<p dir="ltr">I have had this issue with hanging LED&#39;s and it was in the inverter programming, I only had 2 SI installed. I can&#39;t recall what the program issue was but it was easy to see<br>
Jerry</p>
<div class="gmail_quote">On Feb 12, 2014 8:14 AM, &quot;Exeltech&quot; &lt;<a href="mailto:exeltech@yahoo.com">exeltech@yahoo.com</a>&gt; wrote:<br type="attribution"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
Troy,<br>
<br>
Elsewhere in this thread, boB (Midnite) suggested connecting one of the problematic lights and dimmers directly at the inverter output.<br>
<br>
This is a very sound recommendation, and would immediately rule in .. or rule out the conductors (and related circuits) as an issue.<br>
<br>
Another Wrench suggested using an oscilloscope to check the waveform at the load end. &nbsp;This too is excellent advice, and would be even more telling than connecting the lamps and dimmer directly at the inverter. &nbsp;The &lsquo;scope will reveal the AC voltage AND a visual indication of any waveform distortion, either aspect of which could potentially cause the flicker you describe.<br>

<br>
If you don&rsquo;t have access to a &lsquo;scope, boB&rsquo;s comment about connecting at the inverter won&rsquo;t require any test equipment.<br>
<br>
At a minimum, set your DVM to record the voltage minimum; connect it the lamp circuit, and turn on the 1 kW load you described. &nbsp;If the voltage is dropping notably, this too would introduce visible flicker. &nbsp;The DVM method is less accurate than an oscilloscope, but better than nothing, and depends greatly on the quality (or not) of your DVM.<br>

<br>
The above aside, anything else would be strictly conjecture .. which we can do all day, and never be correct.<br>
<br>
<br>
Dan<br>
<br>
<br>
<br>
--------------------------------------------<br>
On Wed, 2/12/14, August Goers &lt;<a href="mailto:august@luminalt.com">august@luminalt.com</a>&gt; wrote:<br>
<br>
&nbsp;Subject: Re: [RE-wrenches] Long transmission line inductance and LED light flicker<br>
&nbsp;To: &quot;RE-wrenches&quot; &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
&nbsp;Date: Wednesday, February 12, 2014, 9:01 AM<br>
<br>
&nbsp;Hi Troy,<br>
<br>
Have you double checked that your grounding systems both in the house and at the inverters/array are all up to snuff?<br>
<br>
Sorry I can&rsquo;t offer any help with the inductance issue.<br>
<br>
Best,<br>
<br>
August<br>
<br>
<br>
<br>
From: <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a> [mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of Troy Harvey<br>

Sent: Tuesday, February 11, 2014 5:45 PM<br>
To: RE-wrenches<br>
Subject: Re: [RE-wrenches] Long transmission line inductance and LED light flicker<br>
<br>
<br>
Richard,<br>
<br>
<br>
The system configuration is:<br>
Approx 24.7kW of modules connected to:<br>
&nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; 2 x 9kW Sunnyboys<br>
&nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; 1 x 5kW Sunnyboys<br>
<br>
Plus<br>
4 x 6kW sunnyislands, with 2 Parallel 48V Strings of (12 x 4V Surrettes ) using 350MCM cable<br>
<br>
<br>
<br>
Wire<br>
<br>
The wire is about 1000 feet long 350 MCM in a &quot;twisted&quot; bundle to this outbuilding<br>
<br>
Conditions<br>
<br>
The conditions were during the day with full sun, so during the test there is approx. 47kW of available inverter pointed at only &gt;15 amps (120V) of load(!).<br>
<br>
The steady state conditions was a few LED lights, maybe 60 watts worth, plus a handful of vampire loads, maybe 100-200 watts total. When a pure resistance load, like a 1000W curling iron was turned on the lights would flicker.<br>

<br>
Since the lights flickered from a resistive load, but didn&#39;t stay dim, I assumed it was from a reactive-phase issues due to the transient &nbsp;turn-on - screwing with the LED dimmer circuits which are already doing a bit of magic to turn TRIAC waveforms into a DC constant current.<br>

<br>
thanks,<br>
<br>
Troy Harvey<br>
---------------------<br>
Principal Engineer<br>
Heliocentric<br>
801-453-9434<br>
<a href="mailto:taharvey@heliocentric.org">taharvey@heliocentric.org</a><br>
<br>
<br>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>