<div dir="ltr"><div class="gmail_default" style="font-family:verdana,sans-serif">Both the bus and conductors need to be rated for 217 amps minimum. As you mentioned, the bus is not a problem. The way I interpret it, the conductor size required would be after derate factors are applied. The rating of the conductor is ultimately dependent on the derate factors.</div>

<div class="gmail_default" style="font-family:verdana,sans-serif"><br></div><div class="gmail_default" style="font-family:verdana,sans-serif">If you can locate your subpanel adjacent to the main distribution panel, you may be able to use Exception #3 to 310.15(B)(2) by connecting the panels with a short nipple. I assume you are just looking at a number of conductor derate and not an ambient temperature derate.</div>

<br><div id="WISESTAMP_SIG_gmail_session"><div style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif"><div style="margin:0 0 8px 0"><p style="margin:0"><span><span>Jason Szumlanski</span></span></p><p style="margin:0">

</p><div class="gmail_default" style="font-family:verdana,sans-serif;display:inline">Fafco Solar</div><br>&nbsp;<p></p><div style="clear:both"></div></div><img src="https://wisestamp.appspot.com/pixview.gif?p=chrome&amp;v=3.31.0&amp;t=1393961350220&amp;u=ce9344a8140ce271" width="1" height="1"></div>

</div><div class="gmail_extra"><br><br><div class="gmail_quote">On Tue, Mar 4, 2014 at 12:05 PM, Kirk Herander <span dir="ltr">&lt;<a href="mailto:kirk@vtsolar.com" target="_blank">kirk@vtsolar.com</a>&gt;</span> wrote:<br>

<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div lang="EN-US" link="blue" vlink="purple"><div><p class="MsoNormal"><span style="font-size:14.0pt">Hello,<u></u><u></u></span></p>

<p class="MsoNormal"><span style="font-size:14.0pt">I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp breaker. My inverter breaker feeding the sub panel is 60 amps. So 225 a bus x 1.2 = 270 amps. That&rsquo;s less than the sum of the two breakers of 260 amps, so no issue there. The conductors between sub and main panel have to be rated for at least 260/1.2 = 217 amps, correct? Is this 217 amps before or after derating the conductor?<u></u><u></u></span></p>

<p class="MsoNormal"><span style="font-size:14.0pt"><u></u>&nbsp;<u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt"><u></u>&nbsp;<u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">Kirk Herander<u></u><u></u></span></p>

<p class="MsoNormal"><span style="font-size:14.0pt">VT Solar, LLC<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">dba Vermont Solar Engineering<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">NABCEP<sup>TM </sup>Certified Inaugural Certificant<u></u><u></u></span></p>

<p class="MsoNormal"><span style="font-size:14.0pt">NYSERDA-eligible Installer<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">VT RE Incentive Program Partner<u></u><u></u></span></p><p class="MsoNormal">

<span style="font-size:14.0pt"><a href="tel:802.863.1202" value="+18028631202" target="_blank">802.863.1202</a><u></u><u></u></span></p><p class="MsoNormal"><u></u>&nbsp;<u></u></p></div></div></blockquote></div><br></div></div>