<html><head><meta http-equiv="content-type" content="text/html; charset=utf-8"></head><body dir="auto"><div>I agree, the pre insulated splices are okay for if you need an extension in a box, that stays dry, and the wire isn't pushed up against something. Otherwise apply separate heat shrink after the splice. Just don't forget to slip it on the wire before splicing!</div><div><br></div><div>I kind of like the idea of a properly torqued set screw splice with insulated heatshrink. There's got to be a direct bury kit available.&nbsp;</div><div><br>Brian</div><div><br>On Jun 25, 2014, at 2:01 PM, Ray Walters &lt;<a href="mailto:ray@solarray.com">ray@solarray.com</a>&gt; wrote:<br><br></div><blockquote type="cite"><div>
  
    <meta content="text/html; charset=ISO-8859-1" http-equiv="Content-Type">
  
  
    <div class="moz-cite-prefix">I've had butt splices fail, due to a
      ratchet release type crimper that didn't pinch the wires tight
      enough. <br>
      I now use a good old Klein crimper that puts a big indent on one
      side.&nbsp; The problem with this however, is that it damages the built
      in insulation.&nbsp; My favorite butt splice is uninsulated, and then
      slide adhesive shrink wrap up tubing up over the connection
      after.&nbsp; We use these on submersible pumps that are 100 ft under
      water with no issues.<br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 6/25/2014 11:43 AM, Nathan Charles wrote:<br>
    </div>
    <blockquote cite="mid:CANdZe6+2dMkfPYnprHwx5sySU6gWvp6epFO7g3KW=KU4kASixA@mail.gmail.com" type="cite">
      <div dir="ltr">Hi All,
        <div><br>
        </div>
        <div>Has anybody had success with these butt splices with the
          adhesive shrink tubing? &nbsp;<a moz-do-not-send="true" href="http://www.mcmaster.com/#butt-splices/=skb9qs" target="_blank">http://www.mcmaster.com/#butt-splices/=skb9qs</a></div>
        <div><br>
        </div>
        <div>Best,</div>
        <div><br>
        </div>
      </div>
      <div class="gmail_extra"><br>
        <br>
        <div class="gmail_quote">On Wed, Jun 25, 2014 at 1:12 PM, August
          Goers <span dir="ltr">&lt;<a moz-do-not-send="true" href="mailto:august@luminalt.com" target="_blank">august@luminalt.com</a>&gt;</span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">Hi All -<br>
            <br>
            We have been using outdoor Ideal brand wire nuts (the blue
            ones packed<br>
            with waterproof gel/grease) for all of our residential DC
            side splices<br>
            (typically #10 wire) for 10 years now and have never had a
            single problem.<br>
            If the installers properly strip the conductors and follow
            the<br>
            instructions I feel that these wire nuts make very robust
            connections. We<br>
            always do a good pull test after twisting the wire nut on. I
            would never<br>
            recommend standard wire nuts without the grease and have
            seen these fail<br>
            numerous times during inspections of systems installed by
            others.<br>
            Insulated terminal blocks also work well but don't have that
            nice<br>
            waterproof grease in them to help avoid moisture issues. You
            can wrap them<br>
            with a good splicing tape to help keep moisture out but the
            cost for these<br>
            connections is significantly higher than wire nuts:<br>
            <br>
            <a moz-do-not-send="true" href="http://solutions.3m.com/wps/portal/3M/en_US/EMDCI/Home/Products/Catalog/%7E?%0AN=5433135&amp;rt=c3" target="_blank">http://solutions.3m.com/wps/portal/3M/en_US/EMDCI/Home/Products/Catalog/~?<br>
              N=5433135&amp;rt=c3</a><br>
            <br>
            Normally I error on the robust conservative side of the
            installation<br>
            spectrum but in this case it sounds like I may not.<br>
            <br>
            Just my $0.02<br>
            <br>
            Best, August<br>
            <br>
            <br>
            -----Original Message-----<br>
            From: RE-wrenches [mailto:<a moz-do-not-send="true" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>]
            On<br>
            Behalf Of William Miller<br>
            Sent: Wednesday, June 25, 2014 8:40 AM<br>
            To: RE-wrenches<br>
            Subject: Re: [RE-wrenches] AFCI disturbances.<br>
            <br>
            Richard:<br>
            <br>
            Possibly. I think I prefer din mount connector blocks.
            However, if a wire<br>
            nut can arc internally a connector block might also. I am
            still wondering<br>
            about this concept.<br>
            <br>
            William<br>
            <br>
            Miller Solar<br>
            <br>
            &gt; On Jun 25, 2014, at 6:09 AM, <a moz-do-not-send="true" href="mailto:Richard.L.Ratico@valley.net">Richard.L.Ratico@valley.net</a>
            (Richard L<br>
            Ratico) wrote:<br>
            &gt;<br>
            &gt; William,<br>
            &gt; Would UL listed crimp sleeves be an acceptable
            substitute where you<br>
            &gt; would otherwise use wirenuts?<br>
            &gt;<br>
            &gt; Dick Ratico<br>
            &gt; Solarwind Electric<br>
            &gt;<br>
            &gt;<br>
            &gt; --- You wrote:<br>
            &gt; Bob-O:<br>
            &gt;<br>
            &gt;<br>
            &gt;<br>
            &gt; When you say verboten, what does that mean? &nbsp;Not
            kosher? &nbsp;Frowned upon?<br>
            &gt; Disallowed by law???<br>
            &gt;<br>
            &gt;<br>
            &gt;<br>
            &gt; I am quite curious about this subject. &nbsp;Here is what I
            have learned so<br>
            far:<br>
            &gt;<br>
            &gt;<br>
            &gt;<br>
            &gt; This is a unique case where we are replacing 3 dead SMA
            U series<br>
            &gt; inverters with 2 US series inverters. &nbsp;The U series
            seem to all be<br>
            &gt; dying at about 12 to 14 years of age. &nbsp;We have about a
            dozen of these<br>
            &gt; to swap on our calendar and expect more. &nbsp;It may be
            that to do this<br>
            &gt; right requires that we pull new wire from the arrays.
            &nbsp;This makes the<br>
            job a lot more expensive.<br>
