<div dir="ltr"><div class="gmail_default" style="font-family:verdana,sans-serif">Sorry, typo - that&#39;s a 48V string (one string of 8 batteries).</div><br><div id="WISESTAMP_SIG_gmail_session" href="http://WISESTAMP_SIG_gmail_session">

<div style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif"><div style="margin:0 0 8px 0"><p style="margin:0"><span><span>Jason Szumlansk</span></span><span style="font-family:verdana,sans-serif">\u200bi</span></p>

<p></p><p style="margin:0"><span><span></span></span></p><div class="gmail_default" style="font-family:verdana,sans-serif;display:inline">Fafco Solar</div><p></p><div style="clear:both"></div></div><img src="https://wisestamp.appspot.com/pixview.gif?p=chrome&amp;v=3.42.0&amp;t=1404328593153&amp;u=d0c775731865b324" width="1" height="1"></div>

<img src="http://ws-stats.appspot.com/ga/pixel.png?yes__count=true&amp;e=legacy_impression"></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Wed, Jul 2, 2014 at 3:15 PM, Jason Szumlanski <span dir="ltr">&lt;<a href="mailto:jason@fafcosolar.com" target="_blank">jason@fafcosolar.com</a>&gt;</span> wrote:<br>

<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="ltr"><div style="font-family:verdana,sans-serif"><div class="gmail_extra" style="font-family:arial"><div style="font-family:verdana,sans-serif">

\u200bEven at 9600W, which is above the 5 second surge rating of the inverter,\u200b we&#39;re looking at about 200A on the DC side, which would be a 1-hr rate on an L-16 string. While that is high, it should not be an issue. Even at the 1ms surge of 16,800W, a 48 string of L16&#39;s should be able to handle that.</div>


<div style="font-family:verdana,sans-serif"><br></div><div style="font-family:verdana,sans-serif"><span style="font-family:Verdana,Arial,Helvetica,sans-serif;font-size:13px">Jason Szumlanski</span><br>
</div></div><div class="gmail_extra" style="font-family:arial"><div href="http://WISESTAMP_SIG_gmail_session"><div style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif"><div style="margin:0px 0px 8px">
<p style="margin:0px"></p><div style="font-family:verdana,sans-serif;display:inline">\u200bFafco Solar\u200b</div><br> <p></p></div></div></div></div></div><div class="gmail_extra"><br><br><div class="gmail_quote">
On Wed, Jul 2, 2014 at 2:35 PM, Roy Butler <span dir="ltr">&lt;<a href="mailto:roy@four-winds-energy.com" target="_blank">roy@four-winds-energy.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-color:rgb(204,204,204);border-left-style:solid;padding-left:1ex">



  
    
  
  <div bgcolor="#FFFFFF" text="#000000">
    <div>I haven&#39;t seen anyone mention the
      battery bank. If I understand correctly, there&#39;s a single string
      of sealed<br>
      L16 batteries on this inverter. I have my doubts as to whether or
      not that bank can provide the high current<br>
      the inverter needs to start this load.<br>
      <pre cols="72">Roy Butler
NABCEP Certified Solar PV Installer®
NYSERDA eligible PV &amp; wind installer
IREC Certified Master Trainer\u2122 for Small Wind Installer
Four Winds Renewable Energy, LLC
8902 Route 46, Arkport, NY 14807
<a href="tel:607-324-9747" value="+16073249747" target="_blank">607-324-9747</a>  <a href="http://www.four-winds-energy.com" target="_blank">www.four-winds-energy.com</a>

Join us at the 10th Annual Small Wind Conference
A Gathering of Installers, Manufacturers, Dealers, &amp; Distributors
June 17 and 18, 2014 in Stevens Point, Wisconsin
<a href="http://www.smallwindconference.com" target="_blank">www.smallwindconference.com</a>

Although no trees were killed in the sending of this message, 
a large number of electrons were terribly inconvenienced.

