<div dir="ltr">Hi Ray,<div><br></div><div>The Sunny Islands are capable of working with DC input if you include a shunt on the battery side (see page 52 here<a href="http://files.sma.de/dl/15216/SI4548_6048-US-TB_en-13w.pdf">http://files.sma.de/dl/15216/SI4548_6048-US-TB_en-13w.pdf</a>), and Midnite will have a comm box that makes it look like an SMA device in the SMA network. I&#39;m not sure if you still need this shunt if you include this in your design. This is supposed to be out any day now.</div>
<div><br></div><div>Sounds like a fun project.</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Tue, Mar 25, 2014 at 10:37 PM, Ray Walters <span dir="ltr">&lt;<a href="mailto:ray@solarray.com" target="_blank">ray@solarray.com</a>&gt;</span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Thanks Kevin;<br>
<br>
I follow what you are saying on the charge algorithm: both the inverter and charge controller are very smart, but aren&#39;t talking to each other, which makes for a dysfunctional family with the batteries being the neglected kids. In this case, I could see that a full on SMA solution would work nicely: Sunny boys AC coupled, SIs hooked up with the Multicluster box, etc.<br>

I yearn for those good, old days, when I could build dream systems, while charging full retail. Lately, I work twice as hard just to build systems that will still work on much tighter budgets.<br>
I&#39;ll hit up the folks at SMA, as I think that SIs will be in the mix in some fashion.<div class="im HOEnZb"><br>
<br>
R.Ray Walters<br>
CTO, Solarray, Inc<br>
Nabcep Certified PV Installer,<br>
Licensed Master Electrician<br>
Solar Design Engineer<br>
<a href="tel:303%20505-8760" value="+13035058760" target="_blank">303 505-8760</a><br>
<br></div><div class="HOEnZb"><div class="h5">
On 3/25/2014 10:08 PM, Kevin Pegg wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
Hi Ray,<br>
<br>
Suggest you give the techs a call @ SMA and get some design assistance. They are good.<br>
<br>
Sunny Islands can be used as regular inverter/charger units yes.<br>
<br>
&gt;From my experience, we have done 1 string of 3 SI inverters (ie 18 kW @ 120/208) without the multicluster box. Anything larger than 1 string we have always used the MC box. I believe it&#39;s required - or at least the control board that handles communication between inverters is required. The MC cabinet is very nicely done and makes inspectors very happy this is for sure.<br>

<br>
As far as DC input from charge controller ie Classic yes this is also possible. Screws up the inverter&#39;s very smart battery charge algorithm, however. So there is a trade-off there. It will depend how much this site is relying on diesel vs PV input.<br>

<br>
Kevin<br>
<br>
-----Original Message-----<br>
From: <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-<u></u>wrenches.org</a><br>
[mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@<u></u>lists.re-wrenches.org</a>]On Behalf Of Ray<br>
Walters<br>
Sent: March 25, 2014 4:37 PM<br>
To: RE-wrenches<br>
Subject: Re: [RE-wrenches] 208 3 phase Off Grid Inverter<br>
<br>
<br>
OK everyone is steering me towards the Sunny Island.  I can probably<br>
justify the inverter cost difference to the customer, then I found the<br>
SMA Multicluster Box for the SI. It seems like a glorified AC Combiner<br>
and transfer switch box, but it retails for over $20K! Yikes.<br>
Do we have to use that for a 3 phase install, or are there much lower<br>
cost alternatives. This is out of the country and does not need to be<br>
NEC2014 compliant. (maybe NEC 1956 compliant would be about in keeping<br>
with the rest of the wiring.......) This would be a budget buster for<br>
sure.<br>
<br>
R.Ray Walters<br>
CTO, Solarray, Inc<br>
Nabcep Certified PV Installer,<br>
Licensed Master Electrician<br>
Solar Design Engineer<br>
<a href="tel:303%20505-8760" value="+13035058760" target="_blank">303 505-8760</a><br>
<br>
On 3/25/2014 4:21 PM, Kevin Pegg wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
Hi Ray,<br>
<br>
I have several 3-phase off-grid inverter/battery/generator systems out there.<br>
<br>
- SMA Sunny Island is the best. Can scale to at least 180 kW, maybe more. Reliable &amp; very solid. I have several sites going over 2 years without a single second of power outage.<br>
- Xantrex XW. It can work in a 3-ph config, but it&#39;s not as stable system. We have taken to preventatively rebooting the systems every 4 months and that helps a lot - at least the outage can be planned and on our terms.<br>

