partymiller<br>
Solar Energy Solutions LLC<br>
<a href="tel:%28877%29%20312-7456" value="+18773127456">(877) 312-7456</a><br>
<a href="mailto:matt@solar-energy-solutions.com">matt@solar-energy-solutions.com</a><br>
<div><div class="h5"><br>
On Wed, September 24, 2014 6:49 pm, Carl Adams wrote:<br>
&gt; Bruce,<br>
&gt; We routinely cut off DWV as suggested by earlier posts so that they are at<br>
&gt; least 1 inch below the surface of the back of the module.<br>
&gt;<br>
&gt; To be clear these are sewage intake air vents and not exhaust vents for<br>
&gt; heating appliances.<br>
&gt;<br>
&gt; We do place a quarter inch wire cloth over the cut off vent and apply a<br>
&gt; four inch stainless steel hose clamp around the pipe just to prevent<br>
&gt; foreign objects from entering the vent pipe.<br>
&gt;<br>
&gt; I have never had an inspector question this method.<br>
&gt;<br>
&gt;<br>
&gt; With Regards<br>
&gt; Carl Adams, President<br>
&gt; SunRock Solar<br>
&gt; <a href="tel:513.290.9072" value="+15132909072">513.290.9072</a> (cell)<br>
&gt; <a href="tel:513.766.6025" value="+15137666025">513.766.6025</a> (office)<br>
&gt;<br>
&gt;<br>
&gt; On Sep 24, 2014, at 1:37 PM, Ray Walters &lt;<a href="mailto:ray@solarray.com">ray@solarray.com</a>&gt; wrote:<br>
&gt;<br>
&gt;<br>
&gt; I agree with Kurt: you need a licensed       plumber in your area to<br>
&gt; advise you, if you&#39;re trying to keep the AHJs happy . 2nd,  I&#39;m very sure<br>
&gt; you don&#39;t want an exhaust/ combustion type vent under the array.  I&#39;ve<br>
&gt; had several over the years, and seen some arrays installed over them.<br>
&gt; They can get fairly hot and put quite a bit of steam out.  I would not<br>
&gt; trust the module backing material to a concentrated long term dose; which<br>
&gt; module is going to have a problem first? R.Ray Walters<br>
&gt; CTO, Solarray, Inc<br>
&gt; Nabcep Certified PV Installer,<br>
&gt; Licensed Master Electrician<br>
&gt; Solar Design Engineer<br>
&gt; <a href="tel:303%20505-8760" value="+13035058760">303 505-8760</a><br>
&gt; On 9/24/2014 11:16 AM, Kurt Johnsen wrote:<br>
&gt;<br>
&gt;&gt; Should you decide to lower your plumbing vents I have found an inside<br>
&gt;&gt; pipe cutter to be an inexpensive and handy tool. Cut the vent and lead<br>
&gt;&gt; off an inch above your desired pipe height and use the inside cutter to<br>
&gt;&gt; cut the pvc pipe. Go slow and be careful to keep air space between the<br>
&gt;&gt; pvc and lead as the lead will cut very easily.<br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt; Also I wouldn&#39;t rely on us well intentioned wrenches to make the call<br>
&gt;&gt; on the plumbing code in your jurisdiction. Though the state plumbing<br>
&gt;&gt; codes are usually based on the international code, there will be<br>
&gt;&gt; differences. If you can&#39;t pull up your state plumbing code online then<br>
&gt;&gt; ask your plumbing inspector. In Florida the minimum height above a roof<br>
</div></div>&gt;&gt; surface is 6&quot; (904.1). As for relocating 905.2 states that â\u20ac\u0153all vent<br>
<span class="">&gt;&gt; and branch vent pipes shall be so graded and connected as to drain back<br>
</span>&gt;&gt; to the drainage pipe by gravityâ\u20ac . Table 710.1(1) shows that for<br>
&gt;&gt; 1.5â\u20ac  pipe a slope of Â¼â\u20ac  per foot is sufficient to handle 3<br>
&gt;&gt; fixtures. I would take that to indicate Â¼â\u20ac  / foot is plenty for a<br>
&gt;&gt; 1.5â\u20ac  vent.<br>
<div class="HOEnZb"><div class="h5">&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt;&gt; On Wed, Sep 24, 2014 at 11:20 AM, Dave Click &lt;<a href="mailto:daveclick@fsec.ucf.edu">daveclick@fsec.ucf.edu</a>&gt;<br>
&gt;&gt;&gt; wrote:<br>
&gt;&gt;&gt; Flipping through the &#39;04 plumbing code I see a few slopes called out<br>
&gt;&gt;&gt; (1/4&quot; per 1&#39; for fixture vents, 1&quot; per 1&#39; for circuit vents, 1/2&quot; per<br>
&gt;&gt;&gt; 1&#39; for combination drain/vent...). Fixture vents have a maximum<br>
&gt;&gt;&gt; distance of a few feet from fixture trap to vent, but I don&#39;t think<br>
&gt;&gt;&gt; this prevents you from then running that vent horizontally. 916.2<br>
