<div dir="ltr">Esteemed Wrenches;<div><br></div><div style>A weird troubleshooting call today for my business partner DanB. I wish I had been along if only for shock and awe and lessons learned.</div><div style><br></div><div style>
A nicely installed vintage 12VDC PV system that someone else designed and installed over 10 years ago, we replaced a dead/frozen battery bank a month ago. DanB went back today because customer reported low battery bank voltage.</div>
<div style><br></div><div style>He found the PV input breaker tripped, a Square D QO 2-pole 60 amp. About 600 watts of PV 12vdc nominal on the roof. Reset the breaker, and a few minutes later it was too hot to touch.</div>
<div style><br></div><div style>So our working theory -- the 60a QO on *DC* has a 1.2x ampacity derate, which puts 600w PV right at 60 amps instead of 50. There&#39;s also a bit of a high altitude derate, which I don&#39;t understand at all. And during the battery disaster last year bank voltage was certainly 11vdc or less, and was a bit over 11vdc on DanB&#39;s arrival since the PV had not been charging. That puts us at possibly 65.5 amps. The breaker was maybe just doing its job correctly, though the heat was disturbing I am told.Or maybe it got damaged during the battery disaster......both + and - were connected thru the 2 poles.</div>
<div style><br></div><div style>In any case, our question --- due to my fuzzy memory and poor shopping skills, we have a 100 amp QO 2 pole breaker in stock that needs a home, and it&#39;ll plug right in. I have a nice tech bulletin from Schneider Electric about DC ratings of their breakers that doesn&#39;t show that a 100a QO 2 pole even exists, and a Schneider FAQ that says it&#39;ll work fine:</div>
<div style><a href="http://www.schneider-electric.us/sites/us/en/support/faq/faq_main.page?page=content&amp;country=US&amp;lang=en&amp;id=FA125383&amp;redirect=true">http://www.schneider-electric.us/sites/us/en/support/faq/faq_main.page?page=content&amp;country=US&amp;lang=en&amp;id=FA125383&amp;redirect=true</a><br>
</div><div style><br></div><div style>Any advice on this? We&#39;d sure love to just drop by and pop in the new 100a amp QO breaker instead of installing a whole new DC rated Midnite box. But we don&#39;t want to leave a fire hazard either. With 15 years service on our local volunteer fire department, It would be rather embarrassing if a &quot;fix&quot; we made to this old off-grid system caused a fire. ;-) We are aware of the 5k AIR issue with these breakers, but the battery bank is small enough I don&#39;t think it&#39;s quite up there, and information on AIR interruption from battery manufacturers is hard to find......and of course it&#39;s a weird curve.</div>
<div><br></div><div>Thanks in advance;</div><div><br clear="all"><div>Dan Fink,<br>Executive Director;<br>Otherpower<br>Buckville Energy Consulting<br>Buckville Publications LLC<br>NABCEP / IREC accredited Continuing Education Providers<br>