<br><font size=2 face="sans-serif">Hi,</font>
<br><font size=2 face="sans-serif">That is correct...the XW does have a
frequency shift (Batt V=Bulk) that causes grid-tie inverter to disconnect.
Remember, the </font>
<br><font size=2 face="sans-serif">total kW of the grid-tie unit cannot
exceed the rating of a single XW, even in a multi-unit system.</font>
<br><font size=2 face="sans-serif">Eric<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Eric Bentsen</b> &nbsp;| &nbsp;</font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>&nbsp; | &nbsp;Solar
Business</b> &nbsp;| &nbsp; <b>UNITED STATES</b> &nbsp;| &nbsp; <b>Technical
Support Representative</b> <b><br>
Phone:</b> +(650) 351-8237 ext. 001# &nbsp;| &nbsp; <b><br>
Email:</b> </font><a href="mailto:eric.bentsen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>eric.bentsen@schneider-electric.com</u></font></a><font size=1 face="Arial">
&nbsp;| &nbsp; <b>Site:</b></font><a href="http://www.schneider-electric.com/solar" target=_blank><font size=1 color=blue face="Arial"><u>
www.schneider-electric.com/solar</u></font></a><font size=1 face="Arial">
&nbsp;| &nbsp; <b>Address:</b> 250 South Vasco Rd., Livermore, CA 94551
<br>
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><a href="www.schneider-electric.com/solar"><img src=cid:_2_125F90CC125F8D24006CA59D88257BB9></a><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=1 face="Arial">
</font><font size=3><br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">Ryan &lt;ryan@kb1uas.com&gt;</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">re-wrenches@lists.re-wrenches.org</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">07/31/2013 11:16 AM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">Re: [RE-wrenches] Outback AC coupling
Sunpower?</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">re-wrenches-bounces@lists.re-wrenches.org</font></table>
<br>
<hr noshade>
<br>
<br>
<br><font size=3>Ray<br>
You did not mention the XW, it frequency dithers so it is a pretty straight
forward setup. It also comes in 4, 4.5 and 6KW<br>
<br>
Ryan<br>
</font><img src=cid:_2_0FF159C80FF15650006CA59D88257BB9><font size=3><br>
</font>
<br><font size=3>On 7/31/2013 2:04 PM, Ray Walters wrote:</font>
<br><font size=3>Hi Kelly;<br>
<br>
I agree the Radian system is appealing. &nbsp;Its basically uses a circuit
breaker that can be controlled like a relay as well, and just disconnects
the GT inverter.<br>
I'm going to offer a brief table of what I've found for my choices:<br>
</font>
<table border width=100%>
<tr valign=top>
<td width=9%><font size=3>Brand</font>
<td width=24%><font size=3>Control Method</font>
<td width=27%><font size=3>Pros </font>
<td width=38%><font size=3>Cons</font>
<tr valign=top>
<td><font size=3>SMA Sunny Island</font>
<td><font size=3>Frequency shift to disconnect GT inverter</font>
<td><font size=3>simplest wiring, Trusted GT industry player</font>
<td><font size=3>most expensive, Freq shift can cause other problems</font>
<tr valign=top>
<td><font size=3>Outback Radian</font>
<td><font size=3>Remote controlled Circuit breaker disconnects GT inverter</font>
<td><font size=3>fairly simple wiring, &nbsp;relay and breaker are combined,
better control of battery charging</font>
<td><font size=3>still expensive, not available in smaller than 8 kw model</font>
<tr valign=top>
<td><font size=3>Magnum</font>
<td><font size=3>Diversion load controls for battery regulation &nbsp;(soon
to offer AC load control)</font>
<td><font size=3>lower cost, proven technology, freq shift control offered
as fail safe</font>
<td><font size=3>most complicated wiring, &nbsp;diversion loads not always
reliable or available</font>
<tr valign=top>
<td><font size=3>Modsine Backup system</font>
<td><font size=3>no AC coupling, just an old fashioned backup system</font>
<td><font size=3>low cost</font>
<td><font size=3>complicated, needs customer interaction, not as efficient,
GT PV not used, dedicated PV modules only charge backup system</font>
<tr valign=top>
<td><font size=3>Generator</font>
<td><font size=3>No AC coupling, generator runs backup loads</font>
<td><font size=3>lowest cost, &nbsp;backup power available for as long
as outage (no batteries)<br>
best for week long outages that only occur every few years</font>
<td><font size=3>Not Renewable, fuel storage issues, doesn't switch fast
enough to maintain computers, etc.</font></table>
<br><font size=3><br>
<br>
I'm still pricing out the options, but the SI and Radian seem a bit overkill
for smaller systems. &nbsp;Backup inverter power of just a couple thousand
watts is all that most people need. &nbsp;The Magnum is appealing, &nbsp;but
I have quite a bit of experience with load diversion controls from &nbsp;wind
