<div dir="ltr">Insulated taps are for voltage.<div>L1 is forward, L2 backward, so as to measure total current in both legs with one CT.</div><div><br><div><br></div></div></div><div class="gmail_extra"><br><br><div class="gmail_quote">
On Thu, Jul 10, 2014 at 4:39 PM, Corey Shalanski <span dir="ltr">&lt;<a href="mailto:cshalanski@joule-energy.com" target="_blank">cshalanski@joule-energy.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div dir="ltr">Wrenches,<div><br></div><div>One of our customers has a utility meter CT cabinet ahead of his main disconnect - please see attached image.</div><div><br></div><div>I have never seen this arrangement and would be interested if anyone can explain why the conductors are run in this fashion: I assume the insulated taps are for voltage reference purposes or to power the meter? I also assume the large donut is the CT? Are the conductors run criss-crossed due to they&#39;re being 180 out of phase?</div>

<div><br></div><div>We are more particularly interested in the correct location to make a supply side interconnection in order to ensure that all PV energy is properly metered (our utility installs net meters in place of the customer&#39;s original meter). Assuming that our AHJ approves of an interconnection inside the CT cabinet, where would we splice into the service conductors: load side of the CT?</div>

<div><br></div><div>--</div><div>Corey Shalanski</div><div>Joule Energy</div><div>New Orleans, LA</div><div hspace="streak-pt-mark" style="max-height:1px"><img style="width:0px;max-height:0px" src="https://mailfoogae.appspot.com/t?sender=aY3NoYWxhbnNraUBqb3VsZS1lbmVyZ3kuY29t&amp;type=zerocontent&amp;guid=bb506524-f100-4688-8efc-9059736ad120"><font color="#ffffff" size="1">\u1427</font></div>

</div>
<br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br><div dir="ltr">Chris Mason<div><div style="color:rgb(136,136,136)"><span style="font-size:13px">NABCEP Certified Solar PV Installer\u2122</span></div><div style="color:rgb(136,136,136)">
<span style="color:rgb(34,34,34)">Solar Design Engineer</span></div><div style="color:rgb(136,136,136)"><span style="font-size:13px">Generac Generators Industrial technician</span></div></div><div style="color:rgb(136,136,136)">
<span style="font-size:13px"><br></span></div><div><a href="http://www.cometenergysystems.com" target="_blank">www.cometsolar.com</a></div><div>264.235.5670</div><div>869.662.5670</div><div>Skype: netconcepts</div></div>
</div>