<br><font size=2 face="sans-serif">Hi Brian,</font>
<br><font size=2 face="sans-serif">That is the issue.....LBX mode is the
only way the SW can disconnect from </font>
<br><font size=2 face="sans-serif">a qualified source of AC, thus maximizing
solar production. The best way is </font>
<br><font size=2 face="sans-serif">to get approved to sell, which probably
won't happen with an inverter that old.</font>
<br><font size=2 face="sans-serif">Rgds,<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Eric Bentsen</b> &nbsp;| &nbsp;</font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>&nbsp; | &nbsp;Solar
Business</b> &nbsp;| &nbsp; <b>UNITED STATES</b> &nbsp;| &nbsp; <b>Technical
Support Representative</b> <b><br>
Phone:</b> +(650) 351-8237 ext. 001# &nbsp;| &nbsp; <b><br>
Email:</b> </font><a href="mailto:eric.bentsen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>eric.bentsen@schneider-electric.com</u></font></a><font size=1 face="Arial">
&nbsp;| &nbsp; <b>Site:</b></font><a href="http://www.schneider-electric.com/solar" target=_blank><font size=1 color=blue face="Arial"><u>
www.schneider-electric.com/solar</u></font></a><font size=1 face="Arial">
&nbsp;| &nbsp; <b>Address:</b> 250 South Vasco Rd., Livermore, CA 94551
<br>
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><a href="www.schneider-electric.com/solar"><img src=cid:_2_0B0F3DC40B0F3A6000751CD888257BFA></a><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=1 face="Arial">
</font><font size=3><br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">Brian Mehalic &lt;brian@solarenergy.org&gt;</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">RE-wrenches &lt;re-wrenches@lists.re-wrenches.org&gt;</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">10/04/2013 01:39 PM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">Re: [RE-wrenches] Trace SWs in Energy
Management Mode</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">re-wrenches-bounces@lists.re-wrenches.org</font></table>
<br>
<hr noshade>
<br>
<br>
<br><font size=3>Thanks, I was thinking about using LBX, but the customer
is really not too excited about it. &nbsp;And based on the manual, Energy
Management Mode seems like it fits the bill, but it doesn't seem to be
going back into stand-alone/inverter mode when the timer is supossed to
turn off.</font>
<br>
<br>
<br><font size=3>Brian Mehalic <br>
NABCEP Certified Solar PV Installation Professional\u2122&nbsp;R031508-59</font>
<br><font size=3>IREC ISPQ Certified Affiliated Instructor/PV US-0132</font>
<br>
<br><font size=3>PV Curriculum Developer and Instructor</font>
<br><font size=3>Solar Energy International</font><font size=3 color=blue><u><br>
</u></font><a href=http://www.solarenergy.org/ target=_blank><font size=3 color=blue><u>http://www.solarenergy.org</u></font></a>
<br><font size=3><br>
</font>
<br><font size=3>On Fri, Oct 4, 2013 at 3:42 PM, &lt;</font><a href="mailto:Eric.Bentsen@schneider-electric.com" target=_blank><font size=3 color=blue><u>Eric.Bentsen@schneider-electric.com</u></font></a><font size=3>&gt;
wrote:</font>
<br><font size=3 face="sans-serif"><br>
Hi Brian,</font><font size=3> </font><font size=3 face="sans-serif"><br>
LBX would be better for the way this customer is using the system, because
it only connects</font><font size=3> </font><font size=3 face="sans-serif"><br>
&nbsp;to the grid when the batteries get low. Unfortunately, the timers
do not affect LBX, so charging <br>
may occur during the peak rate....or it may not :C)</font><font size=3>
<br>
</font><font size=3 face="sans-serif"><br>
