The breakers in common commercially available outdoor breaker boxes are
for dry locations only, and the boxes are NEMA 3R. <br><br>
Mounting a breaker under a solar module could present a code problem, as
the breakers are not readily available.&nbsp; <br><br>
At 03:19 PM 4/24/2014, you wrote:<br>
<blockquote type=cite class=cite cite="">If you are mounting under panels
(which is my preference to keep it out of the elements and for
aesthetics), I still recommend the Soladeck. It accepts other DIN rail
mounted breakers... shop around...<br><br>
<br>
Jason Szumlanski \ Vice President<i><br>
</i>
<a href="http://s.wisestamp.com/links?url=http%3A%2F%2FFafcoSolar.com&amp;sn=amFzb25Ac3p1bWxhbnNraS5jb20%3D">
<img src="http://www.fafcosolar.com/download/576/Email-Signature-Logo.png" width=150 height=87 alt="[]">
</a></i><br>
Tel: 239-574-1500<br>
 <br><br>
<br>
On Wed, Apr 23, 2014 at 4:48 PM, Kirpal Khalsa
&lt;<a href="mailto:solarworks@gmail.com">solarworks@gmail.com</a>&gt;
wrote:<br>

<dl>
<dd>Friends,<br>

<dd>I just discovered that Midnite Solar also has a 3 circuit combiner
mountable down to a 3/12 pitch for AC micros at 240VAC.  They have a
fingered buss bar that has offsets to catch every other pole on the dual
pole breaker sets.....in addition it has their external lockable, visible
disconnect on the exterior of the box.......<br><br>

<dd>So am discovering that there are options......I will probably use the
midnite solar option as the breakers are a small fraction of the cost of
the breakers used int he Soladeck...<br>

<dd>Thanks for all the help...<br>

<dd>Cheers,<br><br>
<br>

<dd>Sunny Regards,<br>

<dd>Kirpal Khalsa<br>

<dd>NABCEP Certified PV Installation Professional<br>

<dd>Renewable Energy Systems<br>

<dd><a href="http://www.oregonsolarworks.com">www.oregonsolarworks.com</a>
<br>

<dd><a href="tel:541-218-0201">541-218-0201</a> m<br>

<dd><a href="tel:541-299-0402">541-299-0402</a> o<br><br>
<br>

<dd>On Wed, Apr 23, 2014 at 1:23 PM, Jason Szumlanski
&lt;<a href="mailto:jason@fafcosolar.com">jason@fafcosolar.com</a>&gt;
wrote:<br>

<dl>
<dd>While the interior of a raceway in a wet location is considered a wet
location, the interior of a NEMA 3R enclosure is not.. The breakers need
not be listed for use in wet locations. That's the interpretation of all
area AHJs here, and there is tons of evidence to support this logical
conclusion (NM cable into exterior mounted NEMA 3R disconnects, switch
enclosures; NEMA 1 enclosures inside larger NEMA 3R enclosures,
etc.)<br><br>

<dd>I hope I didn't just open a can or worms... :)<br><br>

<dd>Jason Szumlanski<br><br>

<dd>\u200bFafco Solar\u200b<br><br>
<br><br>

<dd>On Wed, Apr 23, 2014 at 3:12 PM, Glenn Burt
&lt;<a href="mailto:glenn..burt@glbcc.com">glenn.burt@glbcc.com</a>&gt;
wrote:<br>

<dl><br>

<dd>Are these breakers listed for use in wet locations?<br><br>

<dd> <br><br>

<dd>From:</b>
<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">
re-wrenches-bounces@lists.re-wrenches.org</a>
[<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" eudora="autourl">
mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of
</b>Jason Szumlanski<br>

<dd>Sent:</b> Wednesday, April 23, 2014 1:51 PM<br>

<dd>To:</b>
<a href="mailto:chris@solarandwindfx.com">chris@solarandwindfx.com</a>;
RE-wrenches<br>

<dd>Subject:</b> Re: [RE-wrenches] Stainless NEMA4x load center,
SolarDeck w/ breakers<br><br>

