    Allan<br>
    The MNSPD115 is designed for low voltage. As you pointed out 90VAC
    or less. So there is a chance it was conducting some and causing the
    Outback to stay awake. The Proper use of the MNSPD115 is for Low
    voltage control circuits and the likes. <br>
    <br>
    In the case of 120VAC or 120/240VAC the MNSPD300 is the proper
    choice.<br>
    <br>
    I apologize for the confusion and promise to look over the website
    and literature asap. <br>
    <br>
    Ryan<br>
    <img src="cid:part1.07050902.05040101@kb1uas.com" border="0"><br>
    <br>
    <div class="moz-cite-prefix">On 8/13/2013 2:22 PM, Allan Sindelar
      wrote:<br>
    </div>
    <blockquote cite="mid:520A7979.5070808@positiveenergysolar.com"
      type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      <div class="moz-cite-prefix">Ryan,<br>
        I may have found the answer to my original post, but it raises
        more questions. <br>
        <br>
        I wrote that these were MV units (MNSPD300), but I checked with
        my lead tech and learned that in both cases he used LV units
        (MNSPD115). Could this be the reason? He told me that he has
        used the LV with 120V inverters and the MV with 120/240V
        inverters. The instruction manual states that the LV units are
        designed to be used on nominal 90VAC and 115VDC circuits, and
        have a Maximum Continuous Operating Voltage of 180V. The manual
        states: "The MidNite Solar SPD voltage rating should be chosen
        according to the nominal voltage of the system. Do not install
        an SPD with Maximum Continuous Operating Voltage (MCOV) below
        the nominal voltage of the system; this will deteriorate the SPD
        and making it unavailable when you most need it." If this is
        true, then the LV (with its 180 MCOV) should be fine at 120VAC.
        The instructions are confusing: should we use an MNSPD115 or an
        MNSPD300 with 120VAC output? And in this case, could this be the
        cause of the failure-to-sleep problem?<br>
        <br>
        If we should be using the MNSPD300 with 120VAC inverter output,
        then the description on the Midnite website is confusing at
        best. It states that the MNSPD115 "is designed for both AC and
        DC systems and provides protection to service panels, load
        centers or where the SPD is directly connected to the electronic
        device requiring protection." But service panels and load
        centers seldom if ever carry AC at less than 90VAC, the nominal
        rating of the MNSPD115. Please clarify all of this!<br>
        <br>
        Thanks, Allan<br>
        <div class="moz-signature">
          <meta http-equiv="Content-Type" content="text/html;
            charset=ISO-8859-1">
          <meta name="ProgId" content="Word.Document">
          <meta name="Generator" content="Microsoft Word 11">
          <meta name="Originator" content="Microsoft Word 11">
          <link rel="File-List" href="SignatureNew_files/filelist.xml">
          <!--[if gte mso 9]><xml>
 <o:DocumentProperties>
  <o:Author>pe</o:Author>
  <o:Template>Normal</o:Template>
  <o:LastAuthor>pe</o:LastAuthor>
  <o:Revision>5</o:Revision>
  <o:TotalTime>1</o:TotalTime>
  <o:Created>2013-06-07T19:15:00Z</o:Created>
  <o:LastSaved>2013-06-10T19:03:00Z</o:LastSaved>
  <o:Pages>1</o:Pages>
  <o:Words>73</o:Words>
  <o:Characters>420</o:Characters>
  <o:Company>pe</o:Company>
  <o:Lines>3</o:Lines>
  <o:Paragraphs>1</o:Paragraphs>
  <o:CharactersWithSpaces>492</o:CharactersWithSpaces>
  <o:Version>11.9999</o:Version>
 </o:DocumentProperties>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:WordDocument>
  <w:SpellingState>Clean</w:SpellingState>
  <w:GrammarState>Clean</w:GrammarState>
  <w:ValidateAgainstSchemas/>
  <w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
  <w:IgnoreMixedContent>false</w:IgnoreMixedContent>
  <w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
  <w:Compatibility>
   <w:UseFELayout/>
  </w:Compatibility>
  <w:BrowserLevel>MicrosoftInternetExplorer4</w:BrowserLevel>
 </w:WordDocument>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:LatentStyles DefLockedState="false" LatentStyleCount="156">
