<DIV align=left><FONT color=#000000><FONT size=3 face="Times New Roman">Sounds 
like I may be misinterpreting something but I don't think 
so...</FONT></FONT></DIV>
<DIV align=left><FONT color=#000000 size=3 
face="Times New Roman"></FONT>&nbsp;</DIV>
<DIV align=left><FONT color=#000000><FONT size=3 face="Times New Roman">NFPA 70, 
2014 NEC 705.12(D2)(3)(b) states,&nbsp;"</FONT><FONT size=3 
face="Times New Roman">The sum of 125% of the inverter(s) output circuit current 
and the rating of the </FONT></FONT></FONT></FONT></FONT><FONT size=2 
face=Tahoma><FONT size=2 face=Tahoma><FONT size=2 face=Tahoma><FONT size=3 
face="Times New Roman">overcurrent device protecting the busbar shall not exceed 
120% of the ampacity of the busbar."</FONT></FONT></FONT></FONT></DIV>
<DIV align=left><FONT size=3 face="Times New Roman"></FONT>&nbsp;</DIV>
<DIV align=left><FONT color=#ffffff size=2 face=Tahoma><FONT color=#ffffff 
size=2 face=Tahoma><FONT color=#ffffff size=2 face=Tahoma><FONT color=#000000 
size=3 face="Times New Roman">Based on this wording, here's an example 
of&nbsp;the way I calculate whether or not I'm compliant with the 120% 
rule:</FONT></FONT></FONT></FONT></DIV>
<DIV align=left><FONT color=#ffffff size=2 face=Tahoma><FONT color=#ffffff 
size=2 face=Tahoma><FONT color=#ffffff size=2 face=Tahoma><FONT color=#000000 
size=3 face="Times New Roman">1. Circuit#1 inverter output current rating = 
13.5A X 1.25 = 16.88 (OCPD for this circuit = 20A)...(I run 10AWG for these 
circuits)</FONT></FONT></FONT></FONT></DIV>
<DIV align=left><FONT size=3 face="Times New Roman">2. Circuit#2 inverter output 
current rating = 9.0A X 1.25 = 11.25 (OCPD for this circuit = 20A)</FONT></DIV>
<DIV align=left><FONT size=3 face="Times New Roman">3. 16.88A + 11.25A = 
28.13A</FONT></DIV>
<DIV align=left><FONT size=3 face="Times New Roman">4. 28.13A + 100A (rating of 
main OCPD in&nbsp;subpanel) = 128.13A</FONT></DIV>
<DIV align=left><FONT size=3 face="Times New Roman">5. Ampacity of busbar in 
125A rated subpanel = 125A</FONT></DIV>
<DIV align=left><FONT size=3 face="Times New Roman">6. 125A X 1.2 = 
150A</FONT></DIV>
<DIV align=left><FONT size=3 face="Times New Roman">7. 128.13A &lt; 150A, 
therefore, this installation is compliant with 2014 NEC 
705.12(D1-D6).</FONT></DIV>
<DIV align=left><FONT size=3 face="Times New Roman"></FONT>&nbsp;</DIV>
<DIV align=left><FONT size=3 face="Times New Roman">If I used the 100A rating of 
the&nbsp;OCPD instead of the 125A rating of the busbar, I would be limited to 
20A of PV instead of 50A.</FONT></DIV>
<DIV align=left><FONT size=3 face="Times New Roman"></FONT>&nbsp;</DIV>
<DIV align=left><FONT size=3 face="Times New Roman">According to the wording in 
the NEC I ignore load breakers and only concern myself with OCPD for PV inverter 
output circuits and OCPD for the busbar.</FONT></DIV>
<DIV>
<P align=left></FONT><FONT size=2 face=Arial></FONT>&nbsp;</P></DIV>
<DIV>Eric Stikes<BR><!--[if !mso]><![endif]--><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->SunHarvest</DIV></BODY></HTML>