<div dir="ltr">boB,<div><br></div><div>I see and understand the functionality of the input-output bypass switch (breakers). The other breaker labeled &quot;Sunny Boy(s) Input&quot; in the drawing and labeled &quot;Grid Tie Inverter&quot; on the unit, seems to provide a single OCPD for the combined input of the two inverters. The SB 5000 has a maximum output current of 22A and the SB3000 a 15A max output. Seems we should have output breakers on each inverter circuit prior to connection to the SMA E-panel busbar.</div>
<div><br></div><div>It seems there are a couple of options.</div><div>1) A small AC combiner panel with a suitably sizedbreaker protecting each inverter and #6 conductors run from the AC combiner to the SunnyBoy input bus bar in the E-panel. The 60A OCPD (&quot;grid Tie Inverter&quot;) in the E-panel protecting this circuit.</div>
<div>2) Two suitably sized AC breakers installed on the extra DIN rail on the right hand side of the E-panel and output of these breakers feeding the busbar.</div><div>3) Run #6 conductors from the E-Panel Sunny Boy Input Busbars back to each inverter output circuit, and let the 60A &quot;Sunny Boy(s) Input&quot; breaker provide the OCPD for both inverters. Not sure this option passes muster with a single OCPD protecting two devices.</div>
<div><br></div><div>I hope that clarifies the question.</div><div class="gmail_extra"><br>Thanks</div><div class="gmail_extra">Carl</div><div class="gmail_extra"><br><div class="gmail_quote">On Mon, Sep 16, 2013 at 4:32 PM, <a href="mailto:boB@midnitesolar.com">boB@midnitesolar.com</a> <span dir="ltr">&lt;<a href="mailto:boB@midnitesolar.com" target="_blank">boB@midnitesolar.com</a>&gt;</span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div text="#000000" bgcolor="#FFFFFF">
    <div><br>
      Carl, there are actually 2 (two) Sunny Island AC load output
      breakers.<br>
      One set is in the AC input-output bypass switch and the other are<br>
      separate breakers so you can turn off the inverter output.<br>
      <br>
      The Sunny Boy outputs also go through a 2-pole circuit breaker.<br>
      <br>
      What OCPD are you referring to ?<span class="HOEnZb"><font color="#888888"><br>
      <br>
      boB</font></span><div><div class="h5"><br>
      <br>
      <br>
      <br>
      On 9/16/2013 12:31 PM, Carl Adams wrote:<br>
    </div></div></div><div><div class="h5">
    <blockquote type="cite">
      <div dir="ltr">Hello Wrenches,
        <div><br>
        </div>
        <div>We are installing our first Midnite Solar E-panel for SMA.
          The epanel has a bus bar for landing the inverter output
          circuits. The attached diagram from Midnite does not include
          any OCPD in the circuit, but it seems to me these will be
          required . We&#39;ll be installing an SMA SB3000TL and SB5000TL.
          Have any of you installed this SMA E-Panel configuration
          before and if so how did you handle this piece of it?
          <div>
            <br>
          </div>
          <div>Thanks in Advance</div>
          <div>Carl Adams</div>
          <div>SunRock Solar</div>
        </div>
      </div>
      <br>
      <fieldset></fieldset>
      <br>
    </blockquote>
    <br>
  </div></div></div>

</blockquote></div><br></div></div>