      I agree that SCE's position is not suppportable. SCE has a long
      history of obstructing PV while professing to support it; that's
      my opinion based on following online PV newsletters and Wrenches
      posts over the years. If SCE gets away with this, other utilities
      are likely to follow. I don't know what action if any we should
      take, as we're not in California. Should installers outside of
      California weigh in on this? If so, how?<br>
      <br>
      I am also of the opinion that utilities in general are gathering
      resources to fight back against this disruptive technology - PV,
      not batteries - that will fundamentally alter their
      regulated-monopoly-with-guaranteed-rate-of-return business
      structure. New Mexico is no exception, as we have already seen on
      multiple occasions.<br>
      <br>
      Simple reality: buying power at nighttime off peak rates to charge
      batteries in order to sell power back at peak day rates is not
      cost effective when the amortized cost of battery replacement due
      to heavy cycling is factored in. So independent of the legality of
      SCE's position, it simply doesn't make financial sense.<br>
      Allan<br>
      <br>
      <div class="moz-signature">
        <meta http-equiv="Content-Type" content="text/html;
          charset=ISO-8859-1">
        <meta name="ProgId" content="Word.Document">
        <meta name="Generator" content="Microsoft Word 11">
        <meta name="Originator" content="Microsoft Word 11">
        <link rel="File-List" href="SignatureNew_files/filelist.xml">
        <!--[if gte mso 9]><xml>
 <o:DocumentProperties>
  <o:Author>pe</o:Author>
  <o:Template>Normal</o:Template>
  <o:LastAuthor>pe</o:LastAuthor>
  <o:Revision>5</o:Revision>
  <o:TotalTime>1</o:TotalTime>
  <o:Created>2013-06-07T19:15:00Z</o:Created>
  <o:LastSaved>2013-06-10T19:03:00Z</o:LastSaved>
  <o:Pages>1</o:Pages>
  <o:Words>73</o:Words>
  <o:Characters>420</o:Characters>
  <o:Company>pe</o:Company>
  <o:Lines>3</o:Lines>
  <o:Paragraphs>1</o:Paragraphs>
  <o:CharactersWithSpaces>492</o:CharactersWithSpaces>
  <o:Version>11.9999</o:Version>
 </o:DocumentProperties>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:WordDocument>
  <w:SpellingState>Clean</w:SpellingState>
  <w:GrammarState>Clean</w:GrammarState>
  <w:ValidateAgainstSchemas/>
  <w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
  <w:IgnoreMixedContent>false</w:IgnoreMixedContent>
  <w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
  <w:Compatibility>
   <w:UseFELayout/>
  </w:Compatibility>
  <w:BrowserLevel>MicrosoftInternetExplorer4</w:BrowserLevel>
 </w:WordDocument>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:LatentStyles DefLockedState="false" LatentStyleCount="156">
 </w:LatentStyles>
</xml><![endif]-->
        <style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:"MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-alt:"\FF2D\FF33 \660E\671D";
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
@font-face
        {font-family:"\@MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {mso-style-parent:"";
        margin:0in;
        margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:12.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"MS Mincho";
        color:black;}
a:link, span.MsoHyperlink
        {color:blue;}
a:visited, span.MsoHyperlinkFollowed
        {color:blue;}
span.SpellE
        {mso-style-name:"";
        mso-spl-e:yes;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.25in 1.0in 1.25in;
        mso-header-margin:.5in;
        mso-footer-margin:.5in;
        mso-paper-source:0;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 10]>
<style>
 /* Style Definitions */
 table.MsoNormalTable
        {mso-style-name:"Table Normal";
        mso-tstyle-rowband-size:0;
        mso-tstyle-colband-size:0;
        mso-style-noshow:yes;
        mso-style-parent:"";
        mso-padding-alt:0in 5.4pt 0in 5.4pt;
        mso-para-margin:0in;
        mso-para-margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:10.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"Times New Roman";
        mso-ansi-language:#0400;
        mso-fareast-language:#0400;
        mso-bidi-language:#0400;}
</style>
<![endif]--><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="4098"/>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1"/>
 </o:shapelayout></xml><![endif]-->
        <div class="Section1">
          <p class="MsoNormal"><b>Allan <span class="SpellE">Sindelar</span></b><br>
            <span style="font-size:10.0pt"><a
                href="mailto:Allan@positiveenergysolar.com"><u><span
                    style="color:#000099">Allan@positiveenergysolar.com</span></u></a></span><br>
