<div dir="ltr"><div class="gmail_default" style="font-family:verdana,sans-serif">It depends on your applicable code. In the 2008 code, 690.64(B) was specifically titled &quot;Load Side&quot; and the provisions of that section in full were not applicable to supply side connections. That was probably not the intention (i.e. the 120% rule and OCPD requirements should have applied to aggregation panels). In the 2011 code, 705.12(D) is the similar section, but it has been titled &quot;Utility Interactive Inverters.&quot; This section now &quot;allows&quot; load side connections, but the requirements (1) through (7) of this section still apply to supply side connections (my interpretation).</div>

<div class="gmail_default" style="font-family:verdana,sans-serif"><br></div><div class="gmail_default" style="font-family:verdana,sans-serif">The better code organization IMO would be:</div><div class="gmail_default" style="font-family:verdana,sans-serif">

<br></div><div class="gmail_default" style="font-family:verdana,sans-serif">705.12 (A) Allow supply side connections</div><div class="gmail_default" style="font-family:verdana,sans-serif">705.12 (B) Allow load side connections</div>

<div class="gmail_default" style="font-family:verdana,sans-serif">705.12 (C) Integrated Electrical Systems<br></div><div class="gmail_default" style="font-family:verdana,sans-serif">705.12 (D)(1)-(7) The requirements for all interconnection methods</div>

<div class="gmail_default" style="font-family:verdana,sans-serif">705.12 (E) Greater than 100kW</div><div class="gmail_default" style="font-family:verdana,sans-serif"><br></div><div class="gmail_default" style="font-family:verdana,sans-serif">

\u200b</div><div class="gmail_default" style="font-family:verdana,sans-serif">A bit off-topic, but we recently had a utility reject a plan to install a 320A meter socket with a 200A main distribution panel and a 100A solar aggregation panel (with four 20A backfed breakers). The two panels were to be fed from double lugs in the meter can. They said this was not allowed - they didn&#39;t want solar in their meter can. When I pointed out that dual 200A load panels are commonly fed this way and this was no different because I could just backfeed each 200A panel with two 20A breakers, my comment was met with blank stares.</div>

<br><br><div id="WISESTAMP_SIG_gmail_session" href="http://WISESTAMP_SIG_gmail_session"><div style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif"><div style="margin:0px 0px 8px"><p style="margin:0px"><span><span>Jason Szumlanski</span></span></p>

<p style="margin:0px"></p><div class="gmail_default" style="font-family:verdana,sans-serif;display:inline">\u200bFafco Solar\u200b</div><br> <p></p><div style="clear:both"></div></div><img src="https://wisestamp.appspot.com/pixview.gif?p=chrome&amp;v=3.42.0&amp;t=1403872191075&amp;u=dedcb4cd140ce271" width="1" height="1"></div>

<img src="http://ws-stats.appspot.com/ga/pixel.png?yes__count=true &amp;e=legacy_impression"></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Thu, Jun 26, 2014 at 6:11 PM, Corey Shalanski <span dir="ltr">&lt;<a href="mailto:cshalanski@joule-energy.com" target="_blank">cshalanski@joule-energy.com</a>&gt;</span> wrote:<br>


<blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-color:rgb(204,204,204);border-left-style:solid;padding-left:1ex"><div dir="ltr"><div hspace="streak-pt-mark" style="max-height:1px">

<img style="width: 0px; max-height: 0px;" src="https://mailfoogae.appspot.com/t?sender=aY3NoYWxhbnNraUBqb3VsZS1lbmVyZ3kuY29t&amp;type=zerocontent&amp;guid=4710ea9a-f97d-435f-a3b5-0de6c0b1180d"><font color="#ffffff" size="1">\u1427</font></div>