            &gt;<br>
            &gt;<br>
            &gt;<br>
            &gt; We have never used a wire nut on a PV lead until this
            project. &nbsp;It's<br>
            &gt; not that we disapprove of wire nuts in general, it is
            because we know<br>
            &gt; that if we were to use them regularly we would
            eventually have failures<br>
            and call backs.<br>
            &gt; We allow only one splice in a PV lead: between the
            cable provided by<br>
            &gt; the manufacturer of the module and a bulkhead mounted
            MC4 connector<br>
            &gt; direct to THWN in conduit<br>
            &gt; (<a moz-do-not-send="true" href="http://millersolar.com/MillerSolar/practices/PV_wiring/PV_Cable_wirin" target="_blank">http://millersolar.com/MillerSolar/practices/PV_wiring/PV_Cable_wirin</a><br>
            &gt; g/_PV_<br>
            &gt; Cable_Wiring.html).<br>
            &gt;<br>
            &gt;<br>
            &gt;<br>
            &gt; We checked the manufacturer's listing and the wire nuts
            are rated for<br>
            &gt; 600 volts. &nbsp;We do use wire nuts on AC circuits, such as
            switch and<br>
            &gt; receptacle circuits in a power room.<br>
            &gt;<br>
            &gt;<br>
            &gt;<br>
            &gt; A tech at SMA told me that wire nuts "arc internally to
            the spring"<br>
            &gt; causing the AFCI faults. &nbsp;I am not aware of any process
            of "internal<br>
            &gt; arcing." &nbsp;To me, arcing means, as per the dictionary
            definition: "a<br>
            &gt; luminous bridge formed in a gap between two
            electrodes." &nbsp;The same<br>
            &gt; tech told me to solder the leads and apply shrink
            tubing. &nbsp;I don't<br>
            &gt; believe this is an approved method. &nbsp;By the way, we
            have spliced leads<br>
            &gt; on both US series inverters and only one is exhibiting
            AFCI<br>
            disturbances.<br>
            &gt;<br>
            &gt;<br>
            &gt;<br>
            &gt; I do favor mounted terminal blocks, either screw or
            tubular type. I<br>
            &gt; need to check if the Amp model we stock are 600 volt
            rated.<br>
            &gt;<br>
            &gt;<br>
            &gt;<br>
            &gt; I was told by another representative from SMA that on a
            ground-mount<br>
            &gt; system it is legal to disable the AFCI protection.<br>
            &gt;<br>
            &gt;<br>
            &gt;<br>
            &gt; I will be troubleshooting this job tomorrow and I will
            let you all<br>
            &gt; know what I learn.<br>
            &gt;<br>
            &gt;<br>
            &gt;<br>
            &gt; William Miller<br>
            &gt; --- end of quote ---<br>
            &gt; _______________________________________________<br>
            &gt; List sponsored by Redwood Alliance<br>
            &gt;<br>
            &gt; List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            &gt;<br>
            &gt; Change listserver email address &amp; settings:<br>
            &gt; <a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            &gt;<br>
            &gt; List-Archive:<br>
            &gt; <a moz-do-not-send="true" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist</a><br>
            &gt; .html<br>
            &gt;<br>
            &gt; List rules &amp; etiquette:<br>
            &gt; <a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
            &gt;<br>
            &gt; Check out or update participant bios:<br>
            &gt; <a moz-do-not-send="true" href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
            &gt;<br>
            _______________________________________________<br>
            List sponsored by Redwood Alliance<br>
            <br>
            List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change listserver email address &amp; settings:<br>
            <a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive:<br>
            <a moz-do-not-send="true" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm</a><br>
            l<br>
            <br>
            List rules &amp; etiquette:<br>
            <a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out or update participant bios:<br>
            <a moz-do-not-send="true" href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
            _______________________________________________<br>
            List sponsored by Redwood Alliance<br>
            <br>
            List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change listserver email address &amp; settings:<br>
            <a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a moz-do-not-send="true" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
            <br>
            List rules &amp; etiquette:<br>
            <a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out or update participant bios:<br>
            <a moz-do-not-send="true" href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
            <br>
          </blockquote>
        </div>
        <br>
        <br clear="all">
        <div><br>
        </div>
        -- <br>
        <div dir="ltr">Nathan Charles
          <div>Engineer<br>
            <div>NABCEP Certified PV Installation Professional
              #042013-20</div>
          </div>
          <div>Paradise Energy Solutions</div>
          <div>
            (717) 283-2021 direct</div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  

</div></blockquote><blockquote type="cite"><div><span>_______________________________________________</span><br><span>List sponsored by Redwood Alliance</span><br><span></span><br><span>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></span><br><span></span><br><span>Change listserver email address &amp; settings:</span><br><span><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br><span></span><br><span>List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a></span><br><span></span><br><span>List rules &amp; etiquette:</span><br><span><a href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a></span><br><span></span><br><span>Check out or update participant bios:</span><br><span><a href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a></span><br><span></span><br></div></blockquote></body></html>