<p class="MsoNormal"><span style="font-size:12pt;font-family:&quot;Times New Roman&quot;,&quot;serif&quot;">Should you decide to lower your
plumbing vents I have found an inside pipe cutter to be an inexpensive and
handy tool. Cut the vent and lead off an inch above your desired pipe height
and use the inside cutter to cut the pvc pipe. Go slow and be careful to keep
air space between the pvc and lead as the lead will cut very easily. </span><span style="font-size:12pt"></span></p>

<p class="MsoNormal"><span style="font-size:12pt;font-family:&quot;Times New Roman&quot;,&quot;serif&quot;"> </span></p>

<p class="MsoNormal"><span style="font-size:12pt;font-family:&quot;Times New Roman&quot;,&quot;serif&quot;">Also I wouldn&#39;t rely on us well
intentioned wrenches to make the call on the plumbing code in your
jurisdiction. Though the state plumbing codes are usually based on the
international code, there will be differences. If you can&#39;t pull up your state
plumbing code online then ask your plumbing inspector. In Florida the minimum
height above a roof surface is 6&quot; (904.1). As for relocating 905.2 states
that \u201call vent and branch vent pipes shall be so graded and connected as to
drain back to the drainage pipe by gravity\u201d. Table 710.1(1) shows that for 1.5\u201d
pipe a slope of ¼\u201d per foot is sufficient to handle 3 fixtures. I would take
that to indicate ¼\u201d / foot is plenty for a 1.5\u201d vent. </span><span style="font-size:12pt"></span></p>

</div><div class="gmail_extra"><br><div class="gmail_quote">On Wed, Sep 24, 2014 at 11:20 AM, Dave Click <span dir="ltr">&lt;<a href="mailto:daveclick@fsec.ucf.edu" target="_blank">daveclick@fsec.ucf.edu</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div bgcolor="#FFFFFF" text="#000000">
    Flipping through the &#39;04 plumbing code I see a few slopes called out
    (1/4&quot; per 1&#39; for fixture vents, 1&quot; per 1&#39; for circuit vents, 1/2&quot;
    per 1&#39; for combination drain/vent...). Fixture vents have a maximum
    distance of a few feet from fixture trap to vent, but I don&#39;t think
    this prevents you from then running that vent horizontally. 916.2
    states that for vents other than stack vents or vent stacks if your
    vent is &gt;40&#39; you need to upsize the whole vent pipe (tough to do
    for an existing building, of course). Stack vents have a &quot;maximum
    developed length&quot; of 100&#39; for a 1.5&quot; vent which should be enough
    space to get away from under the PV. I don&#39;t see any slope
    requirements specifically for stack vents but my non-plumber&#39;s eye
    may be missing something.<br>
    <br>
    The stack vent sizing Table 916.1 appears (in part) here too and it
    looks like the tables match up to a 2.5&quot;:<br>
    <a href="http://www.engineeringtoolbox.com/drainage-vents-d_1110.html" target="_blank">http://www.engineeringtoolbox.com/drainage-vents-d_1110.html</a><br>
    <br>
    DKC<div><div class="h5"><br>
    <br>
    <br>
    <br>
    <div>On 2014/9/24 10:19, Jason Szumlanski
      wrote:<br>
    </div>
    </div></div><blockquote type="cite"><div><div class="h5">
      <div dir="ltr">
        <div class="gmail_default" style="font-family:verdana,sans-serif">
          <div class="gmail_default" style="font-size:12.7272720336914px">I am unable to find
            anything in the Florida code that precludes covering a
            plumbing vent. The code does require the vent to be 6&quot; above
            the roof surface I believe.</div>
          <div class="gmail_default" style="font-size:12.7272720336914px"><br>
          </div>
          <div class="gmail_default" style="font-size:12.7272720336914px">I was unable to
            determine if these vents need to be vertical with no bends
            in the attic. Obviously you wouldn&#39;t want to create a trap
            in the attic, but a couple of 45&#39;s to relocate a plumbing
            vent to accommodate more PV seems like a desirable thing to
            do sometimes. Does anyone know if these can be relocated,
            i.e. to an adjacent roof surface?</div>
          <div style="font-size:12.7272720336914px"><br>
          </div>
          <div style="font-size:12.7272720336914px">On my own home I had
            a vent to deal with. I broke out my saws-all, split the lead
            like a banana and peeled it back, cut the pipe at an angle,
            and folded the lead back into the pipe after applying
            sealant between the lead and pipe. There is a 1&quot; gap between
            the rim of the pipe and the back of the module. My theory on
            this working safely is that, a) there will be far less
            rainwater falling in and around this pipe with a module over
            it, and b) it is about 24&quot; from the roof ridge and there is
            a module over it so there will be very little water sheeting
            down from above the vent. Code notwithstanding, I felt this
            was a solid method on my own home, and I have inspected it
            after 6 months of Florida downpours and found no issues.</div>
        </div>
        <br>
        <br>
        <div href="http://WISESTAMP_SIG_gmail_session">
          <div style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif">
            <div style="margin:0px 0px 8px">
              <p style="margin:0px"><span><span>Jason Szumlanski</span></span></p>
              <p style="margin:0px"><span><span></span></span></p>
              <div class="gmail_default" style="font-family:verdana,sans-serif;display:inline">Fafco
                Solar</div>
              <br>
            </div>
            <img height="1" width="1"></div>
        </div>
        <div class="gmail_extra"><br>
          <div class="gmail_quote">On Wed, Sep 24, 2014 at 6:38 AM, Bill
            Loesch <span dir="ltr">&lt;<a href="mailto:solar1online@charter.net" target="_blank">solar1online@charter.net</a>&gt;</span>
            wrote:<br>
            <blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
              <div bgcolor="#FFFFFF" text="#000000">
                <div><br>
                  Bruce, August, et al,<br>
                  <br>
                  This is but one more example of confusing terminology.
                  A plumbing vent is not an exhaust vent!<br>
                  <br>
                  A plumbing vent (what August calls a cold vent) is
                  provided to allow the sanitary drain traps (and
                  perhaps more) to operate properly. Without the
                  properly functioning traps you would have sewer gas
                  smell and sewer gas from the plumbing fixtures. This
                  was commonplace when indoor plumbing was introduced to
                  early adopters.<br>
                  <br>
                  An exhaust vent is another animal entirely. An exhaust
                  vent carries the combustion products to a suitable
                  exterior location for dilution with ambient air. With
                  the advent of power vented combustion appliances, a
                  direct vent (one that takes in combustion air from the
                  outside and naturally exhausts combustion products to
                  the outside) is IMHO the only responsible way to
                  install any power vented appliance in a freezing
                  climate. (Power vented appliances come in both
                  condensing and non-condensing flavors-they can
                  penetrate the side wall or the roof). Originally, two
                  separate pipes (with two independent properly
                  separated penetrations) was used. That technique is
                  still often used today. More recently concentric vents
                  have been introduced both for condensing and
                  non-condensing applications. A concentric vent can
                  simplify some installations by putting the exhaust
                  pipe inside a larger air intake pipe allowing for one,
                  albeit larger, penetration. As you might imagine if
                  the exhaust flow is hindered/diverted/redirected by an
                  inappropriately located solar module combustion gasses
                  will be re-ingested into the intake air. Not good for
                  equipment performance. My understanding is the power
                  vented <u>appliance manufacturer</u> dictates what
                  kind of separation/clearances are needed with their
                  product. My guess is you find they want at least a
                  foot of separation between the top of the &quot; inverted
                  cone&quot; and the module. Probably not what you had in
                  mind for an aesthetically pleasing installation.<br>
                  <br>
                  I hope this helps,<br>
                  <pre cols="72">Bill Loesch
Solar 1 - Saint Louis Solar
<a href="tel:314%20631%201094" value="+13146311094" target="_blank">314 631 1094</a></pre>
                  <div>
                    <div> On 23-Sep-14 6:54 PM, August Goers
                      wrote:<br>
                    </div>
                  </div>
                </div>
                <blockquote type="cite">
                  <pre><div><div>Bruce and All,

