<br><font size=2 face="sans-serif">Hi William,</font>
<br><font size=2 face="sans-serif">In off grid applications, you want to
have sufficient RE to keep up with load demand </font>
<br><font size=2 face="sans-serif">and only run the generator when RE cannot
keep up. However, having too much RE is a waste because it will</font>
<br><font size=2 face="sans-serif">&nbsp;result in energy not harvested
(if regulating), however, diversion controllers can allow the excess energy
to be utilized</font>
<br><font size=2 face="sans-serif">&nbsp;(i.e. water heating).</font>
<br><font size=2 face="sans-serif">Running the gen up to the bulk level
replaces approx 80% of capacity, and maximizes fuel consumption, allowing
RE to get the</font>
<br><font size=2 face="sans-serif">&nbsp;batteries charged the last 20%.
Automatic gen start capability with staggered start voltages allow you
to target 50% discharge </font>
<br><font size=2 face="sans-serif">more accurately, and minimizes user
interaction. Try to calculate the total daily kWhrs and match the demand
with RE as </font>
<br><font size=2 face="sans-serif">closely as possible. </font>
<br><font size=2 face="sans-serif">Hope that helps,</font>
<br><font size=2 face="sans-serif">Rgds,<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Eric Bentsen</b> &nbsp;| &nbsp;</font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>&nbsp; | &nbsp;Solar
Business</b> &nbsp;| &nbsp; <b>UNITED STATES</b> &nbsp;| &nbsp; <b>Technical
Support Representative</b> <b><br>
Phone:</b> +(650) 351-8237 ext. 001# &nbsp;| &nbsp; <b><br>
Email:</b> </font><a href="mailto:eric.bentsen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>eric.bentsen@schneider-electric.com</u></font></a><font size=1 face="Arial">
&nbsp;| &nbsp; <b>Site:</b></font><a href="http://www.schneider-electric.com/solar" target=_blank><font size=1 color=blue face="Arial"><u>
www.schneider-electric.com/solar</u></font></a><font size=1 face="Arial">
&nbsp;| &nbsp; <b>Address:</b> 250 South Vasco Rd., Livermore, CA 94551
<br>
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><a href="www.schneider-electric.com/solar"><img src=cid:_2_0554738005546FD8007589B588257BC9></a><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=1 face="Arial">
</font><font size=3><br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">Jay Peltz &lt;jay@asis.com&gt;</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">RE-wrenches &lt;re-wrenches@lists.re-wrenches.org&gt;</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">08/16/2013 02:01 PM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">Re: [RE-wrenches] PV Assist</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">re-wrenches-bounces@lists.re-wrenches.org</font></table>
<br>
<hr noshade>
<br>
<br>
<br><font size=3>Hi William </font>
<br>
<br><font size=3>Thx helps a lot. </font>
<br><font size=3>I can only say how I do it. </font>
<br><font size=3>I'll give the client some options, including the change
of appliances and usually the price difference makes the sale one way or
the other. </font>
<br>
<br><font size=3>Funny reminds me of the old days, only with much smaller
loads/$. </font>
<br>
<br><font size=3>Good luck</font>
<br>
<br><font size=3>Jay</font>
<br>
<br><font size=3><br>
<br>
Sent from my iPhone</font>
<br><font size=3><br>
On Aug 16, 2013, at 12:49 PM, &quot;William Miller&quot; &lt;</font><a href=mailto:william@millersolar.com><font size=3 color=blue><u>william@millersolar.com</u></font></a><font size=3>&gt;
wrote:<br>
</font>
<br><font size=4 color=blue face="Arial">Jay:</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 color=blue face="Arial">There are four systems in question.
&nbsp;In three the loads are year round and one is summer only AC loads.
&nbsp;The year round loaded systems have loads day and night.</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 color=blue face="Arial">One is a highway maintenence station
with at least 4 residences.</font>
<br><font size=4 color=blue face="Arial">One is a family compound with
two homes with electric ranges, water heaters, AC units (I know its stupid,
lord knows I've tried to convince them to change appliances.)</font>
<br><font size=4 color=blue face="Arial">One is an animal rescue operation
with heater loads.</font>
<br><font size=4 color=blue face="Arial">One is a large home with 5 very
small, very new, very sophisticated and frugal AC units</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 color=blue face="Arial">I know it is silly to move these
loads off-grid, but people do it and they will hire someone to work on
the systems. &nbsp;It may as well be me, doing the best I can to use the
resources as wisely as possible.</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 color=blue face="Arial">William</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 color=blue face="Arial">PS: &nbsp;It always happens like
this: &nbsp;I get a call from a client with problems. &nbsp;Well, of course
their expensive battery bank died and it died because of wasteful appliances.
&nbsp;The prescription is a new, expensive battery bank and, at the same
time, new, expensive, efficient appliances. &nbsp;They complain can't afford
both and they have to have the batteries, so that is what they get. &nbsp;Repeat
every two years. &nbsp;Sad....</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 color=blue face="Arial">Wm</font>
<br><font size=3>&nbsp;</font>
<br><font size=3>&nbsp;</font>
<br>
<hr><font size=2 face="Tahoma"><b>From:</b> </font><a href="mailto:re-wrenches-bounces@lists.re-wrenches.org"><font size=2 color=blue face="Tahoma"><u>re-wrenches-bounces@lists.re-wrenches.org</u></font></a><font size=2 face="Tahoma">
[</font><a href="mailto:re-wrenches-bounces@lists.re-wrenches.org"><font size=2 color=blue face="Tahoma"><u>mailto:re-wrenches-bounces@lists.re-wrenches.org</u></font></a><font size=2 face="Tahoma">]
<b>On Behalf Of </b>Jay Peltz<b><br>
Sent:</b> Friday, August 16, 2013 12:22 PM<b><br>
To:</b> RE-wrenches<b><br>
Subject:</b> Re: [RE-wrenches] PV Assist</font><font size=3><br>
</font>
<br><font size=3>Hi William</font>
<br>
<br><font size=3>I feel it's impossible to discuss without more specifics.
</font>
<br>
<br><font size=3>For example if the extreme loads are only every ( just
run the genny) so often vs seasonal ( maybe AC coupling makes more sense
vs cycling a extremely expensive battery 4 x day), &nbsp;vs year round
vs what is do able etc</font>
<br>
<br><font size=3>I would be curious to know what some of the parameters
are, as I'm sure others as well</font>
<br>
<br><font size=3>Jay</font>
<br>
<br><font size=3>Peltz power. </font>
<br>
<br>
<br>
<br><font size=3><br>
<br>
Sent from my iPhone</font>
<br><font size=3><br>
On Aug 16, 2013, at 10:53 AM, &quot;William Miller&quot; &lt;</font><a href=mailto:william@millersolar.com><font size=3 color=blue><u>william@millersolar.com</u></font></a><font size=3>&gt;
wrote:<br>
</font>
<br><font size=4 face="Arial">Friends:</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 face="Arial">We have been receiving a flurry of requests
for design of off-grid systems where the loads are enormous, relative to
normal off-grid requirements. &nbsp;It is obvious that the size of PV and
battery arrays to power these loads is beyond what is practical. &nbsp;We
have dubbed these systems Generator/battery with PV assist, or PV assist
for short.</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 face="Arial">These systems will cycle batteries multiple
times per day. &nbsp;It is my understanding that the extra battery cycels
will shorten battery life. &nbsp;Since generator run is expected, we are
willing to increase generator run time in order to prolong battery life.</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 face="Arial">The parameters I suggest are an aggressive
load start and a very high battery start parameter. &nbsp;This will prevent
deep discharge of the battery bank. &nbsp;I know shallow discharge is not
the norm, but I don't believe shallow cycling is a problem as long is it
as at the top of the voltage window, i.e. the batteries achieve absorption
at least once per day.</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 face="Arial">We know a load start ciuld result in an abbreviated
run time, curtailing absorption period, but we are assuming there will
be a battery votage start at least once per day allowing full absorption.</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 face="Arial">Has anyone else considered these issues,
and what conclusions did you make</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 face="Arial">I am looking forward to a spirited discussion
as usual. &nbsp;I throuroughlyenjoy and beneift from them, even thought
the advice is usually conflilcting. &nbsp;Thanks in advance.</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 face="Arial">William Miller</font>
<br><font size=3>&nbsp;</font>
<br><font size=3>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: </font><a href="mailto:RE-wrenches@lists.re-wrenches.org"><font size=3 color=blue><u>RE-wrenches@lists.re-wrenches.org</u></font></a><font size=3><br>
<br>
Change email address &amp; settings:</font><font size=3 color=blue><u><br>
</u></font><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><font size=3 color=blue><u>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</u></font></a><font size=3><br>
<br>
List-Archive: </font><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><font size=3 color=blue><u>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</u></font></a><font size=3><br>
<br>
List rules &amp; etiquette:</font><font size=3 color=blue><u><br>
</u></font><a href="http://www.re-wrenches.org/etiquette.htm"><font size=3 color=blue><u>www.re-wrenches.org/etiquette.htm</u></font></a><font size=3><br>
<br>
Check out participant bios:</font><font size=3 color=blue><u><br>
</u></font><a href="http://www.members.re-wrenches.org/"><font size=3 color=blue><u>www.members.re-wrenches.org</u></font></a><font size=3><br>
</font>
<br><font size=3>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: </font><a href="mailto:RE-wrenches@lists.re-wrenches.org"><font size=3 color=blue><u>RE-wrenches@lists.re-wrenches.org</u></font></a><font size=3><br>
<br>
Change email address &amp; settings:</font><font size=3 color=blue><u><br>
</u></font><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><font size=3 color=blue><u>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</u></font></a><font size=3><br>
<br>
List-Archive: </font><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><font size=3 color=blue><u>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</u></font></a><font size=3><br>
<br>
List rules &amp; etiquette:</font><font size=3 color=blue><u><br>
</u></font><a href="http://www.re-wrenches.org/etiquette.htm"><font size=3 color=blue><u>www.re-wrenches.org/etiquette.htm</u></font></a><font size=3><br>
<br>
Check out participant bios:</font><font size=3 color=blue><u><br>
</u></font><a href="http://www.members.re-wrenches.org/"><font size=3 color=blue><u>www.members.re-wrenches.org</u></font></a><font size=3><br>
</font>
<br><font size=3><br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________</font><tt><font size=2>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change email address &amp; settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List rules &amp; etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
</font></tt>
<br>
<br>