<div dir="ltr"><div>Sole connection indicates that a GEC is connected to only one type of grounding electrode. This term is easily mis- understood. For example, a GEC can be connected to more than one grounding electrodesay, two ground rodsand still be considered to have a sole connection. Similarly, multiple GECs connected to the same grounding electrode are each considered to have a sole connection. When GECs have a sole connection, their maximum size is limited per NEC Sections 250.66 for an ac system and 250.166 for a dc system. The 2014 NEC adds some clarification on this.</div>
<div><br></div><div class="gmail_extra"><div><div dir="ltr"><div>Brian Mehalic <br>NABCEP Certified Solar PV Installation ProfessionalR031508-59<div>IREC ISPQ Certified Affiliated Instructor/PV US-0132<br><div><br></div>
<div>PV Curriculum Developer and Instructor<div>Solar Energy International<br><a href="http://www.solarenergy.org" target="_blank">http://www.solarenergy.org</a></div></div></div></div></div></div>
<br><br><div class="gmail_quote">On Wed, Sep 18, 2013 at 4:52 PM, Aladdin Solar <span dir="ltr">&lt;<a href="mailto:cpickard@aladdinsolar.com" target="_blank">cpickard@aladdinsolar.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<u></u>





<div lang="EN-US" link="blue" bgcolor="#ffffff" vlink="purple">
<div><font face="Arial">Yes, Jay,this is a TenKSolar system 
--they certainly do havea habit of taking the &#39;thinking outside the 
box&#39; approach!</font></div>
<div><font face="Arial"></font></div>
<div><font face="Arial">The microinverter manufacturer states in their 
installation manual, &quot;Connect the grounding electrode conductor to the 
microinverter ground clamp&quot; so it&#39;squite clear we are dealing with GEC 
rules.</font></div>
<div><font face="Arial"></font></div>
<div><font face="Arial">Thanks for all your comments and the reminder of 
the NEC 250.166(C) exception which I hadn&#39;t really connected with before. 
</font></div>
<div><font face="Arial"></font></div>
<div><font face="Arial">I&#39;m having difficulty understanding what the 
requirement in that paragraph actually means. When it states &quot;that portion of 
the grounding electrode conductor that is the sole connection to the grounding 
electrode shall not be required to be larger than 6AWG...&quot; -- what does &quot;that 
portion&quot; and &quot;sole connection&quot; mean? If we have a number of GEC branches from 
that are irreversably spliced to a single 6AWGconductor bonded to the 
grounding electrode, do those various GECs affect the &quot;that portion&quot; and &quot;sole 
connection&quot; at all?</font></div><div class="im">
<div><font face="Arial"></font></div>
<div><font face="Arial">Charlie Pickard<br>NABCEP Certified PV Installation 
Professional <br>Aladdin Solar, LLC</font></div>
<div><font face="Arial"></font></div>
<div><font face="Arial"></font></div>
</div><blockquote style="BORDER-LEFT:#000000 2px solid;PADDING-LEFT:5px;PADDING-RIGHT:0px;MARGIN-LEFT:5px;MARGIN-RIGHT:0px"><div><div class="h5">
  <div style="FONT:10pt arial">----- Original Message ----- </div>
  <div style="FONT:10pt arial;BACKGROUND:#e4e4e4"><b>From:</b> 
  <a title="billbrooks7@yahoo.com" href="mailto:billbrooks7@yahoo.com" target="_blank">Bill 
  Brooks</a> </div>
  <div style="FONT:10pt arial"><b>To:</b> <a title="re-wrenches@lists.re-wrenches.org" href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">&#39;RE-wrenches&#39;</a> </div>
  <div style="FONT:10pt arial"><b>Sent:</b> Wednesday, September 18, 2013 2:42 
  PM</div>
  <div style="FONT:10pt arial"><b>Subject:</b> Re: [RE-wrenches] GEC sizing for 
  a high amp,low voltage PV system with microinverters</div>
  <div><br></div>
  <div>
