<div dir="ltr">Thanks Dave, I think I was thinking about "on" in the wrong way.<div><br></div><div>-N</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Tue, Apr 15, 2014 at 11:18 AM, Dave Click <span dir="ltr"><<a href="mailto:daveclick@fsec.ucf.edu" target="_blank">daveclick@fsec.ucf.edu</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div bgcolor="#FFFFFF" text="#000000">
<font face="Helvetica, Arial, sans-serif">Nathan, 690.12 only
applies to "PV system circuits installed on or in buildings" so
that might be your answer. You'd only be affected by 690.12 if
you're running to an interior inverter. So- your strategy of
exterior conduit to wall-mounted inverters on the exterior of a
building won't be subjected to the 690.12 requirement.<br>
<br>
</font><div><div class="h5">
<div>On 2014/4/15, 11:09, Nathan Charles
wrote:<br>
</div>
<blockquote type="cite">
<div dir="ltr">Hi All,
<div><br>
</div>
<div>I have a follow up to this discussion. What's the proper
way to think through this regarding ground mounts? It seems
to me that if the goal is to protect firefighters then running
a conduit underground and coming up to outdoor wall mounted
inverters is keeping in the spirit of things, but I'm not sure
if the language of 690.12 supports this. Am I mistaken? Do
you have any best practice advice for this scenario?</div>
<div><br>
</div>
<div>Best regards,</div>
<div>-N</div>
</div>
<div class="gmail_extra"><br>
<br>
<div class="gmail_quote">On Tue, Jan 21, 2014 at 12:36 PM, Drake
<span dir="ltr"><<a href="mailto:drake.chamberlin@redwoodalliance.org" target="_blank">drake.chamberlin@redwoodalliance.org</a>></span>
wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div>
<br>
Bill,<br>
<br>
It is good to see that energized conductors are going to
be disconnected
near the arrays. I've been an advocate of disconnecting
these conductors
by ground fault sensing equipment since ground fault
detection was first
implemented in the code. If contactors are to be installed
on roofs, it
likely won't be long before both ground faults and arc
faults are
automatically cleared. <br>
<br>
When the requirement for AC arc fault branch circuit
protection was first
put in the NEC, it was postdated to allow time for the
electrical
industry to adapt. This new remote disconnecting
requirement does not
provide any lead time. <br>
<br>
As the 2014 NEC is adopted in various jurisdictions,
inspectors may feel
that it is necessary to disallow systems without the newly
required
disconnect feature. This may result in serious problems
for solar
companies and customers, as well as manufacturers. <br>
<br>
The protection of firefighters is essential. The
implementation of
renewables is essential also. Insurance claims for weather
related,
global warming-triggered climatic disasters are rising
exponentially.
Extreme weather related events result in major loss of
life and billions
of dollars in property damage. Atmospheric CO2 levels
continue to climb
from the burning of fossil fuels. This is a crisis of
global proportions.
<br>
<br>
My request for code writers is to please take into account
the effect
that inserting new rules into the NEC may have on the
stability of
renewable energy, and implement new requirements in a way
that will allow
for a smooth interface.<br>
<br>
Thank you, <br>
<br>
Drake <br>
<br>
<a name="14565f780353c402_143b5dffb7433f19__MailAutoSig"></a>Drake
Chamberlin<br>
<i>Athens Electric LLC<br>
OH License 44810<br>
CO License 3773<br>
NABCEP Certified Solar PV <br>
<a href="tel:740-448-7328" value="+17404487328" target="_blank">740-448-7328</a><br>
</i><a href="http://athens-electric.com/" target="_blank">http://athens-electric.com/<br>
<br>
<br>
</a>At 12:45 PM 1/16/2014, you wrote:<br>
<blockquote type="cite">Content-Type:
multipart/alternative;<br>
boundary="----=_NextPart_000_0F94_01CF129F.BCC65BD0"<br>
Content-Language: en-us
<div>
<div><br>
<br>
Jeffrey,<br>
<br>
Sounds like you need to get involved in the code
making process since you
have so many good ideas on how to improve the
language. I like
confrontational discussions as long as they lead to
a better
understanding and constructive outcomes.<br>
<br>
About 30 people worked on this language, so it is
definitely not perfect.
