<html><head><meta http-equiv="Content-Type" content="text/html charset=us-ascii"></head><body style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; ">William,<div><br></div><div>I have a couple customers in a similar situation. The homes are Mexico and they need to operate mini split A/C for a few months. There is no space for increasing the PV array. Once the generator run time is balanced to maintain the batteries between 50% and 80% while also handling any heavy loads, the system can perform well daily.&nbsp;</div><div><br></div><div>The downside is that this deficit charging will lead to early battery failure. The solution I use is to have a "Full Charge Day" bimonthly. The customer must operate the generator through the Bulk and Absorb charge and then start a short, high voltage equalization charge for about 2 hours followed by battery SG testing. This method is the best I could come up with and seems to be working well. During the other months, the PV system can keep up with consumption.</div><div><br></div><div>I too am getting more large system requests. If space is not a problem, I install large PV arrays to minimize generator use.</div><div><br></div><div>Larry</div><div><br></div><div><br>
<br><div><div>On Aug 16, 2013, at 12:53 PM, William Miller &lt;<a href="mailto:william@millersolar.com">william@millersolar.com</a>&gt; wrote:</div><br class="Apple-interchange-newline">

<meta content="text/html; charset=us-ascii" http-equiv="Content-Type">
<meta name="GENERATOR" content="MSHTML 8.00.6001.23515">
<div>
<div><span class="353174017-16082013"><font size="4" face="Arial">Friends:</font></span></div>
<div><span class="353174017-16082013"><font size="4" face="Arial"></font></span>&nbsp;</div>
<div><span class="353174017-16082013"><font size="4" face="Arial">We have been 
receiving a flurry of requests for design of off-grid systems where the loads 
are enormous, relative to normal off-grid requirements.&nbsp; It is obvious that 
the size of PV and battery&nbsp;arrays to power these loads is beyond what is 
practical.&nbsp; We have dubbed these systems Generator/battery with PV assist, 
or PV assist for short.</font></span></div>
<div><span class="353174017-16082013"><font size="4" face="Arial"></font></span>&nbsp;</div>
<div><span class="353174017-16082013"><font size="4" face="Arial">These systems will 
cycle batteries multiple times per day.&nbsp; It is my understanding that the 
extra battery cycels will shorten battery life.&nbsp; Since generator run is 
expected, we are willing to increase generator run time in order to prolong 
battery life.</font></span></div>
<div><span class="353174017-16082013"><font size="4" face="Arial"></font></span>&nbsp;</div>
<div><span class="353174017-16082013"><font size="4" face="Arial">The parameters I 
suggest are an aggressive load start and a very high battery start 
parameter.&nbsp; This will prevent deep discharge of the battery bank.&nbsp; I 
know shallow discharge is not the norm, but I don't believe shallow cycling is a 
problem as long is it as at the top of the voltage window, i.e. the batteries 
achieve absorption at least once per day.</font></span></div>
<div><span class="353174017-16082013"><font size="4" face="Arial"></font></span>&nbsp;</div>
<div><span class="353174017-16082013"><font size="4" face="Arial">We know a load 
start&nbsp;ciuld result in an abbreviated run time, curtailing absorption 
period, but we are assuming there will be a battery votage start at least once 
per day allowing full absorption.</font></span></div>
<div><span class="353174017-16082013"><font size="4" face="Arial"></font></span>&nbsp;</div>
<div><span class="353174017-16082013"><font size="4" face="Arial">Has anyone else 
considered these issues, and what conclusions did you make</font></span></div>
<div><span class="353174017-16082013"><font size="4" face="Arial"></font></span>&nbsp;</div>
<div><span class="353174017-16082013"><font size="4" face="Arial">I am looking forward 
to a spirited discussion as usual.&nbsp; I throuroughlyenjoy and beneift from 
them, even thought the&nbsp;advice is usually conflilcting. &nbsp;Thanks in 
advance.</font></span></div>
<div><span class="353174017-16082013"><font size="4" face="Arial"></font></span>&nbsp;</div>
<div><span class="353174017-16082013"><font size="4" face="Arial">William 
Miller</font></span></div>
<div><span class="353174017-16082013"><font size="4" face="Arial"></font></span>&nbsp;</div></div>
_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Change email address &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br><br>List rules &amp; etiquette:<br>www.re-wrenches.org/etiquette.htm<br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br></div><br></div></body></html>