<div dir="ltr">Bill.....we have been using the Hellerman Tyton Sunbundler cable ties....They are braided stainless steel wire with a UV resistant vinyl jacket....We have been getting them in quantities of 500 for approximately $.59 each....for the 12&quot; length ties....We like them alot....they do not have any sharp edges and are easy to install....<div>
Hope that helps....</div><div><br></div></div><div class="gmail_extra"><br clear="all"><div><div dir="ltr">Sunny Regards,<br>Kirpal Khalsa<br>NABCEP Certified PV Installation Professional<br>Renewable Energy Systems<br><a href="http://www.oregonsolarworks.com" target="_blank">www.oregonsolarworks.com</a><br>
541-218-0201 m<br>541-592-3958 o</div></div>
<br><br><div class="gmail_quote">On Thu, Nov 14, 2013 at 7:46 AM, frenergy <span dir="ltr">&lt;<a href="mailto:frenergy@psln.com" target="_blank">frenergy@psln.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<u></u>





<div>
<div>William, Bill....from another Bill,</div>
<div></div>
<div>  Two things: For the rest of us 
(maybe it&#39;s just me?!) that&#39;s still trying to figure out how (or why)to 
stuff a MC4 connector into conduit and my hesitation in using SS wire ties for 
fear of the sharp edges cutting or chaffing into cables, I&#39;m open for 
advice.Any wire I use on the roof is rated for that type of service and I 
have some off-grid systems that have been in the sun for some 25 years where the 
wire still looks nearly new even when flexing it tolook for 
checking/cracks. It seems thewire/insulation can take it, thus it 
seems like the key to &quot;wire management is to keep the wire from moving and off 
the roof, secured to the racking, thus not compromising the 
insulation.</div>
<div></div>
<div>  I know many on this list are way past 
this point in their installation skills. However my living in a county in 
the bush of just 20K folks, I haven&#39;t had the opportunity to install 100&#39;s of 
systems....yet. Again, I express my humble appreciation of experienced 
wrenches to help those of us working to install the tightest systems possible 
despite living in the boonies. </div>
<div></div>
<div>  Details on where to source 
appropriate SS wire ties (rounded edges?, plastic coated?) would be 
appreciated. My goto place for such things (Grainger) has &quot;regular&quot; SS 
wire ties that range from $1.50 to $3 each, but none that I can see that address 
the sharp edge issue...or is that an issue? Have people been using regular 
SS wire ties in the field for 10-20 years, behind a roof mounted array without 
any issues related to the wire ties?</div>
<div>Thanks for your help and patience,</div>
<div></div>
<div>Bill </div>
<div></div>
<div>Feather River Solar Electric<br>4291 Nelson St.<br>Taylorsville, CA 
95983<br><a href="tel:530.284.7849" value="+15302847849" target="_blank">530.284.7849</a> / 6544 fax</div>
<div><font size="1">&quot;solar powered since 1982&quot;</font></div><div><div class="h5">
<div></div>
<div>----- Original Message ----- 
<div>From: &quot;Bill Loesch&quot; &lt;<a href="mailto:solar1online@charter.net" target="_blank">solar1online@charter.net</a>&gt;</div>
<div>To: &quot;RE-wrenches&quot; &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt;</div>
<div>Sent: Thursday, November 14, 2013 1:34 AM</div>
<div>Subject: Re: [RE-wrenches] PV Wiring methods</div></div>
<div><br></div>&gt; <br>&gt; Hi William (and any other person who wishes to 
describe themselves as <br>&gt; professional (designer, installer, 
etc.)),<br>&gt; <br>&gt; Please accept this note as confirmation that your 
evangelism on wire <br>&gt; management has not fallen on entirely deaf 
ears.<br>&gt; <br>&gt; Additionally, I&#39;m curious how the practice of requiring a 
ten year <br>&gt; equipment warranty squares with the acceptance of plastic wire 
ties.<br>&gt; <br>&gt; Sincere thanks from one convert,<br>&gt; <br>&gt; Bill 
Loesch<br>&gt; Solar 1 - Saint Louis Solar<br>&gt; <br>&gt; <br>&gt; <br>&gt; On 
Wed, Nov 13, 2013 at 3:41 PM, William Miller wrote:<br>&gt; <br>&gt;&gt; 
Bill:<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; I respectfully disagree with your 
logic: Define &quot;perfectly <br>&gt;&gt; installed.&quot; If<br>&gt;&gt; 
your connections are tight and permanent and the conductors are <br>&gt;&gt; 
protected<br>&gt;&gt; from damage, you have a great chance of a reliable, safe 
lifetime of<br>&gt;&gt; service. How can you guarantee that your leads 
will stay protected <br>&gt;&gt; after<br>&gt;&gt; the ties fail? Studies 
show that even UV resistant wire ties will <br>&gt;&gt; fail well<br>&gt;&gt; 
before the life expectancy of the system has expired. When the ties 
<br>&gt;&gt; fail,<br>&gt;&gt; your PV leads are hanging on the roof. Even 
before the ties fail, <br>&gt;&gt; rodents<br>&gt;&gt; can chew on them. 