<dd> <br><br>

<dd>Here is exactly what I ordered:<br><br>

<dd> <br><br>

<dd>(1) RST0760-41AD Soladeck AC/DC Combiner Box<br><br>

<dd>(1) RST0784AC-3K Soladeck AC 3 Circuit Busbar Kit<br><br>

<dd>(2) RST1455.20 ABB Mini Circuit Breaker 120/240VAC 20A<br><br>

<dd>(1) RST1455.15 ABB Mini Circuit Breaker 120/240VAC 15A<br><br>

<dd>(1) RST1440..080 Soladeck Power Block 600V 80A<br><br>

<dd> <br><br>

<dd>\u200bThis model has a cover that is bumped out to fit breakers. Here is
a pic of the closed up box.<br><br>

<dd> <br><br>

<dd>
\u200b<img src="cid:7.1.0.9.0.20140428101646.05ca82b8@redwoodalliance.org.6" width=562 height=224 alt="Inline image 1">
<br><br>

<dd> <br><br>

<dd>Again, I'm not really happy with the way I brought the Enphase cables
into this \u200bSoladeck. The knockout center-points provided by the
manufacturer are too close together to accommodate five water-tight
glands, so I used some offsets to make more space. If it wasn't my own
house, I would have wanted it to look much prettier for a
customer.<br><br>

<dd> <br><br>

<dd>One thing I highly recommend is along the top and sides to use
sealant as indicated in the manual, then sprinkle a generous amount of
granules in the sealant. Otherwise the cover and your fingers get gummed
up when taking the cover off.<br><br>

<dd> <br><br>

<dd>\u200bThe manufacturer's website and documentation is woefully
inadequate for this product. They need to clarify it, obviously, based on
this discussion if they want to sell more. It's a great solution
IMO.\u200b<br><br>

<dd> <br><br>

<dd>Jason Szumlansk\u200bi<br><br>

<dd>Fafco Solar<br><br>

<dd> <br><br>

<dd> <br><br>

<dd>On Wed, Apr 23, 2014 at 12:01 PM, Chris Schaefer
&lt;<a href="mailto:chris@solarandwindfx.com">chris@solarandwindfx.com</a>
&gt; wrote:<br><br>

<dd>Jason,<br><br>

<dd>          &nbsp; I love the picture. Just ran into this a
few days ago on an install. Had two older SolarDeck Model 0780 in stock.
I had the same two pole breakers and attempted to install them here in
the shop before I went out to the project as I was afraid their height
would not allow the cover to seal. And it did not. It appears you have
ABB breakers and I just tried them and they don\u2019t fit either. Now if
you look at your link it shows and states fuse holders, which do fit.
I\u2019m wondering if the newer models in your link are just a little bit
taller than the older models I had in stock. I don\u2019t see size specs on
their web site. Can you please provide the model# you show in your
photo?<br><br>

<dd> <br><br>

<dd>Christopher Schaefer<br><br>

<dd>                              &nbsp;
Chris Schaefer\u2019s<br><br>

<dd>
<img src="cid:7.1.0.9.0.20140428101646.05ca82b8@redwoodalliance.org.7" width=353 height=72 alt="SolarWindFX">
<br><br>

<dd>                    Tel/Fax
<a href="tel:585-229-2083">585-229-2083</a> or Cell
<a href="tel:585-748-1870">585-748-1870</a>&nbsp; <br>
</i><br>

<dd>     5115 South Hill Road ~ Canandaigua New York 14424<br>
</i><br>

<dd><a href="http://www.solarandwindfx.com">www.solarandwindfx.com</a> ~
E-mail:
<a href="mailto:chris@solarandwindfx.com">chris@solarandwindfx.com</a><br>
</i><br>

<dd>
<img src="cid:7.1.0.9.0.20140428101646.05ca82b8@redwoodalliance.org.8" width=60 height=81 alt="[]">
<br><br>

<dd>
<img src="cid:7.1.0.9.0.20140428101646.05ca82b8@redwoodalliance.org.9" width=70 height=76 alt="[]">
<br><br>