&gt;&gt;&gt; states that for vents other than stack vents or vent stacks if your<br>
&gt;&gt;&gt; vent is &gt;40&#39; you need to upsize the whole vent pipe (tough to do for<br>
&gt;&gt;&gt; an existing building, of course). Stack vents have a &quot;maximum<br>
&gt;&gt;&gt; developed length&quot; of 100&#39; for a 1.5&quot; vent which should be enough<br>
&gt;&gt;&gt; space to get away from under the PV. I don&#39;t see any slope<br>
&gt;&gt;&gt; requirements specifically for stack vents but my non-plumber&#39;s eye<br>
&gt;&gt;&gt; may be missing something.<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; The stack vent sizing Table 916.1 appears (in part) here too and it<br>
&gt;&gt;&gt; looks like the tables match up to a 2.5&quot;:<br>
&gt;&gt;&gt; <a href="http://www.engineeringtoolbox.com/drainage-vents-d_1110.html" target="_blank">http://www.engineeringtoolbox.com/drainage-vents-d_1110.html</a><br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; DKC<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; On 2014/9/24 10:19, Jason Szumlanski wrote:<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt; I am unable to find anything in the Florida code that precludes<br>
&gt;&gt;&gt;&gt; covering a plumbing vent. The code does require the vent to be 6&quot;<br>
&gt;&gt;&gt;&gt; above the roof surface I believe.<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt; I was unable to determine if these vents need to be vertical with<br>
&gt;&gt;&gt;&gt; no bends in the attic. Obviously you wouldn&#39;t want to create a trap<br>
&gt;&gt;&gt;&gt; in the attic, but a couple of 45&#39;s to relocate a plumbing vent to<br>
&gt;&gt;&gt;&gt; accommodate more PV seems like a desirable thing to do sometimes.<br>
&gt;&gt;&gt;&gt; Does anyone know if these can be relocated, i.e. to an adjacent<br>
&gt;&gt;&gt;&gt; roof surface?<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt; On my own home I had a vent to deal with. I broke out my saws-all,<br>
&gt;&gt;&gt;&gt; split the lead like a banana and peeled it back, cut the pipe at an<br>
&gt;&gt;&gt;&gt; angle, and folded the lead back into the pipe after applying<br>
&gt;&gt;&gt;&gt; sealant between the lead and pipe. There is a 1&quot; gap between the<br>
&gt;&gt;&gt;&gt; rim of the pipe and the back of the module. My theory on this<br>
&gt;&gt;&gt;&gt; working safely is that, a) there will be far less rainwater falling<br>
&gt;&gt;&gt;&gt; in and around this pipe with a module over it, and b) it is about<br>
&gt;&gt;&gt;&gt; 24&quot; from the roof ridge and there is a module over it so there will<br>
&gt;&gt;&gt;&gt; be very little water sheeting                           down from<br>
&gt;&gt;&gt;&gt; above the vent. Code notwithstanding, I felt this was a solid<br>
&gt;&gt;&gt;&gt; method on my own home, and I have inspected it after 6 months of<br>
&gt;&gt;&gt;&gt; Florida downpours and found no issues.<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt; Jason Szumlanski<br>
&gt;&gt;&gt;&gt; Fafco Solar<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;<br>
</div></div><div class="HOEnZb"><div class="h5">&gt;&gt;&gt;&gt; On Wed, Sep 24, 2014 at 6:38 AM, Bill Loesch<br>
&gt;&gt;&gt;&gt; &lt;<a href="mailto:solar1online@charter.net">solar1online@charter.net</a>&gt; wrote:<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt; Bruce, August, et al,<br>
&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt; This is but one more example of confusing terminology. A plumbing<br>
&gt;&gt;&gt;&gt;&gt; vent is not an exhaust vent!<br>
&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt; A plumbing vent (what August calls a cold vent) is provided to<br>
&gt;&gt;&gt;&gt;&gt; allow the sanitary drain traps (and perhaps more) to operate<br>
&gt;&gt;&gt;&gt;&gt; properly. Without the properly functioning traps you would have<br>
&gt;&gt;&gt;&gt;&gt; sewer gas smell and sewer gas from the plumbing fixtures. This<br>
&gt;&gt;&gt;&gt;&gt; was commonplace when indoor plumbing was introduced to early<br>
&gt;&gt;&gt;&gt;&gt; adopters.<br>
&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt; An exhaust vent is another animal entirely. An exhaust vent<br>