                
</pre><div><div>
      On 7/2/2014 2:10 PM, Jason Szumlanski wrote:<br>
    </div></div></div>
    <blockquote type="cite"><div><div>
      <div dir="ltr">
        <div style="font-family:verdana,sans-serif">To further qualify my
          statements, the inverter will start the pump without issue,
          but I should echo the warnings by others that if there are
          other loads present, especially other motor loads that could
          start \u200bconcurrently, you may experience issues. As long as
          your customer understands the limitations and possibilities,
          you may be just fine.</div>
        <br>
        <br>
        <div href="http://WISESTAMP_SIG_gmail_session">
          <div style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif">
            <div style="margin:0px 0px 8px">
              <p style="margin:0px"><span><span>Jason Szumlanski</span></span></p>
              <p style="margin:0px"><span><span></span></span></p>
              <div style="font-family:verdana,sans-serif;display:inline">\u200b
                Fafco Solar\u200b</div>
              <br>
            </div>
          </div>
          <img src="http://ws-stats.appspot.com/ga/pixel.png?yes__count=true%20&amp;e=legacy_impression"></div>
        <div class="gmail_extra"><br>
          <br>
          <div class="gmail_quote">On Wed, Jul 2, 2014 at 11:00 AM,
            Jason Szumlanski <span dir="ltr">&lt;<a href="mailto:jason@fafcosolar.com" target="_blank">jason@fafcosolar.com</a>&gt;</span>
            wrote:<br>
            <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-color:rgb(204,204,204);border-left-style:solid;padding-left:1ex">
              <div dir="ltr">
                <div style="font-family:verdana,sans-serif">For what
                  it&#39;s worth, I&#39;ve run a single speed 1.5HP pool pump
                  with a MS4448PAE in a mobile application on a 38.4kWh
                  battery bank (sixteen Rolls S-530&#39;s). I have also run
                  a 2.5HP Hayward EcoStar Variable Speed pool pump at
                  full RPM, but that startup current is likely less than
                  you well pump.</div>
                <div style="font-family:verdana,sans-serif"><br>
                </div>
                <div style="font-family:verdana,sans-serif">I&#39;m going to
                  guess your 3/4HP well pump will be a breeze to start
                  with this inverter.</div>
                <br>
                <br>
                <div href="http://WISESTAMP_SIG_gmail_session">
                  <div style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif">
                    <div style="margin:0px 0px 8px">
                      <p style="margin:0px"><span><span>Jason Szumlanski </span></span></p>
                      <p style="margin:0px"><span><span></span></span></p>
                      <div style="font-family:verdana,sans-serif;display:inline">\u200b
                        Fafco Solar\u200b</div>
                      <br>
                    </div>
                  </div>
                </div>
              </div>
              <div class="gmail_extra"><br>
                <br>
                <div class="gmail_quote">
                  On Wed, Jul 2, 2014 at 10:47 AM, Allan Sindelar <span dir="ltr">&lt;<a href="mailto:allan@sindelarsolar.com" target="_blank">allan@sindelarsolar.com</a>&gt;</span>
                  wrote:<br>
                  <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-color:rgb(204,204,204);border-left-style:solid;padding-left:1ex">
                    <div style="color:rgb(0,0,0);background-color:rgb(255,255,255)" bgcolor="#FFFFFF" text="#000000">
                      <div>Drake,<br>
                        As a normal CYA, I&#39;ll always gently let a
                        customer know that this (or any) particular
                        combination of inverter and load sometimes
                        proves incompatible, just in case the unexpected
                        happens. (We once had a MS4448 that would not
                        reliably start and run a condensing boiler; a
                        switch to a different boiler resolved the
                        issue.)<br>
                        <br>
                        Having said that note of caution, I wouldn&#39;t
                        give it any concern. 3/4 HP and 1 HP well pumps
                        have never been an issue; I would expect 1.5 HP
                        to be easy to run. At 2 HP I&#39;d be asking these
                        questions here. <br>
                        <br>
                        You might check that it&#39;s a 3-wire,
                        capacitor-start motor, but nowadays nearly all
                        are. Two-wire pumps (with no control box) can
                        add 50% to the surge.<br>
                        <br>
                        The Magnum has a fairly poor voltage regulation
                        response. Sometimes the AC voltage can drop to
                        ~80 VAC momentarily. So you might also caution
                        your customer that the lights may flicker when
                        the pump starts. In our home we know whenever