            <span style="font-size:10.0pt">NABCEP Certified PV
              Installation Professional <br>
              NABCEP Certified Technical Sales Professional<br>
              New Mexico EE98J Journeyman Electrician<br>
              Founder and Chief Technology Officer<br>
              <b>Positive Energy, Inc.</b>, a Certified B <span
                class="SpellE">Corporation<sup><span
                    style="font-size:7.5pt">TM</span></sup></span><br>
              3209 Richards Lane<br>
              Santa Fe, New Mexico 87507<br>
              <b>505 424-1112 office 780-2738 cell</b><br>
              <a href="http://www.positiveenergysolar.com/"
                target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></p>
          <p class="MsoNormal"><span style="font-size:10.0pt"><span
                style="mso-spacerun:yes">&nbsp;</span></span></p>
        </div>
      </div>
      On 8/8/2013 3:02 PM, Phil Undercuffler wrote:<br>
    </div>
    <blockquote
cite="mid:CAPLQxEL6gXwaGUFc4n2--_iZZRBmPpV8EVJsgGqq1FwFpEy3zw@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small">Wrenches,<br>
        </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small">
          <br>
        </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small">Unfortunately,
          this is affecting all battery-based systems -- it's not
          limited to OutBack.&nbsp;</div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small">
          <br>
        </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small">SCE
          recently issued an External Memorandum stating their position.
          &nbsp;I've read the memorandum, but I've also read SCE's Rule 21
          and their NEM tariff, and the utility's position is not
          supported by their own rules. &nbsp;These systems fully meet the
          requirements of the SCE Rule 21 and NEM Tariff. &nbsp;The new RPS
          Guidebook, which the SCE NEM Tariff uses to define permissible
          systems, allows for two classes of energy storage --
          Integrated, and Directly Connected. &nbsp;With Directly Connected
          energy storage, the system can be charged by any number of
          sources. &nbsp;The customer is allowed to have onsite loads.
          &nbsp;Maintaining a battery is an onsite load. &nbsp;The only energy
          exported is from the renewable source, the PV array. &nbsp;</div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
        </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small">SCE's
          position that the battery can never charge from the grid is
          simply not supported by their own rules, However, their
          current position has put a substantial barrier in place to
          homeowners that desire grid-tie with battery backup, and to
          businesses like your own that support this market. &nbsp;We need to
          push back against this position, and help people move forward
          with their renewable energy systems. &nbsp;</div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
        </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small">I
          would ask any of you affected by this issue to press the CPUC
          to give SCE and the other utilities clear and specific
          guidance on this issue as soon as possible. Explain how this
          current impasse affects your business and your customers.&nbsp;<span
style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Telephone:
            <a moz-do-not-send="true" href="tel:866-849-8390"
              value="+18668498390" target="_blank">866-849-8390</a> or
            <a moz-do-not-send="true" href="tel:415-703-2074"
              value="+14157032074" target="_blank">415-703-2074</a>&nbsp;</span><span
style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Email:
          </span><a moz-do-not-send="true"
            href="mailto:public.advisor@cpuc.ca.gov"
            style="font-family:Calibri,sans-serif;font-size:11pt"
            target="_blank">public.advisor@cpuc.ca.gov</a>.&nbsp;Better yet,
          file a complaint with the CPUC, either as an informal
          complaint or as a formal complaint. &nbsp;Formal complaints carry
          far more weight, but take more work. &nbsp;More info on the process
          is available at&nbsp;<a moz-do-not-send="true"
            href="http://www.cpuc.ca.gov/PUC/aboutus/Divisions/CSID/Public+Advisor/"
            style="font-family:Calibri,sans-serif;font-size:11pt"
            target="_blank">http://www.cpuc.ca.gov/PUC/aboutus/Divisions/CSID/Public+Advisor/</a></div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
        </div>
        <div>
          <div class="gmail_default"
