  <body bgcolor="#FFFFFF" text="#000000">
    <font face="Helvetica, Arial, sans-serif">NEC says 10' from the
      array, defined as "</font><font face="Helvetica, Arial,
      sans-serif">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      A mechanically integrated assembly of modules or panels with a
      support structure and foundation, tracker, and other components,
      as required, to form a direct-current power-producing unit.
      <title>70HB14_CH00_FM_pi_xii.pdf</title>
      " I take this to mean that the "array" definition includes support
      structure, so you could go 10' from the bottom of the pole? <br>
      <br>
      But that doesn't matter, as rapid shutdown requirements only apply
      to PV systems "on or in" buildings; it only applies to a
      ground-mounted system if you bring the dc all the way into a
      building (for at least a 5' run within the structure). So, Rapid
      Shutdown doesn't apply at all to your scenario where only the ac
      wiring from a pole mount enters the building.<br>
      <br>
      DKC<br>
      <br>
      <br>
    </font>
    <div class="moz-cite-prefix">On 2014/6/25, 12:00, Jesse Dahl wrote:<br>
    </div>
    <blockquote
cite="mid:CAJLdFVc10ohBXE949za=Mvs9cRsES4vL+pFF6VQWB5JHc7no3A@mail.gmail.com"
      type="cite">
      <div dir="ltr">Re-reading this rapid shutdown convo.
        <div><br>
        </div>
        <div>&nbsp;Does 10' from the array mean from the modules or the
          "mount"? What if the array is on a pole, the pole is 15' tall
          and the inverter is mounted at the base of the pole? &nbsp;Since
          the array (modules) is 15' from the inverter is rapid shutdown
          required?&nbsp;</div>
        <div><br>
        </div>
        <div>Again, since the title of 690.12 is "On Buildings" is it
          required for pole mounts where only AC enters the building?
          &nbsp;Thoughts?</div>
        <div><br>
        </div>
        <div>Thanks!</div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div>Jesse&nbsp;</div>
      </div>
      <div class="gmail_extra"><br>
        <br>
        <div class="gmail_quote">On Sat, Apr 19, 2014 at 12:22 PM, Dan
          Fink <span dir="ltr">&lt;<a moz-do-not-send="true"
              href="mailto:danbob88@gmail.com" target="_blank">danbob88@gmail.com</a>&gt;</span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div dir="ltr">Hi Aaron, boB, Wrenches;
              <div>
                <div><br>
                </div>
                <div>I think Aaron brings up a good point, and it's
                  certainly confusing to me.</div>
                <div><br>
                </div>
                <div>The boldface type heading of 690.12 is "Rapid
                  Shutdown of PV Systems on Buildings"</div>
                <div><br>
                </div>
                <div>The body of the 690.12 text begins with "PV system
                  *circuits* installed on or in buildings shall....."</div>
                <div><br>
                </div>
                <div>690.2 defines "Photovoltaic source circuit" as
                  "Circuits between modules and from modules to the
                  common connection point(s) of the DC system"&nbsp;</div>
                <div><br>
                </div>
                <div>and "Photovoltaic output circuit" as "Circuit
                  conductors between the PV source circuit(s) and the
                  inverter or DC utilization equipment."</div>
                <div><br>
                </div>
                <div>"PV system" from the heading of 690.12 is not
                  defined in 690.2, other than that the definition of
                  "Photovoltaic system voltage" &nbsp;specifically includes
                  both PV output and source circuits.</div>
                <div><br>
                </div>
                <div>To me the confusing part of 690.12 is "PV Systems
                  on Buildings" is that "system" is not defined, and
                  tends to imply rooftop arrays. But "PV system circuits
                  installed on or in buildings shall....." is pretty
                  clear. I interpret it to mean anything DC and PV stuck
                  to the side of building like conduit, etc, or running
                  inside....which means it applies to ground-mount
                  arrays too if they terminate outside or inside the
                  building.</div>
                <div><br>
                </div>
                <div>What I'm seeing as the easy work-around for us
                  off-grid folk is the old "power shed" idea containing
                  battery bank, balance of system, inverter etc....just
                  build it within 10 feet of the PV array and you're
                  fine.</div>
                <div><br>
                </div>
                <div>Any thoughts?</div>
                <div>
                  <div>
                    <div><br>
                    </div>
                  </div>
                </div>
              </div>
            </div>
            <div class="gmail_extra"><br clear="all">
              <div>Dan Fink,<br>
                Executive Director;<br>
                Otherpower<br>
                Buckville Energy Consulting<br>
                Buckville Publications LLC<br>
                NABCEP / IREC accredited Continuing Education Providers<br>
                <a moz-do-not-send="true" href="tel:970.672.4342"
                  value="+19706724342" target="_blank">970.672.4342</a><br>
                <br>
                &nbsp;</div>
              <br>
              <br>
