    <div class="moz-cite-prefix">Fellow Wrenches:<br>
      <br>
      Per NEMA Standards Publication 250-1997 "Enclosures for Electrical
      Equipment (1000 Volts Maximum)", a NEMA 3-R enclosure is designed
      to provide a DEGREE of protection against 45 degree angled rain.
      When testing for compliance, there can be no significant amount of
      water within the enclosure and no water may be present on live
      parts.<br>
      <br>
      NEMA 250 states is Section 4.4 ENCLOSURE ORIENTATION:<br>
      <blockquote><i>If the acceptability of a Type 2 or 3R enclosure is
          dependent upon a particular mounting orientation,</i><i> </i><i>the
          enclosure shall be marked to indicate the required orientation
          unless the mounting is obvious.</i><i><br>
          <br>
        </i><i>If a Type 2 or 3R enclosure has knockouts for conduit in
          the sides or back of the enclosure in which</i><i> </i><i>the
          equipment to be installed is not known, it shall be marked to
          indicate the area in which live parts are to</i><i> </i><i>be
          installed.</i><i><br>
        </i></blockquote>
      The spec sheet for a NEMA 3-R Square-D safety switch states that
      "Device Mounting" is "Surface". I would interpret that as
      vertical. Also, a vertical orientation of the enclosure would
      minimize the amount of water intrusion from a 45 degree angled
      rain test. <br>
      <br>
      Regards,<br>
      <br>
      Gary Willett<br>
      Icarus Solar<br>
      <br>
      <br>
      On 11/11/13, 1:49 PM, <a class="moz-txt-link-abbreviated" href="mailto:Eric.Bentsen@schneider-electric.com">Eric.Bentsen@schneider-electric.com</a> wrote:<br>
    </div>
    <blockquote
cite="mid:OF0FECC3CE.25A6B6A9-ON88257C20.006C0F6E-88257C20.006CFE50@US.Schneider-Electric.com"
      type="cite">
      <br>
      <font face="sans-serif" size="2">Hi Wrenches,</font>
      <br>
      <font face="sans-serif" size="2">&nbsp;There is no "implication"
        other than confirming how the disco </font>
      <br>
      <font face="sans-serif" size="2">is tested, and thus certified. It
        probably
        makes no difference electrically which position the</font>
      <br>
      <font face="sans-serif" size="2">&nbsp;unit is mounted, but AHJs may
        have differing opinions on whether this would be permitted. </font>
      <br>
      <font face="sans-serif" size="2">Rgds,<br>
      </font><font color="#008000" size="3">_____________________________________________________________________________________</font><font
        size="3">
        <br>
      </font><font face="Arial" size="1"><b><br>
          Eric Bentsen</b> &nbsp;| &nbsp;</font><font color="#008000" face="Arial"
        size="1"><b>
          Schneider Electric </b></font><font face="Arial" size="1"><b>&nbsp;
          | &nbsp;Solar
          Business</b> &nbsp;| &nbsp; <b>UNITED STATES</b> &nbsp;| &nbsp; <b>Technical
          Support Representative</b> <b><br>
          Phone:</b> +(650) 351-8237 ext. 001# &nbsp;| &nbsp; <b><br>
          Email:</b> </font><a moz-do-not-send="true"
        href="mailto:eric.bentsen@schneider-electric.com"><font
          color="blue" face="Arial" size="1"><u>eric.bentsen@schneider-electric.com</u></font></a><font
        face="Arial" size="1">
        &nbsp;| &nbsp; <b>Site:</b></font><a moz-do-not-send="true"
        href="http://www.schneider-electric.com/solar" target="_blank"><font
          color="blue" face="Arial" size="1"><u>
            www.schneider-electric.com/solar</u></font></a><font
        face="Arial" size="1">
        &nbsp;| &nbsp; <b>Address:</b> 250 South Vasco Rd., Livermore, CA 94551
        <br>
      </font><font color="blue" face="Arial" size="1"><u><br>
        </u></font><a moz-do-not-send="true"
        href="www.schneider-electric.com/solar"><img
          src="cid:part3.05030006.02070503@IcarusSolarServices.com"></a><font
        color="#00a000" face="Arial" size="1"><br>
        *** Please consider the environment before printing this e-mail</font><font
        face="Arial" size="1">
      </font><font size="3"><br>
      </font>
      <br>
      <br>
      <br>
      <table width="100%">
        <tbody>
          <tr valign="top">
            <td><font color="#5f5f5f" face="sans-serif" size="1">From:</font>
            </td>
            <td><font face="sans-serif" size="1">Bob-O Schultze
                <a class="moz-txt-link-rfc2396E" href="mailto:bob-o@electronconnection.com">&lt;bob-o@electronconnection.com&gt;</a></font>
            </td>
          </tr>
          <tr valign="top">
            <td><font color="#5f5f5f" face="sans-serif" size="1">To:</font>
            </td>
            <td><font face="sans-serif" size="1">RE-wrenches