Sorry, I hit send before I had a chance to complete my thoughts. What I
meant to say was that I&#39;ve found AHJs often allow us to cover cold
plumbing vents but I&#39;ve never tried or had any luck with covering hot
vents including condensing boiler PVC vents. Once again, if in doubt you
could see what the plan checker or inspector thinks.

Best,

August

-----Original Message-----
From: August Goers [<a href="mailto:august@luminalt.com" target="_blank">mailto:august@luminalt.com</a>]
Sent: Tuesday, September 23, 2014 4:15 PM
To: &#39;RE-wrenches&#39;
Subject: RE: [RE-wrenches] Modules over vents

Bruce,

I&#39;ll send you the CA plumbing code vent section offlist (attachment too
large for this list). The way I read the code is that you technically
can&#39;t cover any type of plumbing or hot vent. However, and I&#39;ve run into
little resistance from AHJs in the Bay Area by covering these. You might
want to check in with your plan checker.

Best,

August

Luminalt

-----Original Message-----
From: RE-wrenches [<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On
Behalf Of Bruce Leininger
Sent: Tuesday, September 23, 2014 3:49 PM
To: RE-wrenches
Subject: [RE-wrenches] Modules over vents

Hi all.  We&#39;re designing a system on a roof that is literally infested
with plumbing, exhaust and combustion vents.  The combustion vents are PVC
and none of the vents are more than 1.5&#39; above the roof.

A racking company says that we can cover them with modules, since the
modules will be at least 4&#39; above the roof.  They have not yet provided
any building code references to say that this is ok.  Do any of you know
if the building code allows this?

Thanks.

Bruce</div></div></pre>
                </blockquote>
              </div>
            </blockquote>
          </div>
          <br>
        </div>
      </div>
      <br>
      <fieldset></fieldset>
      <br>
      </div></div><span class=""><pre>_______________________________________________
List sponsored by Redwood Alliance

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>

</pre>
    </span></blockquote>
    <br>
  </div>

<br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div>