 </w:LatentStyles>
</xml><![endif]-->
          <style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:"MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-alt:"\FF2D\FF33 \660E\671D";
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
@font-face
        {font-family:"\@MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {mso-style-parent:"";
        margin:0in;
        margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:12.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"MS Mincho";
        color:black;}
a:link, span.MsoHyperlink
        {color:blue;}
a:visited, span.MsoHyperlinkFollowed
        {color:blue;}
span.SpellE
        {mso-style-name:"";
        mso-spl-e:yes;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.25in 1.0in 1.25in;
        mso-header-margin:.5in;
        mso-footer-margin:.5in;
        mso-paper-source:0;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 10]>
<style>
 /* Style Definitions */
 table.MsoNormalTable
        {mso-style-name:"Table Normal";
        mso-tstyle-rowband-size:0;
        mso-tstyle-colband-size:0;
        mso-style-noshow:yes;
        mso-style-parent:"";
        mso-padding-alt:0in 5.4pt 0in 5.4pt;
        mso-para-margin:0in;
        mso-para-margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:10.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"Times New Roman";
        mso-ansi-language:#0400;
        mso-fareast-language:#0400;
        mso-bidi-language:#0400;}
</style>
<![endif]--><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="4098"/>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1"/>
 </o:shapelayout></xml><![endif]-->
          <div class="Section1">
            <p class="MsoNormal"><span style="font-size:10.0pt"><span
                  style="mso-spacerun:yes">&nbsp;</span></span></p>
          </div>
        </div>
        On 8/13/2013 11:28 AM, Ryan wrote:<br>
      </div>
      <blockquote cite="mid:520A6CC4.3070201@kb1uas.com" type="cite">
        <meta content="text/html; charset=ISO-8859-1"
          http-equiv="Content-Type">
        Allan<br>
        That is not expected behavior. Which model of SPD are you using?<br>
        <br>
        Ryan<br>
        <img src="cid:part2.09030603.07050400@kb1uas.com" border="0"><br>
        <br>
        <br>
        <div class="moz-cite-prefix">On 8/13/2013 1:08 PM, Allan
          Sindelar wrote:<br>
        </div>
        <blockquote cite="mid:520A680E.1050302@positiveenergysolar.com"
          type="cite">
          <meta http-equiv="content-type" content="text/html;
            charset=ISO-8859-1">
          Wrenches,<br>
          Very seldom do inverters in off grid systems ever go to sleep
          anymore, given the increase in phantom electronic loads and
          greater customer expectations. Coupled with lower module
          prices, we usually size larger arrays and inverters remain on
          continuously. However, we also service and upgrade many
          existing systems, and some customers still want their
          inverters to go into search mode. They typically either have
          gotten used to a more energy frugal lifestyle over many years,
          or (to their credit) choose to buck the system and live with a
          lighter energy and resource footprint. <br>
          <br>
          Twice in recent months we have added Midnite MNSPD MV surge
          arrestors to the AC output of smaller systems and discovered
          that the inverters will no longer go into search mode. It
          doesn't appear to make any difference where the search watts
          threshhold is set. One system used a 24V Outback FX2524T (with
          current boards following a nearby lightning strike) and the
          other used a Magnum MS2812. In the former case, we defeated
          the search (against the customer's preference, as she liked
          the total silence once her day was done). In the latter, the
          customer rejected and we removed the surge arrestor once it
          became clear that the inverter wouldn't sleep.<br>
          <br>
          Has anyone else experienced this? Is there a fix for it?