                <a class="moz-txt-link-rfc2396E" href="mailto:re-wrenches@lists.re-wrenches.org">&lt;re-wrenches@lists.re-wrenches.org&gt;</a></font>
            </td>
          </tr>
          <tr valign="top">
            <td><font color="#5f5f5f" face="sans-serif" size="1">Date:</font>
            </td>
            <td><font face="sans-serif" size="1">11/11/2013 10:09 AM</font>
            </td>
          </tr>
          <tr valign="top">
            <td><font color="#5f5f5f" face="sans-serif" size="1">Subject:</font>
            </td>
            <td><font face="sans-serif" size="1">Re: [RE-wrenches]
                Square D Disconnects
                mounted on the slope of the &nbsp; &nbsp; &nbsp; &nbsp;roof.</font>
            </td>
          </tr>
          <tr valign="top">
            <td><font color="#5f5f5f" face="sans-serif" size="1">Sent
                by:</font>
            </td>
            <td><font face="sans-serif" size="1"><a class="moz-txt-link-abbreviated" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a></font></td>
          </tr>
        </tbody>
      </table>
      <br>
      <hr noshade="noshade">
      <br>
      <br>
      <br>
      <tt><font size="2">Dan,<br>
          I think this thread applied not to OCDs but to an unfused
          600VDC disconnect
          can mounted on a roof which is less than vertical.<br>
          Bob-O<br>
          On Nov 11, 2013, at 9:21 AM, Exeltech wrote:<br>
          <br>
          Wrenches,<br>
          <br>
          There appears to be some misinformation getting into this
          thread.<br>
          <br>
          The "trip" mechanism within standard thermal over-current
          protective
          devices ("OCP devices") is mechanically spring-loaded, and is
          triggered by heat.<br>
          <br>
          Eric mentions below that Square D breakers are tested in a
          vertical orientation
          only - the implication being that's their only "UL certified"
          position. &nbsp;If this were true, it would imply the breakers
          cannot be
          used in any other orientation. &nbsp;This would potentially limit
          the Square
          D OCP market to sub-panels and other enclosures where the
          devices are vertical.
          &nbsp;Inasmuch as the vast majority of panelboards I've encountered
          in
          my 40+ years in this industry have the breakers stacked
          horizontally, it
          would not be a wise business decision for the manufacturer to
          self-inflict
          such a limitation on their product.<br>
          <br>
          This also does not mean any such limitation (real or not)
          applies to all
          breakers.<br>
          <br>
          By way of example, OCP devices work in a horizontal position,
          stacked "pancake"
          style in a main panelboard, as well as vertically oriented
          side-by-side
          in a sub-panel. &nbsp;In either orientation, they are &nbsp;in full
          compliance
          with UL 489, (UL Standard for Circuit Breakers, Switches, and
          Circuit Breaker
          Enclosures). &nbsp;If an OCP device *was* positionally-sensitive,
          UL Standards
          require this sensitivity to be noted in the documentation
          accompanying
          the device. &nbsp;Further to that point, UL 489 Section 7.1.1.13
          states:
          "In determining if a circuit breaker complies with the test
          requirements,
          the device shall be mounted or supported as in service and
          tested under
          conditions approximating those of intended operation, except
          as otherwise
          noted."<br>
          <br>
          Mounting position notwithstanding, a greater concern would be
          the ambient
          temperature of a rooftop location, whereby summer heat would
          tend to make
          the OCP device more sensitive than necessary, potentially
          causing it to
          trip at an amperage below that of its UL ratings. &nbsp;While a
          nuisance,
          a more serious issue arises when operating the OCP device in
          cold ambient
          conditions, whereby the device may allow MORE than its rated
          trip current
          to flow.<br>
          <br>
          Per UL 489, OCP devices are tested at either 25C or 40C
          ambient. &nbsp;Again
          per UL 489, if an OCP device is to be used in ambient
          conditions other
          than those two ranges, the acceptable temperature range for
          that OCP device
          shall be marked on the body of the device.<br>
          <br>
          In UL 489, Supplemental Annex, Section 2, Subsection 2.3.3,
          mechanical
          vibration testing is conducted with OCP devices oriented
