<font color='black' size='2' face='arial'>Thanks for the feedback. &nbsp;Turned out to be 3 separate issues. &nbsp;The AC backfeed turned out to be mostly caused by a missing neutral to ground bond. &nbsp; With that corrected, the backfeed dropped from 30 volts to 2 volts on one leg only... still a puzzle. &nbsp;Other issues were a snow and ice covered regulator which may or may not have affected the starting., &nbsp;Also the magnetic pickup for frequency control was weak and the Kohler guy replaced it. &nbsp;At one point today the generator was just a pile of rubble in the snowbank... wish I had taken a picture. &nbsp;He got it all back together and it ran fine, we reconnected to the radian with the 2 volt backfeed and it worked fine. &nbsp;Time will tell if we still have a problem.&nbsp;<br>
<br>
<br>

<div style="font-family:arial,helvetica;font-size:10pt;color:black">-----Original Message-----<br>
From: Jerry Shafer &lt;jerrysgarage01@gmail.com&gt;<br>
To: RE-wrenches &lt;re-wrenches@lists.re-wrenches.org&gt;<br>
Sent: Mon, Feb 17, 2014 3:49 pm<br>
Subject: Re: [RE-wrenches] AC Backfeed from Radian.<br>
<br>




<div id="AOLMsgPart_2_616b11c6-de0c-4d49-80f9-c93b1f6184ea">

<div dir="ltr">If you disconnect the leads to the Benny from at the inverter do you still have this condition. I had a battery charged supply (ac) in the same conduit as the remote start and the transient voltage would be enough to signal z start up. Your issue is a little different but it might still be transient<br>


Jerry</div>


<div class="gmail_quote">On Feb 16, 2014 7:02 PM, "john" &lt;<a href="mailto:cvsolar@aol.com">cvsolar@aol.com</a>&gt; wrote:<br type="attribution"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<font color="black" face="arial">Wrenches,

<div>&nbsp; &nbsp; I have an off-grid installation with an Outback Radian using a Kohler RES 13 for backup. &nbsp;The generator has had problems from day one and has had control boards replaced and other work done on it. &nbsp;This system started out with a Magnum 4024AE but was undersized for the loads and battery size so we upgraded to the Radian. &nbsp;The current problem is the generator running erratically (frequency and voltage) and running rough. &nbsp;The Kohler repairman said that the problem is that the inverter had damaged the generator with a measured 12 VAC at the inverter side of the AC IN breaker when the generator is off. &nbsp;When I arrived, we started the generator with the MATE 3 and it worked fine for about 10 minutes charging at 4.5 kw and then the engine started running erratically. &nbsp;The frequency readout on the MATE 3 ranged from 56 Hz to 67 Hz and the voltage was sometimes steady at 238 and at times varying from 236 to 244. &nbsp;The MATE 3 showed several manual starts previously where the Initial voltage was 277 briefly (1 second) and then leveled out and locked on. Eventually the generator shut down with Error 13. &nbsp;We also had it fail to start with Locked Rotor error. &nbsp;I did measure 3.1 VAC on the AC out bus of the inverter when the generator was stopped. &nbsp;Is that small voltage present normal for the Radian and is there any way that could affect the generator? &nbsp; When I set the MATE 3 to DROP to disconnect the charging, we could still read the hz and Voltage at the bus and the erratic behavior continued. &nbsp;I think there are serious problems with the generator but the Kohler tech says it is the inverter interference . &nbsp;When we started the generator manually with the input breaker off, it ran erratic and eventually shut down. &nbsp;</div>




<div><br>

</div>



<div>The customer wants the generator guy and myself there tomorrow to figure out how to fix it. &nbsp; I say a new generator might take care of the problem but the customer doesn't want to hear this.</div>



<div>Any ideas? &nbsp;I have dealt with lots of generators and to me this seems like a worn out genny.&nbsp;</div>



<div><br>

</div>



<div>John Blittersdorf</div>



<div>Central Vermont Solar &amp; Wind &nbsp;<br>

<br>

<br>



<div style="font-size:10pt;font-family:arial,helvetica"><br>



<div>

<div lang="EN-US" bgcolor="#ffffff" vlink="purple" link="blue"><blockquote style="BORDER-LEFT:#000000 2px solid;PADDING-LEFT:5px;PADDING-RIGHT:0px;MARGIN-LEFT:5px;MARGIN-RIGHT:0px">

<div>
  

<div class="MsoNormal"><br>

</div>

</div>

</blockquote></div>

 



</div>

</div>

</div>

</font><br>
_______________________________________________<br>

List sponsored by Home Power magazine<br>

<br>

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>

<br>

Change email address &amp; settings:<br>

<a target="_blank" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>

<br>

List-Archive: <a target="_blank" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>

<br>

List rules &amp; etiquette:<br>

<a target="_blank" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>

<br>

Check out participant bios:<br>

<a target="_blank" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>

<br>

<br>
</blockquote></div>


</div>



<div id="AOLMsgPart_3_616b11c6-de0c-4d49-80f9-c93b1f6184ea" style="margin: 0px;font-family: Tahoma, Verdana, Arial, Sans-Serif;font-size: 12px;color: #000;background-color: #fff;">

<pre style="font-size: 9pt;"><tt>_______________________________________________
List sponsored by Home Power magazine

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>

</tt></pre>
</div>
 <!-- end of AOLMsgPart_3_616b11c6-de0c-4d49-80f9-c93b1f6184ea -->



</div>
</font>