<div dir="ltr">A 12KW generator can produce 250A at 48V, and the breaker should be 12KW *125% or 62.5 amps.<div>You may have an unbalanced load, you probably can only put 6KW per leg of the 240V feed.</div></div><div class="gmail_extra">
<br><br><div class="gmail_quote">On Sat, Feb 8, 2014 at 2:46 AM,  <span dir="ltr">&lt;<a href="mailto:bruce@willpowerelect.com" target="_blank">bruce@willpowerelect.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div><span style="font-family:Verdana;color:#0033cc;font-size:10pt"><div>Hi All,</div><div><br></div><div>3 VFX 3648</div><div>2 FM 80</div><div>6.5 kw solar</div><div>12 kw generator</div><div>PSX 240 on generator output and VFX stacking<br>
</div><div>Mate 3<br></div><div>HUP 1690 ah</div><div><br></div><div>System design considering 45 amp charge current from each VFX totaling 135 amps. (135 x ~55v = 7.42kw) Potential charge current from 2 arrays and FM 80&#39;s, 90 - 100 amps. On a good day, reasonable to expect 200+ amps?</div>
<div>Have not been able to exceed 90 amps for more than 30 minutes, with the generator putting out about 9 kw before it&#39;s 70 amp 2pole breaker trips. L1 42 amps, L2 37 amps. 5 amps neutral. Load banked to 12.3 kw (51 amps @ 240v) resistive without breaker trip.</div>
<div>I have had to dial back the maximum charge current in the Mate 3 to 12 amps each on two of the inverters (L1 and L2) and 8 on inverter 3 to keep the generator from tripping out when customer turns on the microwave or coffee pot. In effect, 42 amps charge @ 240 v = 7.6 kw. At the battery, I&#39;m only seeing 80 amps of charge current. Running loads are typically less than 1 kw but there has been a of construction going on with chop saws and compressors creating annoying spikes that are easily handled by the inverters when the generator is off.<br>
</div><div>I don&#39;t want to kill this new battery by not feeding it properly! I would have put in a larger generator, but the owner bought the 12 kw before deciding on the new battery. I thought the 12 would be merely adequate, but not so....</div>
<div>Any suggestions?</div><div><br></div><div>Thanks!<br></div><div><br></div><div>Bruce Fiero-RMI</div><div><span style="font-size:8pt"><b><br></b></span></div><div><span style="font-size:8pt"><img title="signature image" src="cid:sigimg0@ec91c0b7e33819d16bf64da3875a31b0" alt="" border="0" width="125" height="75"><br>
</span></div><div><span style="font-size:8pt"><br></span></div><div><br></div><div><span style="font-size:8pt"><br></span></div><div><b><span style="font-size:8pt">&quot;I&#39;d put my money on the sun and solar energy. What a source of power! I hope we don&#39;t have to wait until oil and coal run out before we tackle that.&quot;  T. Edison, 1931</span></b></div>
</span></div><br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br>Chris Mason<div>President, Comet Systems Ltd</div><div><a href="http://www.cometenergysystems.com" target="_blank">www.cometenergysystems.com</a></div><div>
Cell: 264.235.5670</div><div>Skype: netconcepts</div>
</div>