          Robin, can you chime in here (off list if necessary; I'll
          carefully post your response)?<br>
          <br>
          Thank you,<br>
          Allan<br>
          <div class="moz-signature">-- <br>
            <meta http-equiv="Content-Type" content="text/html;
              charset=ISO-8859-1">
            <meta name="ProgId" content="Word.Document">
            <meta name="Generator" content="Microsoft Word 11">
            <meta name="Originator" content="Microsoft Word 11">
            <link rel="File-List" href="SignatureNew_files/filelist.xml">
            <!--[if gte mso 9]><xml>
 <o:DocumentProperties>
  <o:Author>pe</o:Author>
  <o:Template>Normal</o:Template>
  <o:LastAuthor>pe</o:LastAuthor>
  <o:Revision>5</o:Revision>
  <o:TotalTime>1</o:TotalTime>
  <o:Created>2013-06-07T19:15:00Z</o:Created>
  <o:LastSaved>2013-06-10T19:03:00Z</o:LastSaved>
  <o:Pages>1</o:Pages>
  <o:Words>73</o:Words>
  <o:Characters>420</o:Characters>
  <o:Company>pe</o:Company>
  <o:Lines>3</o:Lines>
  <o:Paragraphs>1</o:Paragraphs>
  <o:CharactersWithSpaces>492</o:CharactersWithSpaces>
  <o:Version>11.9999</o:Version>
 </o:DocumentProperties>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:WordDocument>
  <w:SpellingState>Clean</w:SpellingState>
  <w:GrammarState>Clean</w:GrammarState>
  <w:ValidateAgainstSchemas/>
  <w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
  <w:IgnoreMixedContent>false</w:IgnoreMixedContent>
  <w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
  <w:Compatibility>
   <w:UseFELayout/>
  </w:Compatibility>
  <w:BrowserLevel>MicrosoftInternetExplorer4</w:BrowserLevel>
 </w:WordDocument>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:LatentStyles DefLockedState="false" LatentStyleCount="156">
 </w:LatentStyles>
</xml><![endif]-->
            <style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:"MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-alt:"\FF2D\FF33 \660E\671D";
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
@font-face
        {font-family:"\@MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {mso-style-parent:"";
        margin:0in;
        margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:12.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"MS Mincho";
        color:black;}
a:link, span.MsoHyperlink
        {color:blue;}
a:visited, span.MsoHyperlinkFollowed
        {color:blue;}
span.SpellE
        {mso-style-name:"";
        mso-spl-e:yes;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.25in 1.0in 1.25in;
        mso-header-margin:.5in;
        mso-footer-margin:.5in;
        mso-paper-source:0;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 10]>
<style>
 /* Style Definitions */
 table.MsoNormalTable
        {mso-style-name:"Table Normal";
        mso-tstyle-rowband-size:0;
        mso-tstyle-colband-size:0;
        mso-style-noshow:yes;
        mso-style-parent:"";
        mso-padding-alt:0in 5.4pt 0in 5.4pt;
        mso-para-margin:0in;
        mso-para-margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:10.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"Times New Roman";
        mso-ansi-language:#0400;
        mso-fareast-language:#0400;
        mso-bidi-language:#0400;}
</style>
<![endif]--><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="4098"/>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1"/>
 </o:shapelayout></xml><![endif]-->
            <div class="Section1">
              <p class="MsoNormal"><b>Allan <span class="SpellE">Sindelar</span></b><br>
                <span style="font-size:10.0pt"><a moz-do-not-send="true"
                    href="mailto:Allan@positiveenergysolar.com"><u><span
                        style="color:#000099">Allan@positiveenergysolar.com</span></u></a></span><br>
                <span style="font-size:10.0pt">NABCEP Certified PV
                  Installation Professional <br>
                  NABCEP Certified Technical Sales Professional<br>
                  New Mexico EE98J Journeyman Electrician<br>
                  Founder and Chief Technology Officer<br>
                  <b>Positive Energy, Inc.</b>, a Certified B <span
                    class="SpellE">Corporation<sup><span
                        style="font-size:7.5pt">TM</span></sup></span><br>
                  3209 Richards Lane<br>
                  Santa Fe, New Mexico 87507<br>
                  <b>505 424-1112 office 780-2738 cell</b><br>
                  <a moz-do-not-send="true"
                    href="http://www.positiveenergysolar.com/"
                    target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></p>