          vertically, horizontally,
          and inclined 30 degrees from vertical, with all devices
          energized up to
          200% of the device rated current during the testing.<br>
          <br>
          Given the preceding, and per implication of UL 489 testing
          methods, OCP
          devices are NOT positionally sensitive.<br>
          <br>
          In conclusion, if you DO install a rooftop OCP system, and for
          proper protection,
          please ensure the OCP devices utilized are rated for the
          worst-case ambient
          temperatures involved.<br>
          <br>
          <br>
          Regards to all,<br>
          <br>
          <br>
          Dan Lepinski<br>
          <br>
          <br>
          <br>
          <br>
          At 09:33 AM 11/8/2013, you wrote:<br>
          <br>
          Hi Kirpal,<br>
          <br>
          All Square D safety switches are UL tested in the Vertical
          position ONLY,
          so if someone is trying to install a switch in any other
          position other
          than vertical, that will be between them and the inspector.<br>
          <br>
          Hope this helps. <br>
          <br>
          Eric<br>
____________________________________________________________________________________<br>
          <br>
          Eric Bentsen &nbsp;| &nbsp;Schneider Electric &nbsp; | &nbsp;Solar Business
          &nbsp;| &nbsp; UNITED STATES &nbsp;| &nbsp; Technical Support Representative
          <br>
          Phone: +(650) 351-8237 ext. 001# &nbsp;| &nbsp; Email:
          <a class="moz-txt-link-abbreviated" href="mailto:eric.bentsen@schneider-electric.com">eric.bentsen@schneider-electric.com</a>
          &nbsp;| &nbsp;Site: </font></tt><a moz-do-not-send="true"
        href="www.schneider-electric.com/solar"><tt><font size="2">www.schneider-electric.com/solar</font></tt></a><tt><font
          size="2">
          &nbsp; | &nbsp; Address: 250 South Vasco Rd., Livermore, CA 94551 <br>
          <br>
          <br>
          _______________________________________________<br>
          List sponsored by Home Power magazine<br>
          <br>
          List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
          <br>
          Change email address &amp; settings:<br>
        </font></tt><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font
            size="2">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font
          size="2"><br>
          <br>
          List-Archive: </font></tt><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font
            size="2">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</font></tt></a><tt><font
          size="2"><br>
          <br>
          List rules &amp; etiquette:<br>
        </font></tt><a moz-do-not-send="true"
        href="www.re-wrenches.org/etiquette.htm"><tt><font size="2">www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font
          size="2"><br>
          <br>
          Check out participant bios:<br>
        </font></tt><a moz-do-not-send="true"
        href="www.members.re-wrenches.org"><tt><font size="2">www.members.re-wrenches.org</font></tt></a><tt><font
          size="2"><br>
          <br>
          <br>
          <br>
          _______________________________________________<br>
          List sponsored by Home Power magazine<br>
          <br>
          List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
          <br>
          Change email address &amp; settings:<br>
        </font></tt><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font
            size="2">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font
          size="2"><br>
          <br>
          List-Archive: </font></tt><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font
            size="2">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</font></tt></a><tt><font
          size="2"><br>
          <br>
          List rules &amp; etiquette:<br>
        </font></tt><a moz-do-not-send="true"
        href="www.re-wrenches.org/etiquette.htm"><tt><font size="2">www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font
          size="2"><br>
          <br>
          Check out participant bios:<br>
        </font></tt><a moz-do-not-send="true"
        href="www.members.re-wrenches.org"><tt><font size="2">www.members.re-wrenches.org</font></tt></a><tt><font
          size="2"><br>
          <br>
          <br>
______________________________________________________________________<br>
          This email has been scanned by the Symantec Email
          Security.cloud service.<br>
______________________________________________________________________<br>
        </font></tt>
      <br>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>