            style="font-family:arial,helvetica,sans-serif;font-size:small">Best
            regards,</div>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
        Philip Undercuffler<br>
        Director, Product Management and Strategy<br>
        OutBack Power Technologies<br>
        17825 59th Ave NE, Suite B, Arlington, WA 98223<br>
        <a moz-do-not-send="true" href="tel:360.618.4306"
          value="+13606184306" target="_blank">360.618.4306</a> office
        &nbsp;| &nbsp;<a moz-do-not-send="true" href="tel:425.319.2821"
          value="+14253192821" target="_blank">425.319.2821</a> mobile<br>
        <a moz-do-not-send="true" href="http://www.outbackpower.com"
          target="_blank">www.outbackpower.com</a><br>
        <div class="gmail_extra"><br>
          <br>
          <div class="gmail_quote">On Thu, Aug 8, 2013 at 7:45 AM,
            August Goers <span dir="ltr">&lt;<a moz-do-not-send="true"
                href="mailto:august@luminalt.com" target="_blank">august@luminalt.com</a>&gt;</span>
            wrote:<br>
            <blockquote class="gmail_quote" style="margin:0px 0px 0px
0.8ex;border-left-width:1px;border-left-color:rgb(204,204,204);border-left-style:solid;padding-left:1ex">
              <div link="blue" vlink="purple" lang="EN-US">
                <div>
                  <p>
                    Hi Wrenches,</p>
                  <p>&nbsp;</p>
                  <p>I bumped into this article about an Outback battery
                    backup system being rejected by a utility in
                    Southern CA:</p>
                  <p><a moz-do-not-send="true"
href="http://www.renewableenergyworld.com/rea/news/article/2013/08/solar-battery-backup-under-attack-in-california?cmpid=SolarNL-2013-08-08"
                      target="_blank">http://www.renewableenergyworld.com/rea/news/article/2013/08/solar-battery-backup-under-attack-in-california?cmpid=SolarNL-2013-08-08</a></p>
                  <p>It sounds like the utility is rejecting the system
                    because the batteries have the capability of feeding
                    back to the grid. I'm not familiar enough with the
                    Outback system to know how this would work. We are
                    installing a pretty good amount of Sunny Island
                    based battery backups these days but they don't have
                    the capability of sending battery power to the grid.</p>
                  <p>&nbsp;</p>
                  <p>Thoughts?</p>
                  <p>&nbsp;</p>
                  <p>-August</p>
                  <p>&nbsp;</p>
                  <p>&nbsp;</p>
                  <p><b><span style="font-size:9pt;font-family:'Century
                        Gothic',sans-serif">August Goers</span></b></p>
                  <p><span style="font-size:8pt;font-family:'Century
                      Gothic',sans-serif">Luminalt Energy Corporation</span></p>
                  <p><span style="font-size:8pt;font-family:'Century
                      Gothic',sans-serif">o: <a moz-do-not-send="true"
                        href="tel:415.641.4000" value="+14156414000"
                        target="_blank">415.641.4000</a></span></p>
                  <p><span style="font-size:8pt;font-family:'Century
                      Gothic',sans-serif">m: <a moz-do-not-send="true"
                        href="tel:415.559.1525" value="+14155591525"
                        target="_blank">415.559.1525</a></span></p>
                  <p>&nbsp;</p>
                </div>
              </div>
              <br>
              _______________________________________________<br>
              List sponsored by Home Power magazine<br>
              <br>
              List Address: <a moz-do-not-send="true"
                href="mailto:RE-wrenches@lists.re-wrenches.org"
                target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
              <br>
              Change email address &amp; settings:<br>
              <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
              <br>
              List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
              <br>
              List rules &amp; etiquette:<br>
              <a moz-do-not-send="true"
                href="http://www.re-wrenches.org/etiquette.htm"
                target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
              <br>
              Check out participant bios:<br>
              <a moz-do-not-send="true"
                href="http://www.members.re-wrenches.org"
                target="_blank">www.members.re-wrenches.org</a><br>
              <br>
              <br>
            </blockquote>
          </div>
          <br>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>