                        our Kenmore fridge turns on.<br>
                        <br>
                        Allan<br>
                        <br>
                        <div>
                          <div>
                            <p class="MsoNormal"><b>Allan Sindelar</b><br>
                              <span style="font-size:10pt"><a href="mailto:allan@sindelarsolar.com" target="_blank">allan@sindelarsolar.com</a></span><br>
                              <span style="font-size:10pt">NABCEP
                                Certified PV Installation Professional<br>
                                NABCEP Certified Technical Sales
                                Professional<br>
                                New Mexico EE98J Journeyman Electrician<br>
                                Founder (Retired), <span>Positive
                                  Energy, Inc.</span><br>
                                <b><a href="tel:505%20780-2738" value="+15057802738" target="_blank">505
                                    780-2738</a> cell</b><br>
                                <br>
                              </span></p>
                            <p class="MsoNormal"> </p>
                          </div>
                        </div>
                        <div>
                          <div> On 7/2/2014 8:17 AM, Drake wrote:<br>
                          </div>
                        </div>
                      </div>
                      <blockquote type="cite">
                        <div>
                          <div> Hello Wrenches,<br>
                            <br>
                            We are hoping to use a Magnum PAE 4448 to
                            back up a household that includes a 3/4 HP
                            deep well pump. There is about 120 feet of
                            vertical rise and about 1000 feet of
                            horizontal distance. <br>
                            <br>
                            I have been told that there is a correlation
                            between the locked rotor current of a pump
                            and the predictable ability of a specified
                            inverter to power that pump. <br>
                            <br>
                            The plumber who installed the pump left no
                            paperwork and retained no records of what
                            pump he put in the hole last year. He could
                            only say it was a 3/4 HP pump. We are
                            therefore unable to obtain the
                            manufacturer&#39;s nameplate specifications.<br>
                            <br>
                            The Magnum PAE 4448 has a 1 mS surge of 70 A
                            (at 240 V) and a 100 MS surge of 40 A.
                            According to the NEC Table 430.251(A), a 3/4
                            HP motor has a locked rotor current of 41.4
                            amps at 230 V. <br>
                            <br>
                            This inverter can surge at 35.4 A for 5
                            seconds. The specified battery bank will be
                            8 Full River  L-16 AGMs. Can anyone say if:
                            <ul>
                              <li>Is there enough information to know if
                                this setup will handle the pump, and if
                                so, will it? </li>
                              <li>How can an inverter&#39;s ability to power
                                a motor or pump be calculated by knowing
                                its locked rotor current? Which surge
                                periods should be compared to the locked
                                rotor current? </li>
                              <li>Does the surge current need to equal
                                locked rotor. How long must the inverter
                                meet its required maximum surge? </li>
                              <li>From experience with Magnums and
                                pumps, does this seem like a good
                                combination? </li>
                            </ul>
                            <br>
                            Thank you,<br>
                            <br>
                            Drake <br>
                            <br>
                            Drake Chamberlin<br>
                            <i>Athens Electric LLC<br>
                              OH License 44810<br>
                              CO License 3773<br>
                              NABCEP Certified Solar PV <br>
                              <a href="tel:740-448-7328" value="+17404487328" target="_blank">740-448-7328</a><br>
                            </i><a href="http://athens-electric.com/" target="_blank">http://athens-electric.com/</a> </div>
                        </div>
                      </blockquote>
                    </div>
                  </blockquote>
                </div>
              </div>
            </blockquote>
          </div>
        </div>
      </div>
      <br>
      </div></div></blockquote></div></blockquote></div></div><br></div>
</blockquote></div><br></div></div>