Conduit was invented for a reason and we should be <br>&gt;&gt; 
using<br>&gt;&gt; it.<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; I agree that arc-fault 
breakers will improve the situation, but I <br>&gt;&gt; don&#39;t<br>&gt;&gt; think 
any form of OCPD is a substitute for good wiring practices. I <br>&gt;&gt; 
think<br>&gt;&gt; wire protection is just as important on PV circuits as it is 
on any <br>&gt;&gt; other<br>&gt;&gt; high voltage circuit. Try getting 
away with wiring a rooftop air<br>&gt;&gt; conditioning unit by tying the 
conductors to some metal framework with<br>&gt;&gt; plastic ties and see how 
long it takes to get red-tagged by your local<br>&gt;&gt; 
inspector.<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; I suspect we&#39;ve gotten to where 
we are on lax wire protection <br>&gt;&gt; standards for<br>&gt;&gt; two 
reasons:<br>&gt;&gt;<br>&gt;&gt; 1. In the early days, PV was 
low voltage, 12 to 24 volts, and was <br>&gt;&gt; treated<br>&gt;&gt; as such, 
even though current capabilities exceeded that of <br>&gt;&gt; conventional 
low<br>&gt;&gt; voltage thermostat, door-bell and telephone 
wiring.<br>&gt;&gt;<br>&gt;&gt; 2. It is my understanding that 
PV wiring standards in Europe are <br>&gt;&gt; not<br>&gt;&gt; stringent, and 
European demand drove the PV market for many years. <br>&gt;&gt; 
Products<br>&gt;&gt; were built to satisfy the European market and US standards 
had to work <br>&gt;&gt; with<br>&gt;&gt; the equipment 
available.<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; Some would say: &quot;if it is under 
the array, it is protected.&quot; We have <br>&gt;&gt; seen<br>&gt;&gt; PV wire 
getting damaged under arrays and it is possible to get damaged <br>&gt;&gt; 
under<br>&gt;&gt; BPIV components as well. I believe that protecting PV 
wire is more<br>&gt;&gt; important than protecting conventional AC circuit 
wiring because PV <br>&gt;&gt; circuits<br>&gt;&gt; are more prone to create and 
sustain arcing.<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; Some say that protecting PV 
wire in conduits will add too much expense <br>&gt;&gt; to PV<br>&gt;&gt; 
installations. Consider the cost of fires and, inevitably, injuries 
<br>&gt;&gt; and<br>&gt;&gt; deaths. One news story about an obscure, 
rarely used product is <br>&gt;&gt; already<br>&gt;&gt; causing many of us 
headaches. Statistically, it is inevitable that <br>&gt;&gt; 
more<br>&gt;&gt; accidents will happen. I don&#39;t want that on my 
conscience.<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; I would suggest that we need to 
expand the discussion beyond fire <br>&gt;&gt; hazards.<br>&gt;&gt; I also worry 
about electrocution hazards in high voltage PV circuits. <br>&gt;&gt; 
Good<br>&gt;&gt; wire protection is essential in preventing contact with high 
voltages.<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; Unprotected PV wiring is an 
irresponsible practice. I am fighting an <br>&gt;&gt; uphill<br>&gt;&gt; 
battle to develops methods to protect PV wiring because the industry 
<br>&gt;&gt; is not<br>&gt;&gt; helping at all. The trend has been to make 
it harder to protect <br>&gt;&gt; wiring.<br>&gt;&gt; This trend will result in 
accidents. I think we should do 
better.<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; 
Sincerely,<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; William 
Miller<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; From: <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a><br>&gt;&gt; 
[mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of Bill 
<br>&gt;&gt; Brooks<br>&gt;&gt; Sent: Monday, November 11, 2013 3:38 
PM<br>&gt;&gt; To: &#39;RE-wrenches&#39;<br>&gt;&gt; Subject: Re: [RE-wrenches] 
RE-wrenches Digest, Vol 6, Issue 423<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; William 
and David,<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; This particular problem goes away 
with arc fault detection. The longer <br>&gt;&gt; we<br>&gt;&gt; wait to 
introduce arc fault detection into our systems, the more we <br>&gt;&gt; 
will<br>&gt;&gt; have opportunities for news reports such as the one William 
brings <br>&gt;&gt; forward.<br>&gt;&gt; Wire ties are not the problem. Could a 
wire tie cause a problem-sure, <br>&gt;&gt; just<br>&gt;&gt; like anything 
improperly installed.<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; At the end of the day, 
you can a have a perfectly installed system, <br>&gt;&gt; but if<br>&gt;&gt; it 
does not have arc fault detection and high resolution ground fault<br>&gt;&gt; 
detection, it can still catch on fire. You have no control over <br>&gt;&gt; 
product<br>&gt;&gt; failures other than buying from large companies that can 
actually <br>&gt;&gt; insure<br>&gt;&gt; their products in a 
failure.<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; Fires are not that common, but it 
didn&#39;t take much to get all the <br>&gt;&gt; viewers of<br>&gt;&gt; this news 
report up in arms did it?<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; 
Bill.<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; 
------------------------------<br>&gt;&gt;<br>&gt;&gt; 
_______________________________________________<br>&gt;&gt; List sponsored by 
Home Power magazine<br>&gt;&gt;<br>&gt;&gt; List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>&gt;&gt;<br>&gt;&gt; 
Change email address &amp; settings:<br>&gt;&gt; <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
&gt;&gt;<br>&gt;&gt; 
List-Archive: <br>&gt;&gt; <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>&gt;&gt;<br>&gt;&gt; 
List rules &amp; etiquette:<br>&gt;&gt; <a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>&gt;&gt;<br>&gt;&gt; 
Check out participant bios:<br>&gt;&gt; <a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>&gt; 
_______________________________________________<br>&gt; List sponsored by Home 
Power magazine<br>&gt; <br>&gt; List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>&gt; 
<br>&gt; Change email address &amp; settings:<br>&gt; <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
&gt; 
<br>&gt; List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>&gt; 
<br>&gt; List rules &amp; etiquette:<br>&gt; <a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>&gt; 
<br>&gt; Check out participant bios:<br>&gt; <a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>&gt;</div></div></div>
<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div>