Rgds,</font><font size=3> </font><font size=3 face="sans-serif"><br>
</font><font size=3 color=#008000><br>
_____________________________________________________________________________________</font><font size=3>
</font><font size=1 face="Arial"><b><br>
<br>
Eric Bentsen</b> &nbsp;| &nbsp;</font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>&nbsp; | &nbsp;Solar
Business</b> &nbsp;| &nbsp; <b>UNITED STATES</b> &nbsp;| &nbsp; <b>Technical
Support Representative</b> <b><br>
Phone:</b> +(650) 351-8237 ext. 001# &nbsp;| &nbsp; <b><br>
Email:</b> </font><a href="mailto:eric.bentsen@schneider-electric.com" target=_blank><font size=1 color=blue face="Arial"><u>eric.bentsen@schneider-electric.com</u></font></a><font size=1 face="Arial">
&nbsp;| &nbsp; <b>Site:</b></font><a href="http://www.schneider-electric.com/solar" target=_blank><font size=1 color=blue face="Arial"><u>
www.schneider-electric.com/solar</u></font></a><font size=1 face="Arial">
&nbsp;| &nbsp; <b>Address:</b> 250 South Vasco Rd., Livermore, CA 94551
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><font size=3 color=blue><u><br>
</u></font><a href="http://www.schneider-electric.com/solar" target=_blank></a><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=1 face="Arial">
</font><font size=3><br>
<br>
<br>
</font>
<table width=100%>
<tr valign=top>
<td width=14%><font size=1 color=#5f5f5f face="sans-serif">From:</font><font size=3>
</font>
<td width=85%><font size=1 face="sans-serif">Brian Mehalic &lt;</font><a href=mailto:brian@solarenergy.org target=_blank><font size=1 color=blue face="sans-serif"><u>brian@solarenergy.org</u></font></a><font size=1 face="sans-serif">&gt;</font><font size=3>
</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font><font size=3>
</font>
<td><font size=1 face="sans-serif">RE-wrenches &lt;</font><a href="mailto:re-wrenches@lists.re-wrenches.org" target=_blank><font size=1 color=blue face="sans-serif"><u>re-wrenches@lists.re-wrenches.org</u></font></a><font size=1 face="sans-serif">&gt;</font><font size=3>
</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font><font size=3>
</font>
<td><font size=1 face="sans-serif">10/04/2013 12:04 PM</font><font size=3>
</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font><font size=3>
</font>
<td><font size=1 face="sans-serif">[RE-wrenches] Trace SWs in Energy Management
Mode</font><font size=3> </font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font><font size=3>
</font>
<td><a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target=_blank><font size=1 color=blue face="sans-serif"><u>re-wrenches-bounces@lists.re-wrenches.org</u></font></a></table>
<br><font size=3><br>
</font>
<hr noshade>
<br><font size=3><br>
<br>
<br>
Have a friend that is on an electric co-op where peak $/kWh is 4x the off-peak
rate. &nbsp;Peak hours are 6-10 am in the winter and 12-6 pm in the summer.
<br>
<br>
He has relocated an older system from his previous house to his new one;
circuits were separated out to sub-panel that is connected to the inverter
AC output. &nbsp;The reinstallation is very professional. <br>
<br>
Two Trace SW4024 in series (04/96) <br>
120/240 Vac Grid connected to AC1 of each inverter <br>
575 Ah battery bank <br>
Two C40s with digital displays, ~ 4.5 kW STC array total <br>
Trimetric <br>
<br>
The goal is to not use any utility energy during peak times, unless the
low battery voltage setting is reached, and in general to run as an off-grid
system, minimizing charge time from the grid during off-peak hours as well.