              <div class="gmail_quote">On Fri, Apr 18, 2014 at 3:30 PM,
                <a moz-do-not-send="true"
                  href="mailto:boB@midnitesolar.com" target="_blank">boB@midnitesolar.com</a>
                <span dir="ltr">&lt;<a moz-do-not-send="true"
                    href="mailto:boB@midnitesolar.com" target="_blank">boB@midnitesolar.com</a>&gt;</span>
                wrote:<br>
                <blockquote class="gmail_quote" style="margin:0 0 0
                  .8ex;border-left:1px #ccc solid;padding-left:1ex"><br>
                  Bill Brooks should probably respond to this also, but
                  reading the NEC, it looks like if the wires<br>
                  do not go inside the building to run more than 5 feet
                  (as the crow flies), the the rapid disconnect<br>
                  does not apply. &nbsp; &nbsp;OR, less than 10 feet from the
                  array IF the PV is mounted on that building.<span><font
                      color="#888888"><br>
                      <br>
                      boB</font></span>
                  <div>
                    <div><br>
                      <br>
                      <br>
                      <br>
                      On 4/18/2014 1:34 PM, Aaron Mandelkorn wrote:<br>
                      <blockquote class="gmail_quote" style="margin:0 0
                        0 .8ex;border-left:1px #ccc
                        solid;padding-left:1ex">
                        The rapid shutdown language is so confusing.
                        When looking at the rapid shutdown language,
                        does PV systems "on" a building refer to only
                        situations where the array is on a building; or
                        does it include DC conductors as well. For
                        example, if the DC conductors from a pole
                        mounted array run up the side of a building
                        before punching in to the inverter, does this
                        require rapid shutdown? &nbsp;Is this PV system
                        considered "on" a building?<br>
                        <br>
                        Aaron<br>
                        <br>
                        Aaron Mandelkorn<br>
                        Owner/Solar Specialist<br>
                        Renewable Energy Outfitters<br>
                        <a moz-do-not-send="true"
                          href="tel:719-221-5249" value="+17192215249"
                          target="_blank">719-221-5249</a><br>
                        <a moz-do-not-send="true"
                          href="tel:970-596-3744" value="+19705963744"
                          target="_blank">970-596-3744</a><br>
                        <a moz-do-not-send="true"
                          href="http://www.reosolar.com" target="_blank">www.reosolar.com</a><br>
                        <a moz-do-not-send="true"
                          href="mailto:reosolar@gmail.com"
                          target="_blank">reosolar@gmail.com</a><br>
                        <br>
                        <br>
                      </blockquote>
                      <br>
                      _______________________________________________<br>
                      List sponsored by Home Power magazine<br>
                      <br>
                      List Address: <a moz-do-not-send="true"
                        href="mailto:RE-wrenches@lists.re-wrenches.org"
                        target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
                      <br>
                      Change email address &amp; settings:<br>
                      <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                        target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                      <br>
                      List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                        target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                      <br>
                      List rules &amp; etiquette:<br>
                      <a moz-do-not-send="true"
                        href="http://www.re-wrenches.org/etiquette.htm"
                        target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
                      <br>
                      Check out participant bios:<br>
                      <a moz-do-not-send="true"
                        href="http://www.members.re-wrenches.org"
                        target="_blank">www.members.re-wrenches.org</a><br>
                      <br>
                    </div>
                  </div>
                </blockquote>
              </div>
              <br>
            </div>
            <br>
            _______________________________________________<br>
            List sponsored by Home Power magazine<br>
            <br>
            List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change email address &amp; settings:<br>
            <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
              target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
              target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
            <br>
            List rules &amp; etiquette:<br>
            <a moz-do-not-send="true"
              href="http://www.re-wrenches.org/etiquette.htm"
              target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out participant bios:<br>
            <a moz-do-not-send="true"
              href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
            <br>
            <br>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>