and Hydro systems, and I really feel that its overly complicated for the
less than 1% of the time that the grid is out. &nbsp;Keeping the battery
from being damaged is what's important, but maintaining full 3 stage charging
for a couple of days a year is not. &nbsp;The batteries can be properly
charged once the grid returns. &nbsp;May be able to use Outback's ROCB
with the Magnum? &nbsp;That might get the best of both worlds.<br>
If I was building the entire system to start, I'd just use a single Outback
GVFX with its own PV array, and add GT inverters and array that were independent
for the rest of the GT requirements. &nbsp;This project however is retrofitting
an existing GT system. &nbsp;<br>
I've done many backup systems in the days before Grid Tie, and they work
fairly well. &nbsp;Basically either the modules are not used much of the
time, or the customer has a few circuits that are on the backup system
(off grid) all the time. &nbsp; They operate it just like an off grid system,
the only difference is that when its time to run a generator, they can
just switch to the grid. &nbsp;These are not for your average customer,
but can work well for someone that likes to save money and tinker.<br>
Another consideration is that if the battery bank is large enough relative
to the array, over charging becomes less of an issue; especially with flooded
cells that can stand a bit of over charging (&quot;equalization&quot;)
every now and then. &nbsp; However, I can see that the average small sealed
battery bank hooked up to several KWs of PV could get ruined in a day.<br>
I'll close with a quote from Joe Swartz in his 2012 Solar pro magazine
article : <br>
<br>
&quot;AC coupling is still the Wild West of renewable energy applications&quot;<br>
</font>
<br><tt><font size=3>R.Ray Walters<br>
CTO, Solarray, Inc<br>
Nabcep Certified PV Installer, <br>
Licensed Master Electrician<br>
Solar Design Engineer<br>
303 505-8760</font></tt>
<br><font size=3>On 7/30/2013 11:37 PM, Kelly Keilwitz, Whidbey Sun &amp;
Wind wrote:</font>
<br><font size=3>Ray, </font>
<br><font size=3>The battery-based inverter in an AC-coupled system should
not be grid-interactive. The grid passes through the BB inverter to the
grid-direct inverter(s). The BB inverter is there to create a stable grid-like
signal for the grid-direct inverters when the grid is not present, and
to manage the batteries. Thus, the pass-through AC capability of the BB
inverters normally (there is a complicated work-around) must be able to
handle all of the PV AC output, when loads are low.</font>
<br><font size=3>You probably are aware, but to make it clear in this thread:
the system needs to have some method to protect the batteries from overcharging,
as a result of the grid-direct inverter output when the grid is down and
loads can't use all the solar energy available. With the Sunny Islands
it's done by a signal that reduces output from the Sunny Boys without disconnecting
them. With Outback and others it's done with a installer-designed relay
that disconnects the grid-direct inverter when the battery voltage gets
to a set point. We haven't done an AC-coupled system with the Radian, yet.
Sounds like the remote controlled breaker is Outback's approved and listed
way to do it. About time.</font>
<br>
<br><font size=3>-Kelly </font>
<br><font size=2><br>
Kelly Keilwitz, P.E. <br>
Principal<br>
Whidbey Sun &amp; Wind<br>
Renewable Energy Systems<br>
NABCEP PV Installation Professional<br>
WA Electrical Administrator</font><font size=2 color=blue><u><br>
</u></font><a href=mailto:kelly@whidbeysunwind.com><font size=2 color=blue><u>kelly@whidbeysunwind.com</u></font></a><font size=2><br>
PH &amp; FAX: 360.678.7131</font><font size=3><br>
<br>
</font>
<br>
<br><font size=3>On Jul 30, 2013, at 4:23 PM, Ray Walters &lt;</font><a href=mailto:ray@solarray.com><font size=3 color=blue><u>ray@solarray.com</u></font></a><font size=3>&gt;
wrote:</font>
<br>
<br><font size=3>The Outback rep got me some good info, and I'm liking
the Radian with the Remote controlled breaker to control the GT inverter
when the grid is out. &nbsp;I've heard of quite a few problems related
to the Sunny Island frequency controlled system.<br>
My question is can off grid inverters like the Magnum be AC coupled? &nbsp;I'm
trying to get the price down, and still handle the 240 vac input from the
GT inverter.<br>
I penciled out the Radian and I was topping $10k before installation. &nbsp;
This customer is hoping for a solution under $10k, and closer to $5k if
possible. &nbsp;I think an elegant lower cost solution for Grid tie with
battery back up is in order. &nbsp;A Radian Lite?<br>
For backup, it could even be mod sine, as it wouldn't be much worse than