&nbsp;The assumption (I know it's a tough one, but I'm coming in after
the transition) is that the PV array should at least be able to provide
the bulk of the load; using the grid to charge the batteries to ensure
they are regularly filled and to maximize their life expectancy. &nbsp;The
customer is also managing loads actively. <br>
<br>
It's been a few years, but I used to work on these all the time; however
it was usually off-grid with a genset, or fixing poorly maintained Y2K
systems which were always in float. I'm attempting to use the energy management
mode. <br>
<br>
Inverter settings: <br>
Clocks: Time is accurate <br>
Grid AC1 amps AC: 60 <br>
Max charge amps AC: 10 (each inverter) <br>
<br>
Grid usage: FLT <br>
Set start charge time: 23:00 <br>
Start bulk time: 23:10 <br>
Set end charge time: 05:00 <br>
Set float volts DC: 25.4 <br>
Bulk volts DC: 28.8 <br>
Absorb time: 1.5 hours <br>
Low battery cut-out: 22&nbsp; <br>
Low battery cut-in: 25.4 <br>
<br>
Okay, programmed the system, both inverters are inverting, AC1 is blinking
green, looks good. &nbsp;Then a well pump kicks on, registers 70 A DC on
the Trimetric. &nbsp;This causes inverter 1 to go into bulk charging and
pass through about 10 additional amps from the grid to the load (inverter
2 continued to inverter about 10 amps for the load). &nbsp;Inverter 1 soon
cycled into float, then went back to what invertering (amber light) and
green blinking AC1 (which is what I want it to be at). &nbsp; <br>
<br>
Had to leave, both the customer and I had other obligations. <br>
<br>
He took a picture of the inverter sat 11:15 pm, and they were in bulk,
battery voltage rising...exactly as planned. &nbsp;But then in the next
set of pictures, taken at 7 am, after the end of the charge time, they
were in float, not inverting, even though, based on the Trimetric readings
at 11 (64%, 85A charging), and the fact that charging would have been active
all night, they were not in anyway at a low voltage condition (Trimetric
readings am readings were 85%, trickle charge, 25.6 V). <br>
<br>
Something seems amiss. &nbsp;Any suggestions or insight? <br>
<br>
Thanks! <br>
<br>
Brian Mehalic <br>
NABCEP Certified Solar PV Installation Professional\u2122&nbsp;R031508-59 <br>
IREC ISPQ Certified Affiliated Instructor/PV US-0132 <br>
<br>
PV Curriculum Developer and Instructor <br>
Solar Energy International</font><font size=3 color=blue><u><br>
</u></font><a href=http://www.solarenergy.org/ target=_blank><font size=3 color=blue><u>http://www.solarenergy.org</u></font></a><font size=3>
</font>
<br><font size=3><br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________</font><tt><font size=3>_______________________________________________</font></tt>
<br><tt><font size=3><br>
List sponsored by Home Power magazine<br>
<br>
List Address: </font></tt><a href="mailto:RE-wrenches@lists.re-wrenches.org" target=_blank><tt><font size=3 color=blue><u>RE-wrenches@lists.re-wrenches.org</u></font></tt></a><tt><font size=3><br>
<br>
Change email address &amp; settings:</font></tt>
<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target=_blank><tt><font size=3 color=blue><u>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</u></font></tt></a><tt><font size=3><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target=_blank><tt><font size=3 color=blue><u>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</u></font></tt></a><tt><font size=3><br>
<br>
List rules &amp; etiquette:</font></tt><font size=3 color=blue><u><br>
</u></font><a href="http://www.re-wrenches.org/etiquette.htm" target=_blank><tt><font size=3 color=blue><u>www.re-wrenches.org/etiquette.htm</u></font></tt></a><tt><font size=3><br>
<br>
Check out participant bios:</font></tt><font size=3 color=blue><u><br>
</u></font><a href="http://www.members.re-wrenches.org/" target=_blank><tt><font size=3 color=blue><u>www.members.re-wrenches.org</u></font></tt></a><tt><font size=3><br>
</font></tt><font size=3><br>
<br>
</font>
<br><font size=3><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: </font><a href="mailto:RE-wrenches@lists.re-wrenches.org"><font size=3 color=blue><u>RE-wrenches@lists.re-wrenches.org</u></font></a><font size=3><br>
<br>
Change email address &amp; settings:</font><font size=3 color=blue><u><br>
</u></font><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target=_blank><font size=3 color=blue><u>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</u></font></a><font size=3><br>
<br>
List-Archive: </font><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target=_blank><font size=3 color=blue><u>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</u></font></a><font size=3><br>
<br>
List rules &amp; etiquette:</font><font size=3 color=blue><u><br>
</u></font><a href="http://www.re-wrenches.org/etiquette.htm" target=_blank><font size=3 color=blue><u>www.re-wrenches.org/etiquette.htm</u></font></a><font size=3><br>
<br>
Check out participant bios:</font><font size=3 color=blue><u><br>
</u></font><a href="http://www.members.re-wrenches.org/" target=_blank><font size=3 color=blue><u>www.members.re-wrenches.org</u></font></a><font size=3><br>
<br>
</font>
<br>
<br><font size=3><br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________</font><tt><font size=2>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change email address &amp; settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List rules &amp; etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
</font></tt>
<br>
<br>