<div dir="ltr">Hi Mac, all;<div>Since Colorado just adopted NEC2014 July 1, I have not heard any AHJ stories yet. But look at 690.12 (1):</div><div>&quot;Requirements for controlled conductors shall apply only to PV system conductors of more than 5 ft in length inside a building, OR more than 10 ft from a PV array.&quot;</div>
<div>(my emphasis on &quot;OR&quot;)</div><div><br></div><div>I interpret this to mean that if a ground mount array is more than 10 ft from the building, then any PV circuits that run up the outside of the building from their trench  (for example to penetrate the wall to the power center on the inside) must be controlled because they are &quot;on&quot; the building. And even if you penetrated right from the trench into the crawl space, then up to the power center on the inside wall, with less than 5 ft distance, still needs to be controlled if the array is more than 10 feet from the building because of that &quot;OR&quot;</div>
<div><br></div><div>The logic and safety advantage of this for firefighters is another topic entirely. As a first-arriving firefighter, I would spot the PV racks on the ground, walk over to them, and throw the disconnects on the nicely-labeled combiner boxes located within 10 feet of the array.</div>
<div><br></div><div>All thoughts appreciated, still puzzling this out.</div><div><div class="gmail_extra"><br clear="all"><div><div dir="ltr">Dan Fink<div>Buckville Energy</div><div>Otherpower</div><div>NABCEP / IREC / ISPQ accredited Continuing Education Providers<br>
970.672.4342<br><br></div></div></div></div></div></div>