    <div class="moz-cite-prefix">Hi Jesse;<br>
      <br>
      Midnite's breaker boxes would solve your disconnect issue, but I
      wouldn't use the baby box or Quad box, they're small and tight.&nbsp;
      I'd actually consider their 6 position combiner box, even though
      its outdoor rated.&nbsp; Another option would be the Mini DC box.&nbsp; <br>
      <br>
      Here's my quick, real man's guide to many of Midnite's DC boxes:<br>
      <br>
      <u>Baby Box</u>&nbsp; Good for a couple of circuits, don't go over #10
      wire. <span class="moz-smiley-s1"><span> :-) </span></span><br>
      <br>
      <u>BIg Baby Box</u>&nbsp; Good for a couple of PV inputs, and up to #6
      for one Controller output.<span class="moz-smiley-s1"><span> :-) </span></span><span
        class="moz-smiley-s1"><span> :-) </span></span><br>
      <br>
      <u>QUAD Box</u>, same size, only uses panel mount breakers.&nbsp; Don't
      be fooled into trying #4 with this.&nbsp; It works, but you'll never do
      it again.&nbsp; Keep it to smaller wires, and/or less than 4 circuits,
      and you'll be happy.<span class="moz-smiley-s1"><span> :-) </span></span><br>
      <br>
      <u>MNPV -3</u> Outdoor Combiner box, good for up to 3&nbsp; PV
      circuits.&nbsp; a bit more room than the QUAD box, so it can actually
      handle #4 more readily.<span class="moz-smiley-s1"><span> :-) </span></span><br>
      <br>
      <u>MNPV-6</u> outdoor combiner box.&nbsp;&nbsp; This one is a real
      workhorse, and can be used with bigger wire, and separate
      controller circuits.<span class="moz-smiley-s1"><span> :-) </span></span><span
        class="moz-smiley-s1"><span> :-) </span></span><span
        class="moz-smiley-s1"><span> :-) </span></span><br>
      <br>
      <u>MNDC-15</u>&nbsp; An overpriced POS.&nbsp; It can't take full size
      bussbars, it can't mount a shunt, it has cumbersome breaker
      mounting brackets that prevent you from being able to tighten the
      breaker connections..... Sorry Midnite, but this one needs to be
      totally redesigned and have a serious price reduction too.<span
        class="moz-smiley-s2"><span> :-( </span></span><span
        class="moz-smiley-s2"><span> :-( </span></span><span
        class="moz-smiley-s2"><span> :-(&nbsp;&nbsp; </span></span>an absolute
      black mark in an otherwise stellar line up.<br>
      <br>
      <u>MNDC</u>&nbsp; this box is awesome for all sorts of projects from
      small inverter disconnects, to multiple controller and DC
      disconnects.&nbsp; I've used this one for many years, and prefer it
      over the E panel&nbsp; in certain budget cases.<span
        class="moz-smiley-s1"><span> :-) </span></span><span
        class="moz-smiley-s1"><span> :-) </span></span><span
        class="moz-smiley-s1"><span> :-)&nbsp;&nbsp; </span></span>(its under
      $200!)<br>
      <br>
      <u>E Panel</u>&nbsp; probably the best single inverter solution
      available.&nbsp; No other box takes less wall space.&nbsp; Combines AC and
      DC all under the form of the inverter.&nbsp; Can be a bit confusing
      because of the side mounted breakers, so I move away from this, if
      I have a lot of weird stuff like multiple inverters, multiple
      controllers, DC loads, etc.&nbsp; However, Its actually better than any
      of the inverter manufacturers' own equipment for single inverter
      systems, and really comes with everything you need (breakers,&nbsp; AC
      and DC adapter covers, prewired AC and DC cables, shunt,&nbsp; AC/DC
      bussbars, etc.)<span class="moz-smiley-s1"><span> :-) </span></span><span
        class="moz-smiley-s1"><span> :-) </span></span><span
        class="moz-smiley-s1"><span> :-)&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; </span></span>I've
      happily used this for Magnum, Outback, and Xantrex/ Sheitdner.<br>
      <br>
      Good Luck,<br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 10/24/2013 2:13 PM, Jesse Dahl wrote:<br>
    </div>
    <blockquote
cite="mid:CAJLdFVd_mUfOzijMmCLuZgWo=Ry0_sQ2x-HSUvwb1ZPhr1th=g@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hello,
        <div><br>
        </div>
        <div>Looked at a system today that consisted of the following:</div>
        <div><br>
        </div>
        <div>15 - Kyocera 158W modules</div>
        <div>3 - &nbsp; Kyocera 185W modules</div>
        <div>1 - &nbsp; Outback MX60</div>
        <div>
          8 - &nbsp; New Trojan L16RE (48V system)</div>
        <div>1 - &nbsp; Xantrex SW Plus&nbsp;</div>
        <div><br>
        </div>
        <div>
          <div>6 months ago he swapped out his old charge controller to
            the new MX60 and purchased the new batteries at that time.
            &nbsp;The array wiring did not change and is wired in 6 strings
            of 3. &nbsp;(confusing to the MX60?)</div>
        </div>
        <div><br>
        </div>
        <div>He is now adding 4 Kyocera 240W modules. &nbsp;He also purchased
          another MX60 for this array.</div>
        <div><br>
        </div>
        <div>From my perspective, removing the 3 185W modules and
          getting them on their own controller would be a better use of
          the modules. &nbsp;The system currently does not have any
          disconnects on the PV side. &nbsp;There are fuses in the combiner
          boxes on the array, but no disconnects inside at the charge
          controller. &nbsp;So adding 3 charge controllers, and now needing
          to add GFDI, means a box of some kind needs to be added to
          house these breakers.&nbsp;</div>
        <div><br>
        </div>
        <div>Outbacks GFPs and panel mount breakers will work, but what
          is the best mounting solution for these? &nbsp;One DC Flexware
          enclosure? It will of course allow for all the DC OCPD &nbsp;and
          allow for the landing of the output of the charge controllers.
          &nbsp;Or is there another enclosure/OCPD solution I should look at?
          &nbsp;</div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div>Thanks as always!</div>
        <div><br>
        </div>
        <div>Jesse</div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div>
          <div><br>
          </div>
          <div><br>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>