<div dir="ltr"><div class="gmail_default" style="font-family:verdana,sans-serif">705.12(D) reads, "... the interconnection provisions for the utility-interactive inverter(s) shall comply with (D)(1) through (D)(7)." That's inverters - plural. The interconnection must be protected by dedicated OCPD, not each inverter individually. Microinverters comply because of this interpretation.</div>
<div class="gmail_default" style="font-family:verdana,sans-serif"><br></div><div class="gmail_default" style="font-family:verdana,sans-serif">That said, I've never done it. An accumulator panel is pretty cost effective when you consider the alternative cost of an enclosure and the Polaris connectors. I guess if you are making the Polaris connections inside the main load center or inside an inverter you can eliminate the cost of a dedicated enclosure. There would be some material and labor savings.</div>
<div><br></div><div class="gmail_default" style="font-family:verdana,sans-serif">\u200bIf the inverter has a maximum OCPD rating, you will be limited by that. \u200bMicroinverters "get around" that by the wire and inverter being sized/rated for the entire maximum string.</div>
<br><div id="WISESTAMP_SIG_gmail_session" href="http://WISESTAMP_SIG_gmail_session"><div style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif"><div style="margin:0 0 8px 0"><p style="margin:0"><span><span>Jason Szumlanski</span></span></p>
<p style="margin:0"><span><span></span></span></p><div class="gmail_default" style="font-family:verdana,sans-serif;display:inline">\u200bFafco Solar\u200b</div><p></p></div></div></div></div><div class="gmail_extra"><br><br><div class="gmail_quote">
On Wed, Jun 25, 2014 at 10:40 PM, Isaac Opalinsky <span dir="ltr"><<a href="mailto:David.Opalinsky@sunpower.com" target="_blank">David.Opalinsky@sunpower.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Then how do we install microinverters? 705.12(D)(1) says OCPD for each inverter is required at the point of interconnection with distribution equipment. But
as long as the conductors are sized to the OCPD, we follow the branch-circuit/feeder tap rules, and the inverter\u2019s maximum OCPD limit is not exceeded, what is the issue? I\u2019m assuming the inverter\u2019s maximum OCPD is usually the limiting factor, but I\u2019ve been
intrigued by the fact that the ABB TRIO has an option for AC OCPD in the inverter \u2013 it seems like there must be a cost-effective solution for tapping a trunk cable with a string inverter just as we do with microinverters. Has anyone tried this?<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<div>
<p class="MsoNormal" style="line-height:12.0pt;text-autospace:none"><b><span style="font-size:8.0pt;font-family:"Verdana","sans-serif";color:#5f5f5f">Isaac Opalinsky
</span></b><span style="font-size:8.0pt;font-family:"Verdana","sans-serif";color:#5f5f5f">| Technical Trainer |
<b>SunPower Corporation<u></u><u></u></b></span></p>
<p class="MsoNormal" style="line-height:12.0pt;text-autospace:none"><span style="font-size:8.0pt;font-family:"Verdana","sans-serif";color:#5f5f5f">Desk <a href="tel:443-569-3476" value="+14435693476" target="_blank">443-569-3476</a> | Cell <a href="tel:443-277-6286" value="+14432776286" target="_blank">443-277-6286</a><u></u><u></u></span></p>
</div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<div>
<div style="border:none;border-top:solid #b5c4df 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif""> RE-wrenches [mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>]
<b>On Behalf Of </b>Glenn Burt<br>
<b>Sent:</b> Wednesday, June 25, 2014 10:19 PM<br>
<b>To:</b> RE-wrenches<br>
<b>Subject:</b> Re: [RE-wrenches] Combining Multiple Inverters<u></u><u></u></span></p>
</div>
</div><div><div class="h5">
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif"">Code requires OCPD on the output of each inverter, so not sure where the savings would be..<u></u><u></u></span></p>
</div>
</div>
<div>
<div class="MsoNormal" align="center" style="text-align:center">
<hr size="2" width="100%" align="center">
</div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><b><span style="font-size:11.0pt;font-family:"Calibri","sans-serif"">From:
</span></b><span style="font-size:11.0pt;font-family:"Calibri","sans-serif""><a href="mailto:cshalanski@joule-energy.com" target="_blank">Corey Shalanski</a></span><br>
<b><span style="font-size:11.0pt;font-family:"Calibri","sans-serif"">Sent: </span>
</b><span style="font-size:11.0pt;font-family:"Calibri","sans-serif"">\u200e6/\u200e25/\u200e2014 21:19</span><br>
<b><span style="font-size:11.0pt;font-family:"Calibri","sans-serif"">To: </span></b><span style="font-size:11.0pt;font-family:"Calibri","sans-serif""><a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a></span><br>
<b><span style="font-size:11.0pt;font-family:"Calibri","sans-serif"">Subject: </span>
</b><span style="font-size:11.0pt;font-family:"Calibri","sans-serif"">[RE-wrenches] Combining Multiple Inverters</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">I am curious about best practices for combining the output of multiple inverters:
<u></u><u></u></p>
<div>
<ul type="disc">
<li class="MsoNormal">
We are considering using an insulated tap "Polaris/Burndy" connector in lieu of a solar accumulation panel. We would then run the output of this tap connector through a fused disconnect and on to the interconnection. Does anyone else do this?
<u></u><u></u></li><li class="MsoNormal">
In the above scenario, how should we size the wire between each inverter's output and the tap connector? Since there is no OCPD on this wire, would we have to use the same wire gauge as the combined output? or can we get away with sizing each wire according
to its associated inverter output rating? <u></u><u></u></li></ul>
<div>
<p class="MsoNormal">--<u></u><u></u></p>
</div>
</div>
<div>
<p class="MsoNormal">Corey Shalanski<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">Joule Energy<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">New Orleans, LA<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><img border="0" src="http://portal.mxlogic.com/images/transparent.gif"><span style="font-size:7.5pt;font-family:"Euphemia","sans-serif";color:white">\u1427</span><u></u><u></u></p>
</div>
</div>
</div></div></div>
</div>
<br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div>