<div class="gmail_extra"><span style="font-family:arial,sans-serif;font-size:13px"><font color="#000000">Perhaps I should&#39;ve been more specific with my scenario. I was imagining a supply side connection, as this would more commonly be the case when combining multiple inverters. In this case it seems like the provisions of 705.12(D) for load side conections don&#39;t even apply, no? Rather 705.12(A) becomes the relevant section, and I see very few restrictions there.</font></span><div style="font-family:arial,sans-serif;font-size:13px">



<font color="#000000"><br></font></div><div style="font-family:arial,sans-serif;font-size:13px"><font color="#000000">Even with a load side connection I would tend to agree with Jason&#39;s interpretation: Does the &quot;source interconnection&quot; in 705.12(D)(1) refer to each individual inverter, or can it refer to an aggregated &quot;source&quot;?</font></div>



<div style="font-family:arial,sans-serif;font-size:13px"><font color="#000000"><br></font></div><div style="font-family:arial,sans-serif;font-size:13px"><font color="#000000">I am interested in pursuing this idea, mainly to understand how/where the NEC forbids it. In lieu of a clear Code reference against it, how is this any different from a branch circuit (in reverse)? ie, as with microinverters.</font></div>


<div>
<div style="font-family:arial,sans-serif;font-size:13px"><div><font color="#000000"><br></font></div><div><font color="#000000">--</font></div><div><font color="#000000">Corey Shalanski</font></div><div><font color="#000000">Joule Energy</font></div>



</div></div><div style="font-family:arial,sans-serif;font-size:13px"><font color="#000000">New Orleans, LA<br></font><div><div><font color="#000000"><img src="https://ssl.gstatic.com/ui/v1/icons/mail/images/cleardot.gif"></font></div>



</div><div><div class="gmail_extra"><font color="#000000"><br></font><div class="gmail_quote"><div><font color="#000000">On Thu, Jun 26, 2014 at 9:20 AM, <span dir="ltr">&lt;<a href="mailto:re-wrenches-request@lists.re-wrenches.org" target="_blank">re-wrenches-request@lists.re-wrenches.org</a>&gt;</span> wrote:<br>



</font></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-color:rgb(204,204,204);border-left-style:solid;padding-left:1ex"><font color="#000000"><br>Message: 11<br>Date: Thu, 26 Jun 2014 09:10:07 -0400<br>



From: Jason Szumlanski &lt;<a href="mailto:jason@fafcosolar.com" target="_blank">jason@fafcosolar.com</a>&gt;<div><br>To: RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt;<br>



Subject: Re: [RE-wrenches] Combining Multiple Inverters<br>Message-ID:<br></div>        &lt;<a href="mailto:CAJJtG3oQGBLzatinUHFp_GhivzYD6dLdsLAnkc1ofG9tR1RFgA@mail.gmail.com" target="_blank">CAJJtG3oQGBLzatinUHFp_GhivzYD6dLdsLAnkc1ofG9tR1RFgA@mail.gmail.com</a>&gt;<br>



Content-Type: text/plain; charset=&quot;utf-8&quot;<div><br><br>705.12(D) reads, &quot;... the interconnection provisions for the<br>utility-interactive inverter(s) shall comply with (D)(1) through (D)(7).&quot;<br>
That&#39;s inverters - plural. The interconnection must be protected by<br>
dedicated OCPD, not each inverter individually. Microinverters comply<br>because of this interpretation.<br><br>That said, I&#39;ve never done it. An accumulator panel is pretty cost<br>effective when you consider the alternative cost of an enclosure and the<br>



Polaris connectors. I guess if you are making the Polaris connections<br>inside the main load center or inside an inverter you can eliminate the<br>cost of a dedicated enclosure. There would be some material and labor<br>



savings.<br><br></div>?If the inverter has a maximum OCPD rating, you will be limited by that.<br>?Microinverters &quot;get around&quot; that by the wire and inverter being<div><br>sized/rated for the entire maximum string.<br>


<br>Jason Szumlanski<br><br></div></font></blockquote></div></div></div></div></div></div></blockquote></div></div></div>