- Outback has had so many power quality nightmares I won&#39;t go there anymore.<br>
- I believe Magnum has a 3-ph option but haven&#39;t installed one yet.<br>
<br>
SMA inverters are more expensive. And they work very well. They also have a very good battery charging algorithm and integral gen start control.<br>
<br>
Kevin<br>
<br>
-----Original Message-----<br>
From: <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-<u></u>wrenches.org</a><br>
[mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@<u></u>lists.re-wrenches.org</a>]On Behalf Of Ray<br>
Walters<br>
Sent: March 24, 2014 6:44 PM<br>
To: RE-wrenches<br>
Subject: [RE-wrenches] 208 3 phase Off Grid Inverter<br>
<br>
<br>
Hi All;<br>
<br>
I&#39;m exploring options for an off grid project with an existing 30 Kw<br>
Kohler wired for 208 vac 3 phase. The generator runs some 8 hp air<br>
compressors, so rewiring it is not an option. We&#39;re primarily<br>
interested in reducing gen run time from the current situation: 14 hrs/ day.<br>
So far, only the Outback VFX inverters seem capable of being wired in<br>
208, 3 phase, but according to the manual they can only be stacked 1<br>
inverter per leg. This limits the system to only 3 inverters total, or<br>
10.8 kW. I would like expandability beyond this.<br>
1) are there any other inverters available that I&#39;m over looking?<br>
2) Should I consider a transformer to convert from 208 vac/3phase to 240<br>
vac/ singe phase?<br>
<br>
We&#39;re not going to even try to run the compressors, just the other<br>
single phase loads, mostly 120 vac, but we have a couple of small air<br>
conditioners, that are currently running on 208 single phase. I believe<br>
they would run fine on 240 vac, as they have a name plate rating at 230 vac.<br>
3) We may possibly run 2 separate 3 inverter stacks and only tie<br>
together at the battery, but otherwise they would not be connected. This<br>
seems inefficient, and would require some load balancing of the various<br>
inverters.<br>
<br>
All help and discussion is greatly appreciated as always,<br>
<br>
</blockquote>
______________________________<u></u>_________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.<u></u>org</a><br>
<br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>options.cgi/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>pipermail/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.<u></u>htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
______________________________<u></u>_________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.<u></u>org</a><br>
<br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>options.cgi/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>pipermail/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.<u></u>htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br>
</blockquote>
<br>
______________________________<u></u>_________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.<u></u>org</a><br>
<br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>options.cgi/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>pipermail/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.<u></u>htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</div></div></blockquote></div><br><br clear="all"><div><br></div>-- <br><div><br></div><div><font color="#305A78" face="&#39;times new roman&#39;, serif"><br></font></div><div><br></div>Mac Lewis<br><br><span style="font-family:&#39;Times New Roman&#39;;font-size:medium;color:rgb(255,153,0)"><b><font face="Arial, Helvetica, sans-serif" size="3"><p align="left">
<font color="#000000" face="Verdana, Arial, Helvetica, sans-serif"><span style="font-size:small"><span style="font-family:arial;font-weight:normal;color:rgb(48,90,120)"><font face="&#39;times new roman&#39;, serif">&quot;Yo solo s que no s nada.&quot;</font><span style="font-weight:700;color:rgb(104,104,104)"><font face="&#39;times new roman&#39;, serif">-Scrates</font></span></span></span></font></p>
</font></b></span>
</div>