<HTML><HEAD>
<META content="text/html; charset=utf-8" http-equiv=Content-Type></HEAD>
<BODY>
<DIV>
<DIV style="FONT-SIZE: 11pt; FONT-FAMILY: Calibri,sans-serif">I wonder if the UPS is grumbling about high voltage as the inverters push back current...<BR><BR>Glenn </DIV></DIV>
<DIV dir=ltr>
<HR>
<SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Calibri,sans-serif; FONT-WEIGHT: bold">From: </SPAN><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Calibri,sans-serif"><A href="mailto:swingjunkie@gmail.com">Carl Adams</A></SPAN><BR><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Calibri,sans-serif; FONT-WEIGHT: bold">Sent: </SPAN><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Calibri,sans-serif">\u200e8/\u200e4/\u200e2014 10:29</SPAN><BR><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Calibri,sans-serif; FONT-WEIGHT: bold">To: </SPAN><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Calibri,sans-serif"><A href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A></SPAN><BR><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Calibri,sans-serif; FONT-WEIGHT: bold">Subject: </SPAN><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Calibri,sans-serif">[RE-wrenches] UPS disturbance with SMA Inverters</SPAN><BR><BR></DIV>
<DIV dir=ltr>Hello Wrenches, 
<DIV><BR></DIV>
<DIV>I have a site which is experiencing nuisance disturbance of the computer UPS systems at the site. &nbsp;The site owner "suspects" this is due to the <SPAN tabIndex=-1 id=:1ec.1>PV</SPAN> system which is a 50 kW system using 6 <SPAN tabIndex=-1 id=:1ec.2>SMA</SPAN> <SPAN tabIndex=-1 id=:1ec.3>SunnyBoy</SPAN> inverters. &nbsp;The nuisance disturbance is a clicking noise in the UPS units. &nbsp;The disturbance is not enough to cause the UPS to engage, so it seems to be a small disturbance on the AC power. &nbsp; The site owner "suspects" the inverters are the source of this disturbance since 1) It seems to only occur when we have a good solar day. &nbsp;2) If the inverters are shut down the problem goes away, and if you start up the inverters the problem exhibits again.</DIV>
<DIV><BR></DIV>
<DIV>The site was commissioned in March of 2012 and has had no problems till this issue last month. &nbsp;In reviewing the event log on Sunny Portal there are no inverter anomalies. &nbsp;<SPAN tabIndex=-1 id=:1ec.4>SMA</SPAN> tech support had not run into this issue and had no ideas, they too agree the inverters are not reporting any anomalies.</DIV>
<DIV><BR></DIV>
<DIV>The problem is not persistent but rather intermittent making this harder to troubleshoot.</DIV>
<DIV><BR></DIV>
<DIV>So my questions are</DIV>
<DIV>1) Has anyone else seen this sort of issue before, related to <SPAN tabIndex=-1 id=:1ec.5>SMA</SPAN> <SPAN tabIndex=-1 id=:1ec.6>SunnyBoy</SPAN> inverters.</DIV>
<DIV>2) Can you recommend an AC power monitoring tool which would support &nbsp;frequency and voltage monitoring on the AC line. &nbsp;Perhaps one data set on the circuit feeding the computers and another on the inverter output circuit.</DIV>
<DIV><BR></DIV>
<DIV>For clarity the six <SPAN tabIndex=-1 id=:1ec.7>SunnyBoys</SPAN> feed into an AC Combiner panel which <SPAN tabIndex=-1 id=:1ec.8>backfeeds</SPAN> into the building main distribution panel. &nbsp;The service is 240V single phase.</DIV>
<DIV><BR></DIV>
<DIV>With Regards</DIV>
<DIV>Carl Adams, <SPAN tabIndex=-1 id=:1ec.9>SunRock</SPAN> Solar</DIV>
<DIV><SPAN tabIndex=-1 id=:1ec.10>NABCEP</SPAN> Certified <SPAN tabIndex=-1 id=:1ec.11>PV</SPAN> Installer</DIV></DIV></BODY></HTML>