&gt;&gt;&gt;&gt;&gt; carries the combustion products to a suitable exterior location<br>
&gt;&gt;&gt;&gt;&gt; for dilution with ambient air. With the advent of power vented<br>
&gt;&gt;&gt;&gt;&gt; combustion appliances, a direct vent (one that takes in<br>
&gt;&gt;&gt;&gt;&gt; combustion air from the outside and naturally exhausts combustion<br>
&gt;&gt;&gt;&gt;&gt; products to the outside) is IMHO the only responsible way to<br>
&gt;&gt;&gt;&gt;&gt; install any power vented appliance in a freezing climate. (Power<br>
&gt;&gt;&gt;&gt;&gt; vented appliances come in both condensing and non-condensing<br>
&gt;&gt;&gt;&gt;&gt; flavors-they can penetrate the side wall or the roof).<br>
&gt;&gt;&gt;&gt;&gt; Originally, two separate pipes (with two independent properly<br>
&gt;&gt;&gt;&gt;&gt; separated penetrations) was used. That technique is still often<br>
&gt;&gt;&gt;&gt;&gt; used today. More recently concentric vents have been introduced<br>
&gt;&gt;&gt;&gt;&gt; both for condensing and non-condensing applications. A concentric<br>
&gt;&gt;&gt;&gt;&gt; vent can simplify some installations by putting the exhaust pipe<br>
&gt;&gt;&gt;&gt;&gt; inside a larger air intake pipe allowing for one, albeit larger,<br>
&gt;&gt;&gt;&gt;&gt; penetration. As you might imagine if the exhaust flow is<br>
&gt;&gt;&gt;&gt;&gt; hindered/diverted/redirected by an inappropriately located solar<br>
&gt;&gt;&gt;&gt;&gt; module combustion gasses will be re-ingested into the intake air.<br>
&gt;&gt;&gt;&gt;&gt; Not good for equipment performance. My understanding is the power<br>
&gt;&gt;&gt;&gt;&gt; vented appliance manufacturer dictates what kind of<br>
&gt;&gt;&gt;&gt;&gt; separation/clearances are needed with their product. My guess is<br>
&gt;&gt;&gt;&gt;&gt; you find they want at least a foot of separation between the top<br>
&gt;&gt;&gt;&gt;&gt; of the &quot; inverted cone&quot; and the module. Probably not what you had<br>
&gt;&gt;&gt;&gt;&gt; in mind for an aesthetically pleasing installation.<br>
&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt; I hope this helps,<br>
&gt;&gt;&gt;&gt;&gt; Bill Loesch<br>
&gt;&gt;&gt;&gt;&gt; Solar 1 - Saint Louis Solar<br>
&gt;&gt;&gt;&gt;&gt; <a href="tel:314%20631%201094" value="+13146311094">314 631 1094</a><br>
&gt;&gt;&gt;&gt;&gt; On 23-Sep-14 6:54 PM, August<br>
&gt;&gt;&gt;&gt;&gt; Goers wrote:<br>
&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt; Bruce and All,<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt; Sorry, I hit send before I had a chance to complete my<br>
&gt;&gt;&gt;&gt;&gt;&gt; thoughts. What I meant to say was that I&#39;ve found AHJs often<br>
&gt;&gt;&gt;&gt;&gt;&gt; allow us to cover cold plumbing vents but I&#39;ve never tried or<br>
&gt;&gt;&gt;&gt;&gt;&gt; had any luck with covering hot vents including condensing boiler<br>
&gt;&gt;&gt;&gt;&gt;&gt; PVC vents. Once again, if in doubt you<br>
&gt;&gt;&gt;&gt;&gt;&gt; could see what the plan checker or inspector thinks.<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt; Best,<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt; August<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt; -----Original Message-----<br>
&gt;&gt;&gt;&gt;&gt;&gt; From: August Goers [mailto:<a href="mailto:august@luminalt.com">august@luminalt.com</a>]<br>
&gt;&gt;&gt;&gt;&gt;&gt; Sent: Tuesday, September 23, 2014 4:15 PM<br>
&gt;&gt;&gt;&gt;&gt;&gt; To: &#39;RE-wrenches&#39;<br>
&gt;&gt;&gt;&gt;&gt;&gt; Subject: RE: [RE-wrenches] Modules over vents<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt; Bruce,<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt; I&#39;ll send you the CA plumbing code vent section offlist<br>
&gt;&gt;&gt;&gt;&gt;&gt; (attachment too<br>
&gt;&gt;&gt;&gt;&gt;&gt; large for this list). The way I read the code is that you<br>
&gt;&gt;&gt;&gt;&gt;&gt; technically can&#39;t cover any type of plumbing or hot vent.<br>
&gt;&gt;&gt;&gt;&gt;&gt; However, and I&#39;ve run into<br>
&gt;&gt;&gt;&gt;&gt;&gt; little resistance from AHJs in the Bay Area by covering these.<br>
&gt;&gt;&gt;&gt;&gt;&gt; You might<br>
