<p dir="ltr">I have done systems in Hawaii, here is one with a 30 k PV system and with a 250k Cummins back up genny. We have a contactor in the ATS that will open if the genny is operating, this in turn sends a door open signal to the Satcon shutting it down I don&#39;t want anything effecting the genset operation so with the open created in the ATS it tricks the inverter to shut off safely. We as a policy will not run a genset and PV unless as a AC coupling system and you have some active over voltage like freq and voltage triggers.<br>

Jerry</p>
<div class="gmail_quote">On Feb 8, 2014 7:31 AM, &quot;Kirk Herander&quot; &lt;<a href="mailto:kirk@vtsolar.com">kirk@vtsolar.com</a>&gt; wrote:<br type="attribution"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div lang="EN-US" link="blue" vlink="purple"><div><p class="MsoNormal"><span style="font-size:14.0pt">Hello,<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt"><u></u>&nbsp;<u></u></span></p><p class="MsoNormal">
<span style="font-size:14.0pt">I recently posed the question to Solaredge tech support, wondering if their inverter, in this case a 20kw 480 3-phase, would have any issues if it were connected to an AC panel backed up by a generator. They told me no problem, for the inverter&rsquo;s anti-islanding will work if it sees the &ldquo;generator frequency&rdquo; and therefore will not try to push PV power to the panel. But isn&rsquo;t 60 hz, 60hz regardless of origin? There&rsquo;s got to be more to it than that. I question this because I asked the same to SMA several years ago and they were hard-set against connecting Sunnyboys to a panel with generator backup, so I always would establish the point of interconnection upstream of the generator feed. Comments? Thanks.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:14.0pt"><u></u>&nbsp;<u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">Kirk Herander<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">VT Solar, LLC<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:14.0pt">dba Vermont Solar Engineering<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">NABCEP<sup>TM </sup>Certified Inaugural Certificant<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:14.0pt">NYSERDA-eligible Installer<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">VT RE Incentive Program Partner<u></u><u></u></span></p><p class="MsoNormal">
<span style="font-size:14.0pt"><a href="tel:802.863.1202" value="+18028631202" target="_blank">802.863.1202</a><u></u><u></u></span></p><p class="MsoNormal"><u></u>&nbsp;<u></u></p></div></div><br>_______________________________________________<br>

List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div>