<div dir="ltr">Re-reading this rapid shutdown convo.<div><br></div><div> Does 10&#39; from the array mean from the modules or the &quot;mount&quot;? What if the array is on a pole, the pole is 15&#39; tall and the inverter is mounted at the base of the pole?  Since the array (modules) is 15&#39; from the inverter is rapid shutdown required? </div>
<div><br></div><div>Again, since the title of 690.12 is &quot;On Buildings&quot; is it required for pole mounts where only AC enters the building?  Thoughts?</div><div><br></div><div>Thanks!</div><div><br></div><div><br></div>
<div>Jesse </div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Sat, Apr 19, 2014 at 12:22 PM, Dan Fink <span dir="ltr">&lt;<a href="mailto:danbob88@gmail.com" target="_blank">danbob88@gmail.com</a>&gt;</span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="ltr">Hi Aaron, boB, Wrenches;<div><div><br></div><div>I think Aaron brings up a good point, and it&#39;s certainly confusing to me.</div>
<div><br></div><div>The boldface type heading of 690.12 is &quot;Rapid Shutdown of PV Systems on Buildings&quot;</div>

<div><br></div><div>The body of the 690.12 text begins with &quot;PV system *circuits* installed on or in buildings shall.....&quot;</div><div><br></div><div>690.2 defines &quot;Photovoltaic source circuit&quot; as &quot;Circuits between modules and from modules to the common connection point(s) of the DC system&quot; </div>


<div><br></div><div>and &quot;Photovoltaic output circuit&quot; as &quot;Circuit conductors between the PV source circuit(s) and the inverter or DC utilization equipment.&quot;</div><div><br></div><div>&quot;PV system&quot; from the heading of 690.12 is not defined in 690.2, other than that the definition of &quot;Photovoltaic system voltage&quot;  specifically includes both PV output and source circuits.</div>


<div><br></div><div>To me the confusing part of 690.12 is &quot;PV Systems on Buildings&quot; is that &quot;system&quot; is not defined, and tends to imply rooftop arrays. But &quot;PV system circuits installed on or in buildings shall.....&quot; is pretty clear. I interpret it to mean anything DC and PV stuck to the side of building like conduit, etc, or running inside....which means it applies to ground-mount arrays too if they terminate outside or inside the building.</div>


<div><br></div><div>What I&#39;m seeing as the easy work-around for us off-grid folk is the old &quot;power shed&quot; idea containing battery bank, balance of system, inverter etc....just build it within 10 feet of the PV array and you&#39;re fine.</div>

<div><br></div><div>Any thoughts?</div><div><div><div><br></div></div></div></div></div><div class="gmail_extra"><br clear="all"><div>Dan Fink,<br>Executive Director;<br>Otherpower<br>Buckville Energy Consulting<br>Buckville Publications LLC<br>

NABCEP / IREC accredited Continuing Education Providers<br><a href="tel:970.672.4342" value="+19706724342" target="_blank">970.672.4342</a><br><br> </div>
<br><br><div class="gmail_quote">On Fri, Apr 18, 2014 at 3:30 PM, <a href="mailto:boB@midnitesolar.com" target="_blank">boB@midnitesolar.com</a> <span dir="ltr">&lt;<a href="mailto:boB@midnitesolar.com" target="_blank">boB@midnitesolar.com</a>&gt;</span> wrote:<br>

<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><br>
Bill Brooks should probably respond to this also, but reading the NEC, it looks like if the wires<br>
do not go inside the building to run more than 5 feet (as the crow flies), the the rapid disconnect<br>
does not apply.    OR, less than 10 feet from the array IF the PV is mounted on that building.<span><font color="#888888"><br>
<br>
boB</font></span><div><div><br>
<br>
<br>
<br>
On 4/18/2014 1:34 PM, Aaron Mandelkorn wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
The rapid shutdown language is so confusing. When looking at the rapid shutdown language, does PV systems &quot;on&quot; a building refer to only situations where the array is on a building; or does it include DC conductors as well. For example, if the DC conductors from a pole mounted array run up the side of a building before punching in to the inverter, does this require rapid shutdown?  Is this PV system considered &quot;on&quot; a building?<br>


<br>
Aaron<br>
<br>
Aaron Mandelkorn<br>
Owner/Solar Specialist<br>
Renewable Energy Outfitters<br>
<a href="tel:719-221-5249" value="+17192215249" target="_blank">719-221-5249</a><br>
<a href="tel:970-596-3744" value="+19705963744" target="_blank">970-596-3744</a><br>
<a href="http://www.reosolar.com" target="_blank">www.reosolar.com</a><br>
<a href="mailto:reosolar@gmail.com" target="_blank">reosolar@gmail.com</a><br>
<br>
<br>
</blockquote>
<br>
______________________________<u></u>_________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.<u></u>org</a><br>
<br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>options.cgi/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>pipermail/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.<u></u>htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</div></div></blockquote></div><br></div>
<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div>