generator power or the average UPS setup.<br>
<br>
<br>
R.Ray Walters<br>
CTO, Solarray, Inc<br>
Nabcep Certified PV Installer,<br>
Licensed Master Electrician<br>
Solar Design Engineer<br>
303 505-8760<br>
<br>
On 7/30/2013 2:59 PM, Ray Walters wrote:</font>
<br><font size=3>Hi All;<br>
<br>
I know AC coupled systems have been covered before, but I have a new issue:
&nbsp;positive grounding. &nbsp;A customer with an existing 8kw Sunpower
system wants to add backup. &nbsp; He was put off by the high cost the
Sunny Island, so I was steering him towards a single Outback VFX coupled
to just one of his 3 inverters. &nbsp;The issue is how will the VFX work
with positive grounded inverters. &nbsp;I'm assuming that since the two
inverters will only be connected by AC, that the positive vs negative grounding
of their separate DC systems will not matter. &nbsp;Any experience with
this particular scenario: Sunpower system AC coupled to an Outback?<br>
Also, would I even need a GVFX, since the inverter would only be used during
outages &nbsp;(which might allow a generator to be used later as well)
&nbsp;A VFX should still AC couple to the GT inverter during an outage,
right?<br>
<br>
Thanks as always,<br>
</font>
<br><font size=3><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: </font><a href="mailto:RE-wrenches@lists.re-wrenches.org"><font size=3 color=blue><u>RE-wrenches@lists.re-wrenches.org</u></font></a><font size=3><br>
<br>
Change email address &amp; settings:</font><font size=3 color=blue><u><br>
</u></font><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><font size=3 color=blue><u>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</u></font></a><font size=3><br>
<br>
List-Archive: </font><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><font size=3 color=blue><u>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</u></font></a><font size=3><br>
<br>
List rules &amp; etiquette:</font><font size=3 color=blue><u><br>
</u></font><a href="http://www.re-wrenches.org/etiquette.htm"><font size=3 color=blue><u>www.re-wrenches.org/etiquette.htm</u></font></a><font size=3><br>
<br>
Check out participant bios:</font><font size=3 color=blue><u><br>
</u></font><a href="http://www.members.re-wrenches.org/"><font size=3 color=blue><u>www.members.re-wrenches.org</u></font></a><font size=3><br>
</font>
<br>
<br><font size=3><br>
</font>
<br><tt><font size=3>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: </font></tt><a href="mailto:RE-wrenches@lists.re-wrenches.org"><tt><font size=3 color=blue><u>RE-wrenches@lists.re-wrenches.org</u></font></tt></a><tt><font size=3><br>
<br>
Change email address &amp; settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=3 color=blue><u>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</u></font></tt></a><tt><font size=3><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=3 color=blue><u>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</u></font></tt></a><tt><font size=3><br>
<br>
List rules &amp; etiquette:<br>
</font></tt><a href="http://www.re-wrenches.org/etiquette.htm"><tt><font size=3 color=blue><u>www.re-wrenches.org/etiquette.htm</u></font></tt></a><tt><font size=3><br>
<br>
Check out participant bios:<br>
</font></tt><a href="http://www.members.re-wrenches.org/"><tt><font size=3 color=blue><u>www.members.re-wrenches.org</u></font></tt></a><tt><font size=3><br>
<br>
</font></tt>
<br><font size=3><br>
<br>
</font>
<br><tt><font size=3>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: </font></tt><a href="mailto:RE-wrenches@lists.re-wrenches.org"><tt><font size=3 color=blue><u>RE-wrenches@lists.re-wrenches.org</u></font></tt></a><tt><font size=3><br>
<br>
Change email address &amp; settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=3 color=blue><u>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</u></font></tt></a><tt><font size=3><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=3 color=blue><u>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</u></font></tt></a><tt><font size=3><br>
<br>
List rules &amp; etiquette:<br>
</font></tt><a href="http://www.re-wrenches.org/etiquette.htm"><tt><font size=3 color=blue><u>www.re-wrenches.org/etiquette.htm</u></font></tt></a><tt><font size=3><br>
<br>
Check out participant bios:<br>
</font></tt><a href="http://www.members.re-wrenches.org/"><tt><font size=3 color=blue><u>www.members.re-wrenches.org</u></font></tt></a><tt><font size=3><br>
<br>
</font></tt>
<br><tt><font size=2>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change email address &amp; settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List rules &amp; etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
</font></tt>
<br>
<br>