However, I don\u2019t think it is quite as bad as you
make it out to be. I
wanted to jump in since some of your conclusions
were not correct.<br>
<br>
This is a circuit requirement, not a disconnecting
means requirement,
since it has to do with shock hazard of PV circuits
in and around a
building. This is for firefighter safety. 30V is the
international
standard for touch safe in a wet location. 240VA is
to set a limit on the
available power on a circuit. Contactor combiners,
which would be part of
a compliant solution, have 24V control circuits. The
other reasoning for
240VA is that internally, 72-Cell PV modules can be
divided into segments
of this power level for the foreseeable future (more
on that another
day).<br>
<br>
If the conductors stay outside, you have 10\u2019 from
the array to place your
shutdown device. On large central systems, this
would likely be a
contactor combinermost manufacturers sell these. If
the conductors are
going immediately into the building, as with
residential and integrated
systems, a shutdown device would have to be within
5\u2019 of entering the
building. If goes outside for a while, then inside
the building, the
total length could be no more than 10\u2019 and no more
than 5\u2019 inside the
buildingthis is not additive. Remember, all this is
for firefighter
safety.<br>
<br>
As Brian Mehalic and others have pointed out, the
language does not
specify where the shutdown initiating device is to
be located. The lack
of detail is more for flexibility than it is to give
an AHJ license to
make an installer do anything they want. <br>
<br>
With grid-tie only systems (no battery backup), it
would be most
convenient and cost effective to have a system that
initiates the
shutdown on loss of utility. In this way, a
firefighter can do what they
normally do, shut down utility power to the
building, and the rapid
shutdown would automatically initiate. This does not
necessitate an
additional disconnecting means for a load-side PV
connection. The main
breaker could be the initiating device. For a
supply-side connection, the
NEC already requires that the PV disconnect switch
be located adjacent to
the service disconnecting means (article 230).<br>
<br>
The biggest issue with string inverters (central
inverters) is that there
is a need to shutdown the capacitor input side of
the inverter since that
stays energized for 5 minutes or more. The 10
seconds was to provide a
means to rapidly discharge the capacitors rather
than requiring a relay
or tripping device. Doing something other than a
relay will require a
test laboratory to evaluate the functionguess
what?we don\u2019t have a
standard yet to evaluate those products. Sounds like
you might want to
work on that committee.<br>
<br>
It is more complicated for battery backup systems.
Midnite Solar\u2019s
birdhouse products are the best I have seen so far
to address this
concern. Since dc and ac circuits are not
differentiated, battery backup
systems need to have a shutdown process that works
independently of a
utility outage for obvious reasons, and it must
shutdown both the dc
circuits and the backup ac circuits. A separate
switch, like the
birdhouse, would be necessary that only controls
these functions in an
emergency situation.<br>
<br>
Is the language not detailedpossibly. This was done
to provide
flexibility rather than create problems. Fire
departments have been
requiring rooftop disconnects for years in
California. These disconnects
are nearly worthless from a shock prevention point
of view since
capacitors in the inverter stay charged or there are
multiple
disconnecting means feeding each other. We have been
trying to hold the
fire community off of rooftop disconnect
requirements so we could work on
a solution that actually does what they want it to
do. There is a long
discussion on this in the appendix of my
\u201cUnderstanding the CalFire
Guidelines\u201d document on the SolarABCs website.<br>
<br>
The 2014 NEC language was a compromise worked out
with the solar industry
(yes string inverter companies as well) in response
to the first version
of the proposal which was to require module-level
shutdown. This is not
module-level shutdown, it is PV output circuit
shutdown (combiner box
shutdown is another way to look at it). However, the
2017 NEC cycle is
this year and there was a lot of talk about
requiring module-level
shutdown this time around. <br>
<br>
I hope this helps. I will be writing articles for
IAEI journal and other
periodicals on this subject since it was a very
far-reaching and
potentially confusing new requirement in the NEC.