&gt;&gt;&gt;&gt;&gt;&gt; want to check in with your plan checker.<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt; Best,<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt; August<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt; Luminalt<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt; -----Original Message-----<br>
&gt;&gt;&gt;&gt;&gt;&gt; From: RE-wrenches<br>
&gt;&gt;&gt;&gt;&gt;&gt; [mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>] On<br>
&gt;&gt;&gt;&gt;&gt;&gt; Behalf Of Bruce Leininger<br>
&gt;&gt;&gt;&gt;&gt;&gt; Sent: Tuesday, September 23, 2014 3:49 PM<br>
&gt;&gt;&gt;&gt;&gt;&gt; To: RE-wrenches<br>
&gt;&gt;&gt;&gt;&gt;&gt; Subject: [RE-wrenches] Modules over vents<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt; Hi all.  We&#39;re designing a system on a roof that is literally<br>
&gt;&gt;&gt;&gt;&gt;&gt; infested with plumbing, exhaust and combustion vents.  The<br>
&gt;&gt;&gt;&gt;&gt;&gt; combustion vents are PVC and none of the vents are more than<br>
&gt;&gt;&gt;&gt;&gt;&gt; 1.5&#39; above the roof.<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt; A racking company says that we can cover them with modules,<br>
&gt;&gt;&gt;&gt;&gt;&gt; since the modules will be at least 4&#39; above the roof.  They have<br>
&gt;&gt;&gt;&gt;&gt;&gt; not yet provided any building code references to say that this<br>
&gt;&gt;&gt;&gt;&gt;&gt; is ok.  Do any of you know if the building code allows this?<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt; Thanks.<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;&gt;&gt; Bruce<br>
&gt;&gt;&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt; _______________________________________________<br>
&gt;&gt;&gt;&gt; List sponsored by Redwood Alliance<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt; List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt; Change listserver email address &amp; settings:<br>
&gt;&gt;&gt;&gt; <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt; List-Archive:<br>
&gt;&gt;&gt;&gt; <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maill" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maill</a><br>
&gt;&gt;&gt;&gt; ist.html<br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt; List rules &amp; etiquette:<br>
&gt;&gt;&gt;&gt; <a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
&gt;&gt;&gt;&gt;<br>
&gt;&gt;&gt;&gt; Check out or update participant bios:<br>
&gt;&gt;&gt;&gt; <a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; _______________________________________________<br>
&gt;&gt;&gt; List sponsored by Redwood Alliance<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; Change listserver email address &amp; settings:<br>
&gt;&gt;&gt; <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; List-Archive:<br>
&gt;&gt;&gt; <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillis" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillis</a><br>
&gt;&gt;&gt; t.html<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; List rules &amp; etiquette:<br>
&gt;&gt;&gt; <a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; Check out or update participant bios:<br>
&gt;&gt;&gt; <a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt; _______________________________________________<br>
&gt;&gt; List sponsored by Redwood Alliance<br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt; List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt; Change listserver email address &amp; settings:<br>
&gt;&gt; <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt; List-Archive:<br>
&gt;&gt; <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist</a>.<br>
&gt;&gt; html<br>
&gt;&gt;<br>
&gt;&gt; List rules &amp; etiquette:<br>
&gt;&gt; <a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
&gt;&gt;<br>
&gt;&gt; Check out or update participant bios:<br>
&gt;&gt; <a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
&gt;&gt;<br>
&gt;<br>
&gt; _______________________________________________<br>
&gt; List sponsored by Redwood Alliance<br>
&gt;<br>
&gt;<br>
&gt; List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
&gt;<br>
&gt;<br>
&gt; Change listserver email address &amp; settings:<br>
&gt; <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
&gt;<br>
&gt;<br>
&gt; List-Archive:<br>
