<br><font size=2 face="sans-serif">Hi Lee,</font>
<br><font size=2 face="sans-serif">The MC version is similar to the standard
SW, but does not have grid usage menu (no sell/lbx), and does not give
AC1 priority (assuming both inputs are present). It will support the generator
with battery power whenever the load exceeds the AC2 Amps setting in Menu
11.</font>
<br><font size=2 face="sans-serif">Eric<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Eric Bentsen</b> &nbsp;| &nbsp;</font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>&nbsp; | &nbsp;Solar
Business</b> &nbsp;| &nbsp; <b>UNITED STATES</b> &nbsp;| &nbsp; <b>Technical
Support Representative</b> <b><br>
Phone:</b> +(650) 351-8237 ext. 001# &nbsp;| &nbsp; <b><br>
Email:</b> </font><a href="mailto:eric.bentsen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>eric.bentsen@schneider-electric.com</u></font></a><font size=1 face="Arial">
&nbsp;| &nbsp; <b>Site:</b></font><a href="http://www.schneider-electric.com/solar" target=_blank><font size=1 color=blue face="Arial"><u>
www.schneider-electric.com/solar</u></font></a><font size=1 face="Arial">
&nbsp;| &nbsp; <b>Address:</b> 250 South Vasco Rd., Livermore, CA 94551
<br>
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><a href="www.schneider-electric.com/solar"><img src=cid:_2_06FD283406FD2404005C088888257B91></a><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=1 face="Arial">
</font><font size=3><br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">&quot;info@solarplexus1.com&quot; &lt;info@solarplexus1.com&gt;</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">RE-wrenches@lists.re-wrenches.org</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">06/21/2013 07:29 AM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">[RE-wrenches] generator support mode</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">re-wrenches-bounces@lists.re-wrenches.org</font></table>
<br>
<hr noshade>
<br>
<br>
<br><tt><font size=2><br>
 &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp;
I have a project using an SW4024 inverter that uses the generator support
mode with a smaller hydro AC generator. &nbsp; Worked well, but one of
the to inverters died. There are plenty of new SWs on the internet, but
all the new ones are SW4024MC2. &nbsp; Apparently the SELL mode does not
exist in the MC2 version and Auto Gen Start is an option. &nbsp; Does anyone
know if the good old generator support is available in the MC2 version,
or has it been scrapped along with the SELL mode. <br>
<br>
 &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp;
Generator support mode--where some inverter AC output can be added to the
generator AC input to meet a load larger than the generator could otherwise
handle. &nbsp;Not just where the inverter backs off the battery charger
enough to use full generator input for the load.<br>
<br>
 &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp;
Any insight on the MC2 version would be helpful. &nbsp;<br>
<br>
Lee Tavenner<br>
Solar Plexus<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change email address &amp; settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List rules &amp; etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
<br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________<br>
</font></tt>
<br>
<br>