  <p class="MsoNormal"><span style="FONT-FAMILY:&#39;Calibri&#39;,&#39;sans-serif&#39;;COLOR:#1f497d;FONT-SIZE:11pt">Nick,<u></u><u></u></span></p>
  <p class="MsoNormal"><span style="FONT-FAMILY:&#39;Calibri&#39;,&#39;sans-serif&#39;;COLOR:#1f497d;FONT-SIZE:11pt"><u></u><u></u></span></p>
  <p class="MsoNormal"><span style="FONT-FAMILY:&#39;Calibri&#39;,&#39;sans-serif&#39;;COLOR:#1f497d;FONT-SIZE:11pt">Thanks 
  for the clarificationit is a mysterious threaded hole.<u></u><u></u></span></p>
  <p class="MsoNormal"><span style="FONT-FAMILY:&#39;Calibri&#39;,&#39;sans-serif&#39;;COLOR:#1f497d;FONT-SIZE:11pt"><u></u><u></u></span></p>
  <p class="MsoNormal"><span style="FONT-FAMILY:&#39;Calibri&#39;,&#39;sans-serif&#39;;COLOR:#1f497d;FONT-SIZE:11pt">Bill.<u></u><u></u></span></p>
  <p class="MsoNormal"><span style="FONT-FAMILY:&#39;Calibri&#39;,&#39;sans-serif&#39;;COLOR:#1f497d;FONT-SIZE:11pt"><u></u><u></u></span></p>
  <p class="MsoNormal"><b><span style="FONT-FAMILY:&#39;Calibri&#39;,&#39;sans-serif&#39;;FONT-SIZE:11pt">From:</span></b><span style="FONT-FAMILY:&#39;Calibri&#39;,&#39;sans-serif&#39;;FONT-SIZE:11pt"> <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a> 
  [mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of </b>Nick 
  Soleil<br><b>Sent:</b> Wednesday, September 18, 2013 10:19 AM<br><b>To:</b> 
  RE-wrenches<br><b>Subject:</b> Re: [RE-wrenches] GEC sizing for a high amp, 
  low voltage PV system with microinverters<u></u><u></u></span></p>
  <p class="MsoNormal"><u></u><u></u></p>
  <div>
  <div>
  <p style="MARGIN-BOTTOM:12pt" class="MsoNormal">Hi Bill and 
  wrenches,<u></u><u></u></p></div>
  <p class="MsoNormal">To clarify, our new Enphase M250 microinverter does not 
  have a grounding terminal. The grounding of the M250 will be provided 
  through the Engage cable. We only have a hole in the lid, in the rare 
  case that a lug will be desired or required by the AHJ, but we do not provide 
  the grounding clip with the microinverter. A grounding terminal can be 
  added to the microinverter. We have an application note on alternate 
  grounding methods for the M250, if needed.<u></u><u></u></p></div>
  <div>
  <p style="MARGIN-BOTTOM:12pt" class="MsoNormal"><u></u><u></u></p></div><pre><u></u><u></u></pre></div><br><br></div></div>__________ Information from ESET 
  NOD32 Antivirus, version of virus signature database 8815 (20130918) 
  __________<div class="im"><br><br>The message was checked by ESET NOD32 Antivirus.<br><br><a href="http://www.eset.com" target="_blank">http://www.eset.com</a><br>
  </div><p></p><div class="im">
  <hr>

  <p></p>_______________________________________________<br>List sponsored by 
  Home Power magazine<br><br>List Address: 
  <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Change email address &amp; 
  settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: 
  <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List 
  rules &amp; etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br><br>Check out 
  participant bios:<br><a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br><br><br><br><br></div>__________ 
  Information from ESET NOD32 Antivirus, version of virus signature database 
  8815 (20130918) __________<div class="im"><br><br>The message was checked by ESET NOD32 
  Antivirus.<br><br><a href="http://www.eset.com" target="_blank">http://www.eset.com</a><br><br></div><p></p></blockquote><br>
<br>
__________ Information from ESET NOD32 Antivirus, version of virus signature database 8817 (20130918) __________<div class="im"><br>
<br>
The message was checked by ESET NOD32 Antivirus.<br>
<br>
<a href="http://www.eset.com" target="_blank">http://www.eset.com</a><br>


</div></div>
<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div></div>