&gt; <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.ht" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.ht</a><br>
&gt; ml<br>
&gt;<br>
&gt; List rules &amp; etiquette:<br>
&gt; <a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
&gt;<br>
&gt; Check out or update participant bios:<br>
&gt; <a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
&gt;<br>
&gt; _______________________________________________<br>
&gt; List sponsored by Redwood Alliance<br>
&gt;<br>
&gt;<br>
&gt; List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
&gt;<br>
&gt;<br>
&gt; Change listserver email address &amp; settings:<br>
&gt; <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
&gt;<br>
&gt;<br>
&gt; List-Archive:<br>
&gt; <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.ht" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.ht</a><br>
&gt; ml<br>
&gt;<br>
&gt; List rules &amp; etiquette:<br>
&gt; <a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
&gt;<br>
&gt; Check out or update participant bios:<br>
&gt; <a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
&gt;<br>
&gt;<br>
<br>
<br>
<br>
<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</div></div></blockquote></div><br><br clear="all"><div><br></div>-- <br><p style="font-size:13px;margin:0px;padding:1em 0px;text-align:justify;color:rgb(0,0,0);font-family:helvetica,sans-serif;line-height:18px">
        <strong style="margin:0px;padding:0px">Benn Kilburn <span style="font-size:9px"></span></strong><br style="margin:0px;padding:0px">
        CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc<br style="margin:0px;padding:0px">
        6706 \u2013 82 Ave NW | Edmonton, AB | T6B 0E7<br style="margin:0px;padding:0px">
        P: 780-474-8992 | F: 888-405-5843 | <a href="http://www.skyfireenergy.com/" style="margin:0px;padding:0px;color:rgb(240,140,0);text-decoration:none;border-width:0px;border-style:none" target="_blank">www.skyfireenergy.com</a><br style="margin:0px;padding:0px">
        <a href="mailto:benn@skyfireenergy.com" style="margin:0px;padding:0px;color:rgb(240,140,0);text-decoration:none;border-width:0px;border-style:none" target="_blank"><img alt="email" height="25" src="http://www.skyfireenergy.com/wp-content/uploads/2014/08/email.png" style="margin:0px;padding:0px;border-width:0px;border-style:none" width="25"></a> <a href="https://www.facebook.com/SkyFireEnergy" style="margin:0px;padding:0px;color:rgb(240,140,0);text-decoration:none;border-width:0px;border-style:none" target="_blank"><img alt="facebook" height="25" src="http://www.skyfireenergy.com/wp-content/uploads/2014/08/facebook.png" style="margin:0px;padding:0px;border-width:0px;border-style:none" width="25"></a> <a href="https://twitter.com/SkyFireEnergy" style="margin:0px;padding:0px;color:rgb(240,140,0);text-decoration:none;border-width:0px;border-style:none" target="_blank"><img alt="twitter" height="25" src="http://www.skyfireenergy.com/wp-content/uploads/2014/08/twitter.png" style="margin:0px;padding:0px;border-width:0px;border-style:none" width="25"></a> <a href="https://www.linkedin.com/company/283735?trk=tyah&amp;trkInfo=tarId%3A1408655033432%2Ctas%3Askyfire%2Cidx%3A2-2-5" style="margin:0px;padding:0px;color:rgb(240,140,0);text-decoration:none;border-width:0px;border-style:none" target="_blank"><img alt="linkedin" height="25" src="http://www.skyfireenergy.com/wp-content/uploads/2014/08/linkedin.png" style="margin:0px;padding:0px;border-width:0px;border-style:none" width="25"></a> <a href="https://plus.google.com/+SkyFireEnergy/" style="margin:0px;padding:0px;color:rgb(240,140,0);text-decoration:none;border-width:0px;border-style:none" target="_blank"><img alt="google" height="25" src="http://www.skyfireenergy.com/wp-content/uploads/2014/08/google.png" style="margin:0px;padding:0px;border-width:0px;border-style:none" width="25"></a></p>
<p style="font-size:13px;margin:0px;padding:1em 0px;text-align:justify;color:rgb(0,0,0);font-family:helvetica,sans-serif;line-height:18px">
        <img alt="SkyFire Energy Logo_horizontal" height="47" src="http://www.skyfireenergy.com/wp-content/uploads/2014/07/SkyFire-Energy-Logo_horizontal.png" style="margin:0px;padding:0px;border-width:0px;border-style:none" width="179"></p>
</div>