<br><font size=2 face="sans-serif">Hi William,</font>
<br><font size=2 face="sans-serif">In theory, this would be possible, but
you have to consider the 60A transfer relay rating, so if we are dealing
with SW5548 (5.5kW) models,</font>
<br><font size=2 face="sans-serif">you will only add approx 1700W of power
(per set) before nuisance tripping a 60A breaker.</font>
<br><font size=2 face="sans-serif">Rgds,<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Eric Bentsen</b> | </font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b> | Solar
Business</b> | <b>UNITED STATES</b> | <b>Technical
Support Representative</b> <b><br>
Phone:</b> +(650) 351-8237 ext. 001# | <b><br>
Email:</b> </font><a href="mailto:eric.bentsen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>eric.bentsen@schneider-electric.com</u></font></a><font size=1 face="Arial">
| <b>Site:</b></font><a href="http://www.schneider-electric.com/solar" target=_blank><font size=1 color=blue face="Arial"><u>
www.schneider-electric.com/solar</u></font></a><font size=1 face="Arial">
| <b>Address:</b> 250 South Vasco Rd., Livermore, CA 94551
<br>
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><a href="www.schneider-electric.com/solar"><img src=cid:_2_0D3DE6B00D3DE330005D920D88257BFA></a><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=1 face="Arial">
</font><font size=3><br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">"William Miller" <william@millersolar.com></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">"'RE-wrenches'" <re-wrenches@lists.re-wrenches.org></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">10/03/2013 10:49 PM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">Re: [RE-wrenches] parallel stacking
SW</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">re-wrenches-bounces@lists.re-wrenches.org</font></table>
<br>
<hr noshade>
<br>
<br>
<br><font size=3 face="Arial">Mac:</font>
<br><font size=3 face="Arial"> </font>
<br><font size=3 face="Arial">I approached this problem some years ago
and posted about it on this forum. What I heard is that, yes, it can be
done. The actual process is known by a few former Trace engineers
and could not be divulged due to confidentiality agreements signed when
Outback split off from Xantrex (or Trace, if that is what it was called
at the time). If you know a former Trace Engineer, you might be able
to wrest the information out of them if the stature of limitations has
expired.</font>
<br><font size=3 face="Arial"> </font>
<br><font size=3 face="Arial">Of course I was not satisfied with \u201cthis
information is only is for some to know,\u201d so I worked on the problem.
My idea is to connect two inverters in series and then feed them into the
AC1 inputs of two more inverters in parallel. Since the SW inverters
can provide true \u201cGen Support\u201d mode, the downstream inverters can assist
the upstream inverters, therefore providing the gross power of all four
inverters. See this </font><a href=http://www.millersolar.com/MillerSolar/case_studies/case_studies.html><font size=3 color=blue face="Arial"><u>page</u></font></a><font size=3 face="Arial">
for a drawing. Look about halfway down the page for Cascading
SW inverters.</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=3 face="Arial">Now I have come up with some pretty strange
ideas in my time, but I think this is one of the more wacky, but actually
possible solutions. I never had the chance to test this scheme, but
I would love to know if it would actually work.</font>
<br><font size=3 face="Arial"> </font>
<br><font size=3 face="Arial">William</font>
<br><font size=3 face="Arial"> </font>
<br><font size=3 face="Arial">PS: Just as I was finishing this email
I remembered the situation I was trying to correct. The other idea is here:
</font><a href=http://www.millersolar.com/MillerSolar/case_studies/pv_school/pv_school_wiring_digrams.html><font size=3 color=blue face="Arial"><u>Link</u></font></a><font size=3 face="Arial">
I don\u2019t recommend this technique for the reasons stated on the web site,
but there may the germ of an idea that may work. It would have to
do with feeding a transformer from opposite ends with paralleled inverters.
How to keep them in sync\u2026</font>
<br><font size=3 face="Arial"> </font>
<br><font size=3 face="Arial">Good Luck,</font>
<br><font size=3 face="Arial"> </font>
<br><font size=3 face="Arial">William Miller</font>
<br><font size=3 face="Arial"> </font>
<br><font size=3 face="Arial"> </font>
<br><font size=3 face="Arial"> </font>
<br><font size=2 face="Tahoma"><b>From:</b> re-wrenches-bounces@lists.re-wrenches.org
[</font><a href="mailto:re-wrenches-bounces@lists.re-wrenches.org"><font size=2 face="Tahoma">mailto:re-wrenches-bounces@lists.re-wrenches.org</font></a><font size=2 face="Tahoma">]
<b>On Behalf Of </b>Mac Lewis<b><br>
Sent:</b> Wednesday, October 02, 2013 8:01 AM<b><br>
To:</b> RE-wrenches<b><br>
Subject:</b> [RE-wrenches] parallel stacking SW</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=3 face="Times New Roman">Hi wrenches,</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=3 face="Times New Roman">I have some folks that I'm meeting
in a couple of days that have 4 Trace SW 5048 inverters. It's a very
large, older compound-style installation that the original installer has
bailed on. They have it set up so that there is a common battery
bank and each pair of series stacked inverters are independently feeding
2 separate 120/240 busses. One of these 120/240 services gets utilized
very heavily, and one isn't really used at all. Is it possible with
this type of inverter, to have all four inverters feeding a common AC bus,
two feed Phase A and the other two feeding phase B?</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=3 face="Times New Roman">I know that is possible to series
stack and to parallel stack this inverter, but can you do both at the same
time?</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=3 face="Times New Roman">If so, does anyone have a pin out
to a parallel stacking cable?</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=3 face="Times New Roman">Thanks in advance</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=3 face="Times New Roman">-- </font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=3 face="Times New Roman">Mac Lewis</font>
<p><font size=3 color=#37605e face="Times New Roman">"Yo solo sé que
no sé nada." </font><font size=3 color=#5f5f5f face="Times New Roman"><b>-Sócrates</b></font>
<div align=center>
<br>
<hr noshade></div>
<br><font size=3 face="Times New Roman">No virus found in this message.<br>
Checked by AVG - </font><a href=http://www.avg.com/><font size=3 color=blue face="Times New Roman"><u>www.avg.com</u></font></a><font size=3 face="Times New Roman"><br>
Version: 2014.0.4142 / Virus Database: 3604/6704 - Release Date: 09/27/13</font>
<p><font size=3><br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________</font><tt><font size=2>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change email address & settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List rules & etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
</font></tt>
<p>
<p>