<dd>
<img src="cid:7.1.0.9.0.20140428101646.05ca82b8@redwoodalliance.org.10" width=88 height=81 alt="[]">
<br><br>

<dd> <br><br>

<dd> <br><br>
<div align="center">
<dd> <br>
</div>
<br>
<div align="center">
<dd> <br>
</div>
<br>
<div align="center">
<dd> <br>
</div>
<br>

<dd> <br><br>
<br>

<dd>Thomas Jefferson, the author of our great Constitution, once said,
&quot;democracy&quot; will cease to exist               
                              &nbsp;   
                  when you take away from those who are
willing to work and give to those who would not.&quot;<br><br>

<dd> <br><br>

<dd>From:</b>
<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">
re-wrenches-bounces@lists.re-wrenches.org</a>
[<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" eudora="autourl">
mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of
</b>Jason Szumlanski<br>

<dd>Sent:</b> Wednesday, April 23, 2014 11:36<br>

<dd>To:</b> RE-wrenches<br>

<dd>Subject:</b> Re: [RE-wrenches] Stainless NEMA4x load center<br><br>

<dd> <br><br>

<dd>See my other response, but you should definitely consider SolaDeck in
this case.. You want SolaDeck Model 0786-41. Make sure you order the
correct breakers, bus bars, and Neutral terminal block.<br><br>

<dd> <br><br>

<dd>
<a href="http://www.rstcenterprises.com/soladeck/products/1741_combiner_enclosure.phtml">
http://www.rstcenterprises.com/soladeck/products/1741_combiner_enclosure.phtml</a>
<br><br>

<dd> <br><br>

<dd>\u200bThe attached picture is the Soladeck on my 3-string \u200bEnphase
system at home (note: neutral block was not on DIN rail yet). There are
four neutrals on the bottom of the N block because I center-fed one
inverter string, so I had four sets of Enphase cable coming into the box,
which is admittedly a little tight. If you need to do this, I recommend
transitioning to THWN in a separate combiner and just bringing in three
strings through one or two conduits.<br><br>

<dd> <br><br>

<dd> <br><br>

<dd>
\u200b<img src="cid:7.1.0.9.0.20140428101646.05ca82b8@redwoodalliance.org.11" width=242 height=236 alt="Inline image 1">
\u200b<br><br>

<dd> <br><br>

<dd>Jason Szumlanski<br><br>

<dd>\u200bFafco Sola<br><br>

<dd>\u200br\u200b<br><br>

<dd> <br><br>

<dd>On Wed, Apr 23, 2014 at 11:17 AM, Kirpal Khalsa
&lt;<a href="mailto:solarworks@gmail.com">solarworks@gmail.com</a>&gt;
wrote:<br><br>

<dd>Drake.....we want it to mount flush to the slope of a sloped
roof....The NEMA 3R are supposed to be mounted vertically....This is for
a large residential Enphase system and we wanted to combine the circuits
on the roof and bring one set of conductors down.....<br><br>

<dd>I did find one custom made by Eaton(Cutler Hammer), but....$952 my
cost is too much..I have had them make me one out of fiberglass in the
past but it is about 3 years into its roof mount life and showing signs
of UV degradation...looking for other options....I think i will dig a
little deeper at Midnite Solar.....They may have something....Theirs and
Outback's PV combiners are rated to be mounted at a slope....i think it
is down to 14 degrees pitch (3/12)<br><br>

<dd>Thanks.<br><br>
<br>

<dd>Sunny Regards,<br>

<dd>Kirpal Khalsa<br>

<dd>NABCEP Certified PV Installation Professional<br>

<dd>Renewable Energy Systems<br>

<dd><a href="http://www.oregonsolarworks.com">www.oregonsolarworks.com</a>
<br><br>

<dd><a href="tel:541-218-0201">541-218-0201</a> m<br>

<dd><a href="tel:541-299-0402">541-299-0402</a> o<br><br>

<dd> <br><br>

<dd>On Wed, Apr 23, 2014 at 8:11 AM, Drake
&lt;<a href="mailto:drake.chamberlin@redwoodalliance.org">
drake.chamberlin@redwoodalliance.org</a>&gt; wrote:<br><br>

