<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    <div class="moz-cite-prefix">Based on many successful installs, I'd
      say a 3/4 HP pump is not a problem at all, and that the Magnum
      could easily run a 1-1/2 HP submersible pump.<br>
      2 HP probably, but that's where you start worrying.<br>
      The Franklin Subpak controller can be used on regular AC pumps and
      not only offers constant pressure, it removes the starting surge.&nbsp;
      This is the future for all pumping systems, and it makes the solar
      installer's life easier too.&nbsp; Grundfos makes the SQE line&nbsp; (as
      others mentioned) but the Franklin Controller is an above ground
      solution, that you can wire in without involving the well guy to
      pull the pump.<br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 7/2/2014 8:17 AM, Drake wrote:<br>
    </div>
    <blockquote cite="mid:20140702141702.3F5231036C@che.dreamhost.com"
      type="cite">
      Hello Wrenches,<br>
      <br>
      We are hoping to use a Magnum PAE 4448 to back up a household that
      includes a 3/4 HP deep well pump. There is about 120 feet of
      vertical
      rise and about 1000 feet of horizontal distance. <br>
      <br>
      I have been told that there is a correlation between the locked
      rotor
      current of a pump and the predictable ability of a specified
      inverter to
      power that pump. <br>
      <br>
      The plumber who installed the pump left no paperwork and retained
      no
      records of what pump he put in the hole last year. He could only
      say it
      was a 3/4 HP pump. We are therefore unable to obtain the
      manufacturer's
      nameplate specifications.<br>
      <br>
      The Magnum PAE 4448 has a 1 mS surge of 70 A (at 240 V) and a 100
      MS
      surge of 40 A. According to the NEC Table 430.251(A), a 3/4 HP
      motor has
      a locked rotor current of 41.4 amps at 230 V. <br>
      <br>
      This inverter can surge at 35.4 A for 5 seconds. The specified
      battery
      bank will be 8 Full River&nbsp; L-16 AGMs. Can anyone say if:
      <ul>
        <li>Is there enough information to know if this setup will
          handle the
          pump, and if so, will it?
        </li>
        <li>How can an inverter's ability to power a motor or pump be
          calculated
          by knowing its locked rotor current? Which surge periods
          should be
          compared to the locked rotor current? </li>
        <li>Does the surge current need to equal locked rotor. How long
          must the
          inverter meet its required maximum surge?
        </li>
        <li>From experience with Magnums and pumps, does this seem like
          a good
          combination?
        </li>
      </ul>
      <br>
      Thank you,<br>
      <br>
      Drake <br>
      <br>
      Drake Chamberlin<br>
      <i>Athens Electric LLC<br>
        OH License 44810<br>
        CO License 3773<br>
        NABCEP Certified Solar PV <br>
        740-448-7328<br>
      </i><a moz-do-not-send="true" href="http://athens-electric.com/">http://athens-electric.com/</a>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>