Thanks for your
interest and let\u2019s keep the constructive dialogue
going on the subject.
It is time to get involved in the NEC update process
again.<br>
<br>
Bill Brooks.<br>
<br>
<b>From:</b> <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>
[<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">
mailto:re-wrenches-bounces@lists.re-wrenches.org</a>]
<b>On Behalf Of
</b>Jeffrey Quackenbush<br>
<b>Sent:</b> Thursday, January 16, 2014 1:09 AM<br>
<b>To:</b> RE-wrenches<br>
<b>Subject:</b> Re: [RE-wrenches] NEC 2014 690.12
Rapid Shutdown<br>
<br>
Wrenches,<br>
<br>
There is no guidance in the Code text for where the
shutdown should take
place. (1) says: "Requirements for controlled
conductors shall apply
only to PV system conductors of more than 1.5m (5')
in length inside a
building, or more than 3m (10') from a PV array."<br>
<br>
<br>
So, the provisions <i>apply if</i> the circuit 10'
from the array and 5'
inside a building, but no mention is made of where
the shutdown actually
needs take place in the circuit. In the video Bill
Brooks suggests that
the shutdown mechanism should also be placed within
this 10'/5' boundary
but that is just an inference -- nowhere in the text
is this actually
specified. If that was the intent of the Code
committee, then they've
done a poor job actually expressing it in English.<br>
<br>
I'm concerned that some AHJs will interpret this to
exclude all central
inverter systems (without the addition of
cost-inducing secondary DC-DC
converters like Tigo) because the combiner or
junction box can be many
feet from the actual beginning of a home run under
the array.
Alternately, permissive AHJs could allow this
function to be fulfilled
anywhere, meaning that the implementation won't meet
the intent of the
writers.<br>
<br>
I'm also concerned, as Isaac mentioned, that there
are no requirements
for how the shutdown be initiated, or that it
contains of the
accessibility and grouping requirements that are
always included for
disconnects. I really think this should be treated
and categorized as a
disconnect requirement, not a circuit requirement,
because that is the
ultimate function that's intended. <br>
<br>
I'm surprised none of the inverter manufacturers
have chosen to comment
here, as this could dramatically impact the sales of
central
inverters.<br>
<br>
Jeffrey Quackenbush<br>
<br>
<br>
<br>
<hr>
<a href="http://www.avast.com/" target="_blank">
<img src="http://static.avast.com/emails/avast-mail-stamp.png" alt="[]">
</a><a href="http://www.avast.com/" target="_blank"> </a><br>
<br>
This email is free from viruses and malware because
<a href="http://www.avast.com/" target="_blank">avast!
Antivirus</a> protection is
active. <br>
<br>
</div>
</div>
<div>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br>
<br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">
www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" target="_blank">
www.members.re-wrenches.org</a></div>
</blockquote>
</div>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br>
</blockquote>
</div>
<br>
<br clear="all">
<div><br>
</div>
-- <br>
<div dir="ltr">Nathan Charles
<div>Engineer<br>
<div>NABCEP Certified PV Installation Professional
#042013-20</div>
</div>
<div>Paradise Energy Solutions</div>
<div><a href="tel:%28717%29%20283-2021" value="+17172832021" target="_blank">(717) 283-2021</a> direct</div>
</div>
</div>
<br>
<fieldset></fieldset>
<br>
<pre>_______________________________________________
List sponsored by Home Power magazine
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>
Change email address & settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>
Check out participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>
</pre>
</blockquote>
<br>
</div></div></div>
<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br><div dir="ltr">Nathan Charles<div>Engineer<br><div>NABCEP Certified PV Installation Professional #042013-20</div></div><div>Paradise Energy Solutions</div>
<div>(717) 283-2021 direct</div></div>
</div>