<dd>That would be a nice piece of hardware. Is there any reason you can't
use a NEMA 3R panel?&nbsp; They are used on roofs quite a bit, and are
readily available.&nbsp; The Square D, 8 space, outdoor box should work
in most rooftop environments for the purpose you describe.&nbsp;
<br><br>
<br>

<dd>At 06:18 PM 4/21/2014, you wrote:<br>

<dl><br>

<dd>Hello Friends!<br>

<dd>Anyone have a lead for NEMA 4x</u> stainless load centers (electrical
panel)? Â Looking for 4 circuit version rated at about 60-100A @
240VAC.<br><br>
<br>

<dd>Would like to use it for rooftop combiner for 3 Enphase inverter
output circuits.<br>

<dd>Thank you!!<br><br>

<dd>Sunny Regards,<br>

<dd>Kirpal Khalsa<br>

<dd>NABCEP Certified PV Installation Professional<br>

<dd>Renewable Energy Systems<br>

<dd><a href="http://www.oregonsolarworks.com">www.oregonsolarworks.com</a>
<br>

<dd><a href="tel:541-218-0201">541-218-0201</a><br><br>

<dd>______________<br><br>

</dl>
</dl><br><br>

<dd>_______________________________________________<br>

<dd>List sponsored by Home Power magazine<br><br>

<dd>List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br><br>

<dd>Change email address &amp; settings:<br>

<dd>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches..org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>

<dd>List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>

<dd>List rules &amp; etiquette:<br>

<dd><a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a><br><br>

<dd>Check out participant bios:<br>

<dd><a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a><br><br>
<br>

</dl><br><br>

<dd>_______________________________________________<br>

<dd>List sponsored by Home Power magazine<br><br>

<dd>List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br><br>

<dd>Change email address &amp; settings:<br>

<dd>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches..org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>

<dd>List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>

<dd>List rules &amp; etiquette:<br>

<dd><a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a><br><br>

<dd>Check out participant bios:<br>

<dd><a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a><br><br>
<br>

</dl><br>
Content-Type: image/png; name=&quot;image007.png&quot;<br>
Content-Disposition: inline; filename=&quot;image007.png&quot;<br>
Content-ID: &lt;image007.png@01CF5F06.719C60B0&gt;<br>
X-Attachment-Id: 2c7c4a8b63a5163e_0.0.6<br><br>
Content-Type: image/jpeg; name=&quot;image006.jpg&quot;<br>
Content-Disposition: inline; filename=&quot;image006.jpg&quot;<br>
Content-ID: &lt;image006.jpg@01CF5F06.719C60B0&gt;<br>
X-Attachment-Id: 2c7c4a8b63a5163e_0.0.5<br><br>
Content-Type: image/jpeg; name=&quot;image004.jpg&quot;<br>
Content-Disposition: inline; filename=&quot;image004.jpg&quot;<br>
Content-ID: &lt;image004.jpg@01CF5F06.719C60B0&gt;<br>
X-Attachment-Id: 2c7c4a8b63a5163e_0.0.3<br><br>
Content-Type: image/png; name=&quot;image002.png&quot;<br>
Content-Disposition: inline; filename=&quot;image002.png&quot;<br>
Content-ID: &lt;image002.png@01CF5F06.719C60B0&gt;<br>
X-Attachment-Id: 2c7c4a8b63a5163e_0.0.1<br><br>
Content-Type: image/jpeg; name=&quot;image005.jpg&quot;<br>
Content-Disposition: inline; filename=&quot;image005.jpg&quot;<br>
Content-ID: &lt;image005.jpg@01CF5F06.719C60B0&gt;<br>
X-Attachment-Id: 2c7c4a8b63a5163e_0.0.4<br><br>
Content-Type: image/png; name=&quot;image003.png&quot;<br>
Content-Disposition: inline; filename=&quot;image003.png&quot;<br>
Content-ID: &lt;image003.png@01CF5F06.719C60B0&gt;<br>
X-Attachment-Id: 2c7c4a8b63a5163e_0.0.2<br><br>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote></body>
</html>