<br><font size=2 face="sans-serif">Hi William,</font>
<br><font size=2 face="sans-serif">Fluid intrusion can be very problematic
and lead to highly erratic behavior, if not a complete shutdown.</font>
<br><font size=2 face="sans-serif">If an IC was internally damaged by moisture
allowing for an undesirable current path, then a chipset may </font>
<br><font size=2 face="sans-serif">solve the issue. It may be a challenge
to clean sufficiently unless you remove (unsolder) the DIP sockets (big
job). </font>
<br><font size=2 face="sans-serif">&nbsp;However, if other components were
damaged, it may require a complete control board replacement. </font>
<br><font size=2 face="sans-serif">We still have them available, if you
want pricing, email me off list.</font>
<br><a href="mailto:eric.bentsen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>eric.bentsen@schneider-electric.com</u></font></a>
<br><font size=2 face="sans-serif">Rgds,</font>
<br><font size=2 face="sans-serif"><br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Eric Bentsen</b> &nbsp;| &nbsp;</font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>&nbsp; | &nbsp;Solar
Business</b> &nbsp;| &nbsp; <b>UNITED STATES</b> &nbsp;| &nbsp; <b>Technical
Support Representative</b> <b><br>
Phone:</b> +(650) 351-8237 ext. 001# &nbsp;| &nbsp; <b><br>
Email:</b> </font><a href="mailto:eric.bentsen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>eric.bentsen@schneider-electric.com</u></font></a><font size=1 face="Arial">
&nbsp;| &nbsp; <b>Site:</b></font><a href="http://www.schneider-electric.com/solar" target=_blank><font size=1 color=blue face="Arial"><u>
www.schneider-electric.com/solar</u></font></a><font size=1 face="Arial">
&nbsp;| &nbsp; <b>Address:</b> 250 South Vasco Rd., Livermore, CA 94551
<br>
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><a href="www.schneider-electric.com/solar"><img src=cid:_2_094B8348094B7F000077B46888257BC8></a><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=1 face="Arial">
</font><font size=3><br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">&quot;William Miller&quot; &lt;william@millersolar.com&gt;</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">&quot;RE-wrenches&quot; &lt;re-wrenches@lists.re-wrenches.org&gt;</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">08/15/2013 02:37 PM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">[RE-wrenches] Mouse pee in the SW</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">re-wrenches-bounces@lists.re-wrenches.org</font></table>
<br>
<hr noshade>
<br>
<br>
<br><font size=4 face="Arial">Friends:</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 face="Arial">I had a mouse take up residency in an SW
inverter (SW4024). &nbsp;It peed on the top circuit board and chewed on
one wire, at least that we found. &nbsp;We have had this happen before
and solved the problem by cleaning and drying. &nbsp;</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 face="Arial">This time the mouse pee was minimal and cleaned
off easily and what appeared to be throughly. &nbsp;However we can't get
the inverter to work reliably. &nbsp;Sometimes it works and sometimes it
does not. &nbsp;The overload light is solid and the error light flashes.
&nbsp;The controls work on some menus and not on others. &nbsp;If I shut
the inverter down it won't come back on. &nbsp;I take off the cover, look
around, connect and disconnect ribon cables and it comes back on, only
to go out a day later.</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 face="Arial">I have a spare display and chipset. &nbsp;I
am considering changing out one then the other.</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 face="Arial">Any adivce would be appreciated.</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 face="Arial">As always, I am very grateful to all of you.
&nbsp;It seems I have been receiving more advice than I have been giving
lately so I look forwards to the opportuntiy to reciprocate.</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 face="Arial">Sincerely,</font>
<br><font size=3>&nbsp;</font>
<br><font size=4 face="Arial">William Miller</font>
<br><font size=3><br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________</font><tt><font size=2>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change email address &amp; settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List rules &amp